    PVC Conduit

    I'm looking to run about 75 ft. of conduit, underground, from one building to another. Looking on local BORG website for conduit and fittings and I see that Southwire makes push on connectors for PVC conduit. No glue involved and they're rated water tight. They call them SIMPush. Has anyone used them or know anything about them?
    Confidence: The feeling you experience before you fully understand the situation

  2. #2
    Haven't seen that but am familiar with Sharkbite.

    Sounds like a good idea (except for cost) as glued fittings in long runs sometimes don't hold.

  3. #3
    Join Date
    Apr 2005
    Location
    Central MA
    Posts
    1,591
    What do you gain? Glue is cheap and easy, and regardless of fittings underground conduit is always considered a wet location per the NEC.

  4. #4
    Join Date
    Apr 2013
    Location
    Okotoks AB
    Posts
    3,499
    Blog Entries
    1
    Properly used, the PVC solvent cement will hold a fitting that will not break loose.

  5. #5
    Join Date
    Sep 2013
    Location
    Wayland, MA
    Posts
    3,667
    They probably work just fine if they're UL listed, as noted watertight is irrelevant underground as the conduit will fill up with condensation if nothing else over a period of time. Every one I've ever taken up has been full of water. An advantage over glue would be if they're reasonably easy to undo, like sharkbites. (not that you want to be undoing the underground connections often, but I just had to do exactly that while replacing a rotted lighted sign pole). Plenty of bad/incomplete glue joints out there, they almost have to be better for mechanical strength and water intrusion from the soil.

  6. #6
    Quote Originally Posted by John Lanciani View Post
    What do you gain? Glue is cheap and easy, and regardless of fittings underground conduit is always considered a wet location per the NEC.
    I ran electric for a hot tub recently, & struggled a bit with fittings going around trees etc.. Couldn't get the fish tape through (ream your pipe ends!) & cut one joint apart as I thought some crud must have got in there. Could have used some push-on fittings...

  7. #7
    Join Date
    May 2008
    Location
    Peshtigo,WI
    Posts
    1,409
    In the video they were easy to disassemble, but they were new. They are rated NEMA4. I'm not an electrician but it sounds impressive.
    Confidence: The feeling you experience before you fully understand the situation

  8. #8
    Join Date
    Feb 2014
    Location
    Lake Gaston, Henrico, NC
    Posts
    9,060
    Use primer first just like you do on PVC waterlines, and not only will it be watertight, but they won't come apart. I comes in clear as well as purple. I think it's mostly just Acetone, but I'm not sure. In any case it's a lot more liquid than water, and you will get it somewhere you don't want it. Wear disposable nitrile gloves.

    You can heat it and bend it if stock fittings won't do what you need. There are even special heating blankets to soften it just right for such bending.

    Best to keep all the hub ends going one way, and remember which way so you can easily get a fish tape through it. A fish tape will hang up going the other way.
    Last edited by Tom M King; 05-19-2023 at 9:05 PM.

  9. #9
    Quote Originally Posted by Jerry Bruette View Post
    ... 75 ft. of conduit, underground, ...
    Quote Originally Posted by roger wiegand View Post
    ... the conduit will fill up with condensation if nothing else over a period of time. Every one I've ever taken up has been full of water. ...
    A tiny diversion in case it helps, but for the reason cited by Mr. Wiegand, I am fairly sure the NEC prohibits the use of NM (romex) and THN/THHN outdoors - even if run in conduit. I believe direct burial rated cable (type UF, IIRC) is called for - even if run in conduit. Perhaps a properly licensed electrician can confirm?

  10. #10
    Join Date
    Jul 2005
    Location
    Eastern Iowa
    Posts
    751
    Quote Originally Posted by Malcolm McLeod View Post
    A tiny diversion in case it helps, but for the reason cited by Mr. Wiegand, I am fairly sure the NEC prohibits the use of NM (romex) and THN/THHN outdoors - even if run in conduit. I believe direct burial rated cable (type UF, IIRC) is called for - even if run in conduit. Perhaps a properly licensed electrician can confirm?
    Just needs to have the letter “w” in the designation. Most THHN is dual rated “THHN/THHWN”
    Comments made here are my own and, according to my children, do not reflect the opinions of any other person... anywhere, anytime.

  11. #11
    Join Date
    Feb 2003
    Location
    Lafayette, IN
    Posts
    4,566
    Quote Originally Posted by Charlie Velasquez View Post
    Just needs to have the letter “w” in the designation. Most THHN is dual rated “THHN/THHWN”
    This. Running a sheathed cable (like direct-bury) in conduit is an exercise in frustration unless you way oversize the conduit. There’s really almost never a good reason to do so.
    Jason

    "Don't get stuck on stupid." --Lt. Gen. Russel Honore


  12. #12
    Join Date
    Feb 2018
    Location
    N CA
    Posts
    1,289
    I can’t see an advantage in a removable fitting in underground. It is a one time thing. Dig your trench, lay out the conduit on boards across the trench, gluing as you go. Do use primer and glue. Let it set up and rest, pull the boards and lower into the trench.

  13. #13
    Join Date
    Mar 2003
    Location
    SE PA - Central Bucks County
    Posts
    65,885
    I kinda agree with Jack relative to this specific application. While a removable fitting used in the shop might be a big benefit for surface mount electrics, for example, because of the inevitable changes over time, for a buried application, it's going in the ground and will therefore be inaccessible. I honestly chose to run UF direct buried between my new shop building and the shed, transitioning from vertical PVC conduit with appropriate fittings on both sides of the run.
    --

    The most expensive tool is the one you buy "cheaply" and often...

  14. #14
    Quote Originally Posted by Charlie Velasquez View Post
    Just needs to have the letter “w” in the designation. Most THHN is dual rated “THHN/THHWN”

    That had me worried, as I run THHN in conduit underground plenty, but I looked and the spools all do say THHN/THWN.

    Re other comments, I don't think the point of the push-on fittings is removability, but ease of use- no glue. Putting everything together above the trench is good, except for tree roots that the conduit must run under.

  15. #15
    Join Date
    Apr 2017
    Location
    Southwest US
    Posts
    1,057
    Quote Originally Posted by Jim Becker View Post
    I kinda agree with Jack relative to this specific application. While a removable fitting used in the shop might be a big benefit for surface mount electrics, for example, because of the inevitable changes over time, for a buried application, it's going in the ground and will therefore be inaccessible. I honestly chose to run UF direct buried between my new shop building and the shed, transitioning from vertical PVC conduit with appropriate fittings on both sides of the run.
    How deep was the run?
    Is there a different depth requirement for a run not in a conduit vs one in conduit?