    Got to run underground in conduit for 75 feet between panel boxes for shop....15 amps twice........lights, fans and refrigerator....2 5000 btu a/c's .........wire size? thanks

  2. #2
    Join Date
    Feb 2003
    Location
    Conway, Arkansas
    Posts
    13,182
    Copper #6 SEC (Sevice Entrance Cable). This will carry you up to 70 Amps safely as well as provide you 220V power to the shop.
    Thanks & Happy Wood Chips,
    Dennis -
    Get the Benefits of Being an SMC Contributor..!
    ....DEBT is nothing more than yesterday's spending taken from tomorrow's income.

  3. #3
    Join Date
    Dec 2005
    Location
    panama city fl
    Posts
    201
    Many thanks Dennis......I be a dumb ol plumber but I know when to ask questions........Thanks again......doug

  4. #4
    Join Date
    May 2004
    Location
    N Illinois
    Posts
    4,602
    Go w dennis's advice but always IMHO go a little MORE than you need. You don't want to have to re dig that trench. I learned at my cabin where I had to go underground about 250 ft. I added phone wire in the trench to keep that service underground too and probably overwired. Be sure to have capacity for a 240V lines for tools u may add later. My 2 cents...G Luck
    Jerry

  5. #5
    Join Date
    Feb 2003
    Location
    South Windsor, CT
    Posts
    3,304
    First, SE cable is specifically prohibited for underground installations per NEC article 338.12(A). You could use USE, which is Service Entrance Cable for Underground use.

    Whichever cable you're talking about, there is NO WAY I'd want to pull SE or USE cable through conduit - that would be a major pain to pull. I'd run individual conductors - THWN. #6 THWN is rated for 65 amps, per table 310.16.

    Dennis - where did you get 70 amps worth of ampacity for #6 SEC?

    Rob

  6. #6
    Join Date
    Feb 2003
    Location
    Conway, Arkansas
    Posts
    13,182
    Quote Originally Posted by Rob Russell
    Dennis - where did you get 70 amps worth of ampacity for #6 SEC?

    Rob
    Good Morning Rob....it's a type-o.....I meant to type 60 (sixty).
    Besides that? I didn't know it wasn't cool to pull SEC in conduit. We used to do it all the time when I worked as an electrician, even up through 1/0 SEC.

    Ok Doug....pull three strands of #6 copper inside your conduit. Just don't do like I guy I know and pull a #12 to his shop and burned it down. He was told to NOT run that 12 wire, but to run a #8....some folks just don't listen.
    Thanks & Happy Wood Chips,
    Dennis -
    Get the Benefits of Being an SMC Contributor..!
    ....DEBT is nothing more than yesterday's spending taken from tomorrow's income.

  7. #7
    Join Date
    Feb 2003
    Location
    South Windsor, CT
    Posts
    3,304
    Quote Originally Posted by Dennis Peacock
    Good Morning Rob....it's a type-o.....I meant to type 60 (sixty).
    Besides that? I didn't know it wasn't cool to pull SEC in conduit. We used to do it all the time when I worked as an electrician, even up through 1/0 SEC.

    Ok Doug....pull three strands of #6 copper inside your conduit. Just don't do like I guy I know and pull a #12 to his shop and burned it down. He was told to NOT run that 12 wire, but to run a #8....some folks just don't listen.
    Dennis,

    I'm not saying you can't pull SE in conduit - I just wouldn't want to do it. The #2 SER I've run is enough fun to work with in the basement, let alone the thicker USE through conduit.

    If Doug is installing a 240v subpanel, he needs 4 conductors - not 3. If he uses a 60 amp breaker for the circuit, Doug could use a #10 copper conductor as an EGC - personally I'd use a #8.

    Rob

  8. #8
    Join Date
    Dec 2005
    Location
    panama city fl
    Posts
    201
    I appreciate the help from all of you and will be running the #6 wire. I will also be running a separate grounding rod to the subpanel. I am using a 60 amp breaker to feed the panel as I have nothing that pulls over 15 amps and no 220 requirements, at this time.. But who knows what the future holds? Thanks again for helping me stay safe........doug

  9. #9
    Join Date
    Feb 2003
    Location
    Collin County Texas
    Posts
    2,417
    Beep, wrong, but thank you for playing. (Dead poets society.)

    I may be wrong, but as i understand it, you can only have ONE earth ground and that must be at the main service entrance. ANY subpanel must connect neutral and equipment ground back to the main distribution panel.
    Best Regards, Ken

  10. #10
    Join Date
    Feb 2003
    Location
    South Windsor, CT
    Posts
    3,304
    Ken,

    What is commonly required to feed another building like a shop or shed is a 4-wire feed. The neutral and grounding conductors are bonded only at the service equipment (typically the main panel). However, at the outbuilding, a ground rod or ground rods are also required and the EGC has to connect to those ground rods. The neutral and EGC are NOT bonded at the outbuilding.

    Some localities want it done differently, so this is one of those "check with the inspector" types of things - see how they want it done.

    Rob

Similar Threads

  1. DJ-20 110V wiring change?
    By Ed Bamba in forum General Woodworking and Power Tools
    Replies: 8
    Last Post: 01-20-2006, 9:18 PM
  2. What size lumber do you WISH you could find?
    By Tom Sontag in forum General Woodworking and Power Tools
    Replies: 5
    Last Post: 06-02-2005, 11:29 AM
  3. Maximizing your table size
    By mike wallis in forum Laser Engraving General Topics
    Replies: 10
    Last Post: 05-30-2005, 1:41 PM
  4. Help! - wiring up a boat trailer and other stuff
    By Fred Voorhees in forum Off Topic Forum
    Replies: 8
    Last Post: 02-27-2005, 8:44 PM
  5. Wire size for new shop sub panel
    By Jim Ketron in forum Off Topic Forum
    Replies: 1
    Last Post: 08-21-2004, 6:58 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •