18A motor on a 20A breaker? 125% of 18A is 22.5A. The cb should be at least this size (22.5A) with wire to match (the next size up is 25A but these can be hard to find for some panels so go preferably with a 30A cb with 10g wire).
18A motor on a 20A breaker? 125% of 18A is 22.5A. The cb should be at least this size (22.5A) with wire to match (the next size up is 25A but these can be hard to find for some panels so go preferably with a 30A cb with 10g wire).
Lee Schierer
USNA '71
Go Navy!
My advice, comments and suggestions are free, but it costs money to run the site. If you found something of value here please give a little something back by becoming a contributor! Please Contribute
Here's my logic on this saw...18A*120V*.70 (efficiency) leaves the motor at about 1500W (under 2hp max) so I assume the motor is rated at 1.5hp or the next usual step down.
The thermal switch was supposed to be delivered March 30, 2 days after ordering, then delivery on or before the 6th, then on or before April 10th....
So I called them and was told it ships from a 3rd party. I let them know how unhappy I was that they did not tell me it was backordered. I have not received any communication from them or the 3rd party vendor. I know of the change delivery dates because I check the website. globalindustrial.com
Update.
So the thermal switch came in and changed out. The saw has been working fine now. Ripping pressure treated 2x without any problems in my shop flooring upgrade.
This would be my tack. I have an 'appliance' cord about 6' long - I guess intended for heavier 120 volt loads like window air conditioners or toaster ovens. I was able to split it so am able to clamp an ammeter around one conductor. The easiest way I know to check the actual amp draw of a machine or other load. If the overload is tripping while the saw is drawing substantially less than its rated amperage, that pretty much indicates your problem.