    Shop Electrical question

    I am going to rewire a large portion of my shop and have some questions.

    My shop is in the basement and the subpanel is in the same room. The existing outlets are wired by running romex along the floor joists and then down into conduit to the actual wall boxes.

    I am planning on running conduit horizonitally around the room about about 54" high and having boxes about every four feet.

    Can or should I run two seperate 20amp circuits through the conduit so I can alternate which circuit is being loaded. Meaning I would alternate every other outlet to a different ciruit so that a vacuum and a drill plugged into two seperate outlets would be on different circuits?


    If I run two seperate 20amp circuits Can I share the neutral or ground and run two hots? Or would I needt to run two hots, two neutrals, and two grounds?

    Should I run 1/2" or 3"4 conduit?

  2. #2
    Join Date
    Mar 2003
    Location
    SE PA - Central Bucks County
    Posts
    65,923
    You can run conductors for more than one circuit in a single conduit as long as it's sized appropriately. I can't answer the sharing question with any respect to code, but personally, I wouldn't.
    --

    The most expensive tool is the one you buy "cheaply" and often...

  3. #3
    Whether or not you should is up to you and your needs. I like the idea, myself. And I think 12/3 is perfect for what you want to do. I'm unaware of any codes that require you to run all new romex for each circuit.
    Jason Beam
    Sacramento, CA

    beamerweb.com

  4. #4
    Join Date
    Oct 2007
    Location
    Minnesota
    Posts
    322
    I can't answer if using 12/3 meets code or not, but it will work. The two hots must be 180 degrees opposite of each other, otherwise you can easily fry the common wire..start a fire, etc. From a safety standpoint, you may want to stick with multiple wires..much easier to identify what is connected to what breaker and if someone accidentally moves a breaker in the box you don't risk a fire.

    What I did was to have the top outlet on one breaker and the bottom outlet on another breaker and marked the outlet plates with marker to show what was on what breaker. That way I could have two large machines in the same outlet running at the same time. If you do that, you need to break away the metal tab on the hot side of the outlet. Again, I can't say if this meets code or not.

    In general, the larger the conduit the better..especially if you plan on pulling more than 1 romex through. You may want to go with 1 inch which would let you pull much larger wire if you needed to add some larger wire for big 220 machines.

  5. #5
    Join Date
    Dec 2007
    Location
    Western PA
    Posts
    107
    You can share the ground but not the neutral. (unless the wire size is twice as large).

    Scott

  6. #6
    Join Date
    Feb 2003
    Location
    South Windsor, CT
    Posts
    3,304
    Steve,

    You don't say whether this is a finished or unfinished basement, but because you have access to the floor joists I'm going to interpret that as being an unfinished basement.

    Based on that assumption, your receptacles must be GFI-protected (per NEC 210.8). You can't have a multiwire circuit and GFI-protect the separate parts of the circuit.

    It's fine to run multiple 20 amp circuits in the same raceway (conduit). Pull (5) #12 THHN/THWN conductors for the (2) hots, (2) neutrals and 1 equipment grounding conductor. Because these are separate circuits, you can make the first receptacle on each circuit a GFI and use the "feed-through" option to protect the receptacles that are down-circuit from there.

    Rob
    (Addy protocol: unlicensed, homeowner electrician)

  7. #7
    Join Date
    Sep 2007
    Location
    Upstate NY
    Posts
    3,789
    Quote Originally Posted by Rob Russell View Post
    Steve,

    Based on that assumption, your receptacles must be GFI-protected (per NEC 210.8). You can't have a multiwire circuit and GFI-protect the separate parts of the circuit.
    Of course you can; you just have to use a GFCI outlet everytime, rather than one for the circuit.
    If you are saying it is a bad idea I agree, but it is possible.

  8. #8
    Join Date
    Feb 2003
    Location
    South Windsor, CT
    Posts
    3,304
    Quote Originally Posted by Wade Lippman View Post
    Of course you can; you just have to use a GFCI outlet everytime, rather than one for the circuit.
    If you are saying it is a bad idea I agree, but it is possible.
    Wade - yeah, I guess you could do it that way. I agree with your statement that it wouldn't be a good idea.

    Rob

  9. #9
    Join Date
    Feb 2003
    Location
    Overland Park, KS
    Posts
    617
    It is an unfinished space, does code really require GFCI circuits? Do they even make a GFCI that supports 20amp, and is grey?

  10. #10
    Join Date
    Jan 2006
    Location
    Mt. Pleasant, MI
    Posts
    2,924
    If I read your question correctly you want to run two circuits of 20 amps each. Alternating individual outlets from circuit to circuit. That wouldn't be hard and you could pull THHN wires or two runs of 12-2w/g NM and feed through the outlet. One keeps going unbroken, the other goes to the outlet.

    I am not sure you really gain that much but it is possible. It would be the same as running two conduits next to each other, as long as it is properly sized. When pulling NM bigger is better for conduit.

    Joe
    JC Custom WoodWorks

    For best results, try not to do anything stupid.

    "So this is how liberty dies...with thunderous applause." - Padmé Amidala "Star Wars III: The Revenge of the Sith"

  11. #11
    Join Date
    Jun 2007
    Location
    Wichita, Kansas
    Posts
    1,795
    Quote Originally Posted by Scott Velie View Post
    You can share the ground but not the neutral. (unless the wire size is twice as large).

    Scott
    What if the OP ran one 240v 20amp circuit with a neutral (3 12ga wires, black, red, and white) and used the EMT conduit as the grounding conductor. If the 120v outlets alternated connection to the hot wires (black/red) then there would, in effect, be two 120v 20amp circuits that share the neutral and the ground and be protected by a common trip breaker. The only current in the neutral would be the difference between the two hot legs so it would not exceed the 20amp breaker rating. The only downside I see is both circuits would go down if the breaker tripped. An upside would be the availability of 240v if/when needed.
    Tom Veatch
    Wichita, KS
    USA

  12. #12
    Join Date
    Feb 2003
    Location
    South Windsor, CT
    Posts
    3,304
    Quote Originally Posted by Steve Roxberg View Post
    It is an unfinished space, does code really require GFCI circuits? Do they even make a GFCI that supports 20amp, and is grey?
    Steve,

    Here are snippets of the applicable section of the NEC:

    210.8 Ground-Fault Circuit-Interrupter Protection for Personnel.
    (A) Dwelling Units.
    All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in (1) through (8) shall have ground-fault circuit-interrupter protection for personnel.

    (5) Unfinished basements
    for purposes of this section, unfinished basements are defined as portions or areas of the basement not intended as habitable rooms and limited to storage areas, work areas, and the like

    GFI receptacles are absolutely available in 20 amp ratings. You can get gray, but that is probably a color you'll have to get from an electrical supply house. Our local big box stores like Home Depot and Lowe's tend to carry white, almond and beige.


  13. #13
    Join Date
    Feb 2003
    Location
    South Windsor, CT
    Posts
    3,304
    Quote Originally Posted by Tom Veatch View Post
    What if the OP ran one 240v 20amp circuit with a neutral (3 12ga wires, black, red, and white) and used the EMT conduit as the grounding conductor. If the 120v outlets alternated connection to the hot wires (black/red) then there would, in effect, be two 120v 20amp circuits that share the neutral and the ground and be protected by a common trip breaker. The only current in the neutral would be the difference between the two hot legs so it would not exceed the 20amp breaker rating. The only downside I see is both circuits would go down if the breaker tripped. An upside would be the availability of 240v if/when needed.
    Tom,

    If Steve did that, he'd need to install a GFI receptacle everywhere. It's cheaper to run another conductor and use the feed-through capability of a GFI receptacle to protect each string of receptacles.

    Rob

  14. #14
    Join Date
    Feb 2003
    Location
    South Windsor, CT
    Posts
    3,304
    Quote Originally Posted by Joe Chritz View Post
    If I read your question correctly you want to run two circuits of 20 amps each. Alternating individual outlets from circuit to circuit. That wouldn't be hard and you could pull THHN wires or two runs of 12-2w/g NM and feed through the outlet. One keeps going unbroken, the other goes to the outlet.

    I am not sure you really gain that much but it is possible. It would be the same as running two conduits next to each other, as long as it is properly sized. When pulling NM bigger is better for conduit.

    Joe
    If he's running conduit, there is no reason to pull NM-cable and some inspectors will give you grief about running NM in conduit. If conduit is required, he's better off pulling THHN/THWN.

    Rob

  15. #15
    Join Date
    Dec 2003
    Location
    SF Bay Area, CA
    Posts
    15,332
    Quote Originally Posted by Rob Russell View Post
    Wade - yeah, I guess you could do it that way. I agree with your statement that it wouldn't be a good idea.

    Rob
    Right...each GFCI protected circuit requires its own neutral so keep that in mind...nearly bit me in my garage rewire. A true multi-wire system has a common neutral returing current for the black and red hot legs. That won't work in a GFCI circuit as you'll need a second neutral.

    I hear they make 14/4 now and the second neutral has a red line on it.
    Wood: a fickle medium....

    Did you know SMC is user supported? Please help.

Similar Threads

  1. Comment, Electrical Question and a Gloat
    By Hal Flynt in forum General Woodworking and Power Tools
    Replies: 22
    Last Post: 10-23-2008, 2:29 AM
  2. Electrical Service Question
    By Clay Crocker in forum Off Topic Forum
    Replies: 14
    Last Post: 08-28-2007, 8:10 AM
  3. Question about Shop Notes....
    By Bill Huber in forum General Woodworking and Power Tools
    Replies: 6
    Last Post: 08-23-2007, 9:17 PM
  4. Another electrical question for shop wiring
    By Alan Tolchinsky in forum General Woodworking and Power Tools
    Replies: 40
    Last Post: 07-22-2007, 5:00 PM
  5. Shop wiring help (I think again =)), 3 phase question as well.
    By Chris Pasko in forum General Woodworking and Power Tools
    Replies: 6
    Last Post: 01-19-2006, 10:27 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •