Thread: rewiring vacuum Pump to 110

  1. #1

    rewiring vacuum Pump to 110

    I am seriously considering moving to a vacuum chuck system.

    http://www.surpluscenter.com/item.as...0&catname=misc
    Based on my reading this pump seems like it would be a good choice. My only issue is it is 220 and I would rather have it on 110. Does anyone know if it could be rewired to work on 110?

    If anyone knows of a better opion I would love to hear it.
    Mike Vickery

  2. #2
    Join Date
    Feb 2003
    Location
    Griswold Connecticut
    Posts
    6,933
    An internet search shows that pump for sale on eBay. The write up specifically states no 120vac.

    Put the part # into a google search and it's the 4th hit on the list.

  3. #3
    Thanks,
    Are most of you using 110 or 220 for your pumps.
    I dont want to wire it into the same line as my lather and dont really want to take the last spot in my subpanel for another 220.
    Mike Vickery

  4. #4
    Join Date
    Nov 2006
    Location
    North Carolina
    Posts
    106
    I have two vacuum pumps and both run on 220. One is from the surplus center and can not be converted to 110. When I was shopping for pumps, any that ran on 110 seemed to sell for more than their 220 counterparts.

  5. #5
    Join Date
    Sep 2005
    Location
    Ft. Worth Tx.
    Posts
    689

    from 220 to 110

    Hi Mike,
    you wont hurt anything running the pump on the same circuit as the lathe. Specs say the pump only draws 1 to 2 amps. Plenty of safety. I plan to install a plug box with 2 outlets for the pump and lathe. Max

  6. #6
    Join Date
    Feb 2003
    Location
    Roanoke, Illinois
    Posts
    863
    I am using the surplus center 220 pump and I have it wired into the same circuit as my lathe. I have never had any problems.

    Terry

  7. #7
    Same here.

  8. #8
    Join Date
    Aug 2006
    Location
    Lancaster PA USA
    Posts
    254
    How much vacuum does a pump have to draw in order to be able to be used for turning?
    I know the voices in my head aren't real but boy do they come up with some good ideas !
    People discuss my art and pretend to understand as if it were necessary to understand, when it's simply necessary to love. - Claude Monet

  9. #9
    Mike,

    I picked one up off the ebay for ~$150 IIRC. It's 110 V. The only reason I didn't go with a 220 V from surplus is I had extra 110V outlets, but had only put 1 220 V in. If I was smarter when I did my wiring, I would have had two 220 V outlets by the lathe.

    Good luck with it!

    If you ever want to check out the "Lowe's" Vacuum chuck, you can stop by and see what I did. It's cheap, but given the volume of bowls you turn, you may want to go with something of higher durability.

  10. #10
    Join Date
    Sep 2006
    Location
    Stow, OH
    Posts
    1,023
    How about a step up transformer? The 220 V pump is going to be ¼ HP 1.5 Amps, anybody knows how big (what VA) a transformer do we need?

    Gordon

  11. #11
    VA = Volts x Amps = 220 x 1.5 = 330 VA

    But always add a bit extra!
    Mike

  12. #12
    Quote Originally Posted by Gordon Seto View Post
    How about a step up transformer? The 220 V pump is going to be ¼ HP 1.5 Amps, anybody knows how big (what VA) a transformer do we need?

    Gordon
    Don't do it! Typical (meaning almost all) transformers are specifically designed for non-reactive loads. Since a motor load is a highly inductive reactance load, it is not satisfactory for that type of service. Operating the motor using such a configuration may cause the transformer to fail due to internal arcing and overheating and it will certainly lower the efficiency of the motor significantly resulting in the motor running much hotter than it would normally. Since these motor run fairly hot anyway, there would probably be enough additional heating to cause the thermal overload breaker to trip.

    I sent an email to surplus center concerning this and I believe that they quit selling the tiny transformers that they formerly advertised as a means of converting them.

    Bill

  13. #13
    Join Date
    Oct 2005
    Location
    Phoenix, AZ
    Posts
    991
    The pump draws 2 amps max (according to Harvey) and your lathe draws how many on a 220V circuit, about 15 max? then a 20 amp circuit is OK. If its 15 amp then there's a problem. Does your lathe's motor give the amp rating for 220V?

Similar Threads

  1. Vacuum pump question
    By Bobby McCarley in forum Turner's Forum
    Replies: 1
    Last Post: 09-03-2006, 10:24 PM
  2. Milking pump for vacuum veneer press?
    By Lynn Kasdorf in forum General Woodworking and Power Tools
    Replies: 7
    Last Post: 03-08-2005, 8:22 AM
  3. Vacuum pump interpretation
    By Mark Blumer in forum General Woodworking and Power Tools
    Replies: 12
    Last Post: 12-10-2004, 11:08 PM
  4. Vacuum pump for chuck?
    By Sparky Paessler in forum General Woodworking and Power Tools
    Replies: 4
    Last Post: 09-17-2004, 1:49 PM
  5. Vacuum Pump Question?
    By George Skinner in forum General Woodworking and Power Tools
    Replies: 15
    Last Post: 07-03-2004, 6:34 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •