    Hi Folks - Long time lurker here who as learned much from the collective wisdom on this site.

    This weekend I went to my shop that is remote from my home. Upon arriving I had multiple breakers tripped but not all (5 of 20). After reset everything works except for 1 breaker and I don't see damage to anything. I assume a lighting strike. Curious if there are other ideas.

    The circuit that doesn't work is a 20A 120V circuit with 3 outlets. The first outlet is a GFCI. I replaced the breaker and GFCI to see if that was it and no improvement. No apparent arc/damage in main panel. Upon reset either the GFCI or breaker immediately trips (Breaker fine if GFCI is tripped but breaker will trip when GFCI is reset). After other checks I have found that the hot (Black) wire from the GFCI to the second outlet is the culprit. If unhooked all is good and if I hook it to the GFCI immediate trip of GFCI or breaker. That is with that wire disconnected completely (all 3 wires) from the second outlet. GFCI has power without that connected. I don't capture any continuity between the black wire and Neutral/Ground when measured wire to wire where the second outlet. I do find continuity between Neutral and ground but GFCI/Breaker don't trip if they are attached to GFCI without black wire.

    This is an old barn and we upgraded electrical prior to insulation and putting up interior walls. Curious of what I might find and interested in any thoughts. Maybe a wire staple or drywall screw through the romex?

    Second question - I'll replace the offending wire but not sure I need to pull it out of the wall. This is pole barn construction with the 2 outlets separated by a 4/6 post. 2x4 studs between the posts to add plywood and wall insulation. Do I need to remove cabinets, plywood and insulation and run correctly or could I fish a replacement wire. behind the wall and let it be loose? I have access at the top 10" that I didn't bother putting plywood on. Don't feel that is the way to go but not looking forward to doing it the right way.

  2. #2
    Join Date
    Mar 2003
    Location
    Ontario, Canada
    Posts
    807
    Check for a connection between the neutral and ground - that can cause problems. I assume that you have everything unplugged.

  3. #3
    9 times out of 10 the problems are at the ends & connections and not in the middle of a wire run, so carefully check at both ends, including for nicks where the wire exits the box.

    If you do replace the Romex run, it's OK to run it some other way and not being fastened much is not a big issue IMO if it is protected. I have seen more problems from too much fastening (staples) than from too little.

  4. #4
    Join Date
    Mar 2003
    Location
    SE PA - Central Bucks County
    Posts
    66,882
    While physical damage to that hot conductor could certainly be because of a screw or something like that, it could also be a critter having a snack. Since you have post frame, if you have horizontal girts behind your wall, you should be able to fish a new cable through if you need to, although it might require a few "fishing holes", depending on the distance.
    --

    The most expensive tool is the one you buy "cheaply" and often...

  5. #5
    Join Date
    Nov 2021
    Location
    Columbia MO & Grafton NH
    Posts
    3,567
    Blog Entries
    3
    The multiple tripped breakers does sound like you had a lightning strike. Did you have a storm? Lighting damage created several very puzzling problems for us. The strike at our house made its way to earth via several pathways and on more than one circuit. It fried a 120 volt circuit and the ethernet cable that ran from our house to our daughters house out back. Several parts of the PC were ruined. We think an extension cord left outside that was purged in during the storm was the culprit. It was near a big oak tree that died instantly.

    IMG_2285.jpg
    Lightning Casualty Tree
    Last edited by Maurice Mcmurry; 09-11-2024 at 5:51 PM. Reason: Lightning Casualty Tree Image

  6. #6
    Join Date
    Aug 2021
    Location
    Redmond, OR
    Posts
    679
    Is the breaker a GFI breaker? You can't have 2 GFI's on the same circuit (I mean the breaker + the outlet).

    Pull the incoming wires off the GFI outlet (flip the breaker off first, of course). Put an ohm meter / continuity meter on the neutral and ground wires. They should be open, no continuity between them.

  7. #7
    Join Date
    Jan 2008
    Location
    1.5 hrs north of San Francisco, CA
    Posts
    845
    Very similar symptoms from a mouse that followed a wire "runway" until it could no longer squeeze through the hole in a stud with an additional wire. It chewed the wire until it shorted, melted several feet of the wire's insulation, fried the mouse, and tripped the breaker, which kept tripping.

    That wouldn't explain five breakers. A lightening strike at my brother's hit a ladder hanging horizontally on the outside wall, followed the ladder, jumped through the garage wall to a junction box, down the wall and across his driveway to the ground stake at the entrance meter & breaker box -- blistering the asphalt driveway above its path. That could definitely leave hidden damage to wiring tripping a GFCI.

    My GFCI problems came from rain leaking into an exterior outlet box, unsealed after siding was replaced. All looked normal & there was no continuity across wires. It took a week after each storm to dry enough for the GFCI to
    remain set.

    Hopefully some ideas.

  8. #8
    Join Date
    Jul 2023
    Location
    SW Michigan
    Posts
    5
    A critter is very possible - This alone may be reason to dig deeper to ensure we don't have to take some other mitigation.

  9. #9
    Join Date
    Jul 2023
    Location
    SW Michigan
    Posts
    5
    The breaker is not a GFCI - only the first outlet. Line/Load are set correctly.

    I have not put the meter on the ohm meter on the Neutral and ground at the GFCI yet but did on the next dowstream and did see continuity. That will be something else to check when I get back out there.

  10. #10
    Join Date
    Jul 2023
    Location
    SW Michigan
    Posts
    5
    Thanks for the input guys. Will share as I learn more.

    This is an old barn with a separate meter and wire running directly from the pole to the barn outside. We have had storms but I unfortunately had not been to the shop for 2 weeks. I didn't look hard but didn't see anything odd outside or in the box and like I mentioned, everything else works fine. I'm wondering if a critter or nail on a staple could have reduced the integrity of the insulation and a lighting strike may have energized enough to make it where there is now an arc across the air gap.

    Also wondering about continuity between neutral and ground I think they are bounded in the breaker box but will have to verify.

    "Fun" brain teaser - just wish I had more time to look into it and more importantly to spend in the shop.

  11. #11
    Quote Originally Posted by Michael Schuch View Post
    Is the breaker a GFI breaker? You can't have 2 GFI's on the same circuit (I mean the breaker + the outlet).

    Pull the incoming wires off the GFI outlet (flip the breaker off first, of course). Put an ohm meter / continuity meter on the neutral and ground wires. They should be open, no continuity between them.
    The only reason you should not have two GFCI's is wasting money, not code prohibition on doing so.

  12. #12
    Join Date
    Mar 2003
    Location
    Ontario, Canada
    Posts
    807
    Quote Originally Posted by Ken Rau View Post
    Thanks for the input guys. Will share as I learn more.

    ...

    Also wondering about continuity between neutral and ground I think they are bounded in the breaker box but will have to verify.

    "Fun" brain teaser - just wish I had more time to look into it and more importantly to spend in the shop.
    Yes, the neutral and ground are bonded at the panel - and in your case probably in the barn panel. When you have a sub-panel powered by the house's main panel, the bonding screw is left in the main panel but removed from the sub-panel. Your barn's panel is likely the "main" panel for its circuits.
    Even though the neutral and ground are bonded, a GFCI will detect if there is any current going down the safety ground (or elsewhere) that should be going down the neutral.
    I had a situation where the previous owner wanted a 3-way switch but didn't have the right cable so he used the ground wire as the third conductor (neutral). Only found out about this when installing a GFCI on the circuit that wouldn't power up without tripping. Electrically without the GFCI it worked but illegal.

  13. #13
    Join Date
    Apr 2013
    Location
    Okotoks AB
    Posts
    3,510
    Blog Entries
    1
    I think he's referring to having a GFCI breaker feed a GFCI receptacle. Doing so can cause issues with the electronics in the GFCI devices.

  14. #14
    Join Date
    Dec 2006
    Location
    Toronto Ontario
    Posts
    11,453
    You may have had insulation damage to the line conductor caused by lightning, which in many cases is not detected by a conventional multimeter.

    The insulation resistance should be checked with an insulation resistance meter, set it to apply 500 volts and check the line to ground and neutral.

    Regards, Rod

  15. #15
    Join Date
    Dec 2019
    Location
    The old pueblo in el norte.
    Posts
    2,006
    Quote Originally Posted by Bill Howatt View Post
    so he used the ground wire as the third conductor (neutral)..
    oof. I'd hate to find that out by touching a grounded case.
    ~mike

    happy in my mud hut