    sub panel, main breaker question

    I will be installing a 200 amp subpanel in the shop. It will only be supplied by 50-70 amps or so. Can I use the existing 200 amp main breaker rather then buy a new lower amp one? To buy a main switch seems to cost more then a breaker does to fit the same panel location serving as a main disconnect.
    Bill D

  2. #2
    Join Date
    Nov 2021
    Location
    Mid West and North East USA
    Posts
    2,930
    Blog Entries
    2
    For sub panels I have always used a main lug rather than a main breaker panel.
    Best Regards, Maurice

  3. #3
    Join Date
    Mar 2018
    Location
    Piercefield, NY
    Posts
    1,695
    In my new workshop I used a used 100 amp panel from the house. I only had 50 amps feeding it. My electrical inspector told me to backfeed the panel through a 50 amp breaker and just leave the 100 amp breaker at the top in place but not connected. It may be different where you are, though.

  4. #4
    Join Date
    Feb 2014
    Location
    Lake Gaston, Henrico, NC
    Posts
    9,072
    The wire to that panel is protected by the properly sized breaker for the wire on the feed end. The main breaker in that panel just becomes a disconnect.

  5. #5
    Join Date
    Jul 2005
    Location
    Eastern Iowa
    Posts
    751
    Yes, you can.
    Done all the time.

    Circuit breakers need to protect the wiring.
    The wires feeding your sub will be protected by the breaker in your main.
    The individual circuits in your ….

    Never mind, I type too slowly.
    I see Tom has already said this.
    Comments made here are my own and, according to my children, do not reflect the opinions of any other person... anywhere, anytime.

  6. #6
    Join Date
    Mar 2006
    Location
    SoCal
    Posts
    22,513
    Blog Entries
    1
    Answers will be geographical. Consult the NEC; I believe we are currently complying with the 2022 edition in SoCal. These things are very easy to comply with once you know what version your state, county, and town are following. Deviations can result in insurance companies not paying if things go sideways.
    "A hen is only an egg's way of making another egg".


    – Samuel Butler

  7. #7
    Join Date
    Mar 2003
    Location
    SE PA - Central Bucks County
    Posts
    65,888
    It will work fine as a disconnect (and it's nice you'll have one at the shop end...my shop disconnect is up at the house where the service splits), but I agree with Glenn that the local jurisdiction is where the final word lands.
    --

    The most expensive tool is the one you buy "cheaply" and often...

  8. #8
    Join Date
    Sep 2016
    Location
    Modesto, CA, USA
    Posts
    10,005
    Logically a over sized breaker is as good or better then a switch rated for even more amps before it fails. But logic does not always apply to rules.
    Bill D

  9. #9
    Join Date
    Nov 2021
    Location
    Mid West and North East USA
    Posts
    2,930
    Blog Entries
    2
    Looking at the code, turns out mine with main lugs is in violation because it is in a detached building. It was inspected and passed. That is not surprising because our town voted in favor of not requiring the city engineer to have a degree in engineering.
    Last edited by Maurice Mcmurry; 02-24-2023 at 8:48 PM.
    Best Regards, Maurice

  10. #10
    Join Date
    Jul 2005
    Location
    Eastern Iowa
    Posts
    751
    Quote Originally Posted by Maurice Mcmurry View Post
    Looking at the code, turns out mine with main lugs is in violation because it is in a detached building. It was inspected and passed. That is not surprising because our town voted in favor of not requiring the city engineer to have a degree in engineering.
    Depends on year code you're area was using. The disconnect rule was started in the 2020 edition. Prior to that it was the rule of six. Must be able to disconnect power with no more than six throws.
    Comments made here are my own and, according to my children, do not reflect the opinions of any other person... anywhere, anytime.

  11. #11
    Join Date
    Mar 2003
    Location
    SE PA - Central Bucks County
    Posts
    65,888
    Yes, many jurisdictions remain on the 2017 (?) version of the NEC for their reference...mine included.
    --

    The most expensive tool is the one you buy "cheaply" and often...

  12. #12
    Join Date
    Nov 2021
    Location
    Mid West and North East USA
    Posts
    2,930
    Blog Entries
    2
    Quote Originally Posted by Charlie Velasquez View Post
    Depends on year code you're area was using. The disconnect rule was started in the 2020 edition. Prior to that it was the rule of six. Must be able to disconnect power with no more than six throws.
    OK! It was 2010 and I have 6 breakers. Good to know. Thank you Charlie.
    Best Regards, Maurice

  13. #13
    Join Date
    Jul 2005
    Location
    Eastern Iowa
    Posts
    751
    Quote Originally Posted by Maurice Mcmurry View Post
    OK! It was 2010 and I have 6 breakers. Good to know. Thank you Charlie.
    Just as an aside, if you had had more than six breakers, and included several 120 volt circuits, you could bring it into compliance by getting approved handle ties and linking a couple of 120’s (or going to 240 volt breakers, one circuit on each leg).

    You would maintain the over-current protection but have to put up with both circuits going off if either circuit trips a breaker.
    Comments made here are my own and, according to my children, do not reflect the opinions of any other person... anywhere, anytime.

  14. #14
    Join Date
    Sep 2016
    Location
    Modesto, CA, USA
    Posts
    10,005
    Quote Originally Posted by Zachary Hoyt View Post
    In my new workshop I used a used 100 amp panel from the house. I only had 50 amps feeding it. My electrical inspector told me to backfeed the panel through a 50 amp breaker and just leave the 100 amp breaker at the top in place but not connected. It may be different where you are, though.
    That seems like a poor idea. In an emergerncy a fire fighter would assume the top centered breaker, not in line with the lower ones was the main breaker.
    Everyone knows the top most breaker is the main breaker without reading the old fadded labels..
    Bill D

  15. #15
    Join Date
    Nov 2021
    Location
    Mid West and North East USA
    Posts
    2,930
    Blog Entries
    2
    Quote Originally Posted by Bill Dufour View Post
    That seems like a poor idea. In an emergerncy a fire fighter would assume the top centered breaker, not in line with the lower ones was the main breaker.
    Everyone knows the top most breaker is the main breaker without reading the old fadded labels..
    Bill D
    I have used convertible panels. They come with "permanent" labels. Relying on labels will keep you compliant in most cases. In an emergency, in smoke, with a BA pack on, expecting a fire fighter to read the labels is asking a lot. I am wishing I had not gotten by with the rule of 6 back in 2010.

    I have been trying to help my father in law sort our a failed inspection in Boston for over 30 years. A big, single function disconnect right inside the front door is required. We eventually received permission to use a shunt rather than rewire the entire main service. That was over 20 years ago. Eventually that work will have to be done. Now we are going to have to replace the entire service, under ground, out to the street, upgrading from 200 amps to 400 to meet the current requirements. I sure wish F.I.L. and his electrician had gotten this sorted out in 1987.
    Last edited by Maurice Mcmurry; 03-02-2023 at 8:27 AM. Reason: ,
    Best Regards, Maurice