    Magnetic or manual starter

    Looking for the best place to get a motor starter for a 2hp 1ph motor.
    Dave
    _____________________

    Dave

    Some mistakes are just too much fun to only make once!

  2. #2
    Join Date
    Sep 2009
    Location
    Bushnell. Florida
    Posts
    43

    motor starters

    Motor starters are nothing but switches unless they have peripheral functions. Magnetic starters switch the motor on, but when power is lost the starter drops out and the motor does not come back on when the power comes back. Some people view this as a safty issue.

    Magnetic starters are expensive, but lower priced units can be purchased at Grizzly and Ebay, and jarring a magnetic starter machine can cause the magnetic starter to drop out.

    A standard two pole switch similar to those you have in your house can be used to control the motor if it has an adequate current rating. One hp = 746 watts so you need 746 times 2 watts == 1492 watts. Watts = voltage times current and voltage usually is 220 volts for 2hp motors. You need at least 7 amps so the standard 15 amp switch will work fine. I would buy a standard 20 amp switch that costs a little more but is adequate for the next machine.

  3. #3
    Join Date
    Jul 2008
    Location
    Courtenay BC Canada
    Posts
    2,750
    Overload protection for the motor is another feature most often offered by a Mag Starter.. A smaller motor like that may have it already, if it doesnt, the Mag Starter will offer protection.

  4. #4
    Join Date
    Jun 2007
    Location
    Wichita, Kansas
    Posts
    1,795
    Quote Originally Posted by Ronald Mancini View Post
    ...
    A standard two pole switch similar to those you have in your house can be used to control the motor if it has an adequate current rating. One hp = 746 watts so you need 746 times 2 watts == 1492 watts. Watts = voltage times current and voltage usually is 220 volts for 2hp motors. You need at least 7 amps so the standard 15 amp switch will work fine. I would buy a standard 20 amp switch that costs a little more but is adequate for the next machine.
    You really need to be a little cautious there. Standard residential switches are not designed for inductive loads. There's a much different voltage-time profile generated when the circuit powering a motor is made or broken. Switches designed for motor control will be rated in HP as well as amperage. And generally the HP rating is significantly less than a straight volt-amps wattage/746 would indicate. Not saying what you suggest wouldn't work, but don't assume that a switch rated for a particular amperage is rated for an inductive load at that amperage.
    Tom Veatch
    Wichita, KS
    USA

  5. #5
    Join Date
    Jun 2007
    Location
    Wichita, Kansas
    Posts
    1,795
    Quote Originally Posted by Rick Fisher View Post
    Overload protection for the motor is another feature most often offered by a Mag Starter.. A smaller motor like that may have it already, if it doesnt, the Mag Starter will offer protection.
    It's always been my assumption, perhaps incorrectly, that the difference between a "Magnetic Starter" and a "Magnetic Switch" was the presence of overload protection (commonly called "heaters"?) in the "Starter" and their absence in the "Switch".
    Tom Veatch
    Wichita, KS
    USA

  6. #6
    Join Date
    Mar 2003
    Location
    Monroe, MI
    Posts
    11,896
    I get stuff like that from FactoryMation.com or Ebay. With some persistence, I've gotten some pretty good deals on name-brand starters on Ebay, some brand new. But you need to know what you are looking for with respect to size, coil voltage, etc. Since most of my applications have been replacing non-magnetic switches, I just pull off the overloads.


  7. #7
    Join Date
    Dec 2006
    Location
    Toronto Ontario
    Posts
    11,304
    Manual and magnetic starters can incorporate overload elements or relays.

    You need to know the motor full load current rating when sizing overload protection for your motor.

    A magnetic starter will provide restart protection following a power outage, as the contactor will drop out if the power is removed.

    This can be a significant safety feature if there is a momentary power outage. Sawing something, then having the lights go out and then back on again is bad enough. It can be worse if the saw starts up again.

    I haven't heard of magnetic starters dropping out from impacts, however there have been reports of the cheap ones closing when subject to vibration or impact.

    Regards, Rod.

  8. #8
    Join Date
    Jul 2009
    Location
    Mission, Texas
    Posts
    976
    At Delta we did get a batch of mag switches that were defective in that they would open when the switch enclosure was hit lightly. They wer for the 3HP 1ph Uni's. Can't remember the manufacturer now, but to my knowledge they were recalled and replaced. Made in China, I suspect, but what isn't these days? Haven't seen this problem since, all of my tools(except the hand units) have mags on them.

  9. #9
    Join Date
    Oct 2006
    Location
    Hudson, NH
    Posts
    436
    can I buy a mag starter rated for 5 hp and install a 2hp motor? I'm thinking that i may soon change to 5 hp but i want to get the machine running for now.
    _____________________

    Dave

    Some mistakes are just too much fun to only make once!

  10. #10
    Just as an aside, I would also not rely on any a switch to do it's job, when working on a machine, so always un-plug a machine when working on it.

  11. #11
    Join Date
    Dec 2006
    Location
    Toronto Ontario
    Posts
    11,304
    Quote Originally Posted by Dave Bureau View Post
    can I buy a mag starter rated for 5 hp and install a 2hp motor? I'm thinking that i may soon change to 5 hp but i want to get the machine running for now.
    Yes, if the overload relay can be adjusted low enough for a 2 HP motor.

    Regards, Rod.

  12. #12
    Join Date
    Mar 2003
    Location
    Monroe, MI
    Posts
    11,896
    Also yes, if the overload functionality isn't necessary in your application.


  13. #13
    Join Date
    Feb 2003
    Location
    Doylestown, PA
    Posts
    7,595

    Tom is right

    Quote Originally Posted by Tom Veatch View Post
    You really need to be a little cautious there. Standard residential switches are not designed for inductive loads. There's a much different voltage-time profile generated when the circuit powering a motor is made or broken. Switches designed for motor control will be rated in HP as well as amperage. And generally the HP rating is significantly less than a straight volt-amps wattage/746 would indicate. Not saying what you suggest wouldn't work, but don't assume that a switch rated for a particular amperage is rated for an inductive load at that amperage.
    I had a Chinese switch (not even a light switch) weld itself shut in the on position. Thank heaven it was on a bandsaw I no longer have and I was able to simply unplug it and replace the switch with something more suitable. If it had been on a different machine or different circumstances life could have been "exciting"

  14. #14
    Join Date
    Sep 2009
    Location
    Bushnell. Florida
    Posts
    43

    switch

    The double pole 25 amp switch is made for motors---light bulbs don't come that big. Magnetic motor controls sometimes contain overload coils, but you can get the same result by sizing a circuit breaker. The choice depends on how much you want to spend and if you think safty is an issue..

  15. #15
    Join Date
    Jul 2008
    Location
    Courtenay BC Canada
    Posts
    2,750
    Quote Originally Posted by Curt Harms View Post
    I had a Chinese switch (not even a light switch) weld itself shut in the on position. Thank heaven it was on a bandsaw I no longer have and I was able to simply unplug it and replace the switch with something more suitable. If it had been on a different machine or different circumstances life could have been "exciting"
    Wow..

    I had a mag starter out of the box stuck one of the hot wires in the hot postion..

    Since then, I really dont trust them..

    Oddly, it was on a bandsaw as well.