    Mini split installation for a house

    I've been waiting for months for someone who is supposedly going to install a mini split, and today when he returned my last call he said that he would be getting a quote to me soon, but it would be higher than the $2-3k range he had guessed at an earlier time. He doesn't design the systems, just installs them. I'm thinking more seriously about doing it myself instead. The plan is to install it on the ground floor, which is open, 15' wide and 31 feet long for the kitchen and living room. There is also an added guest bedroom on one side but I am not worried about that for now. The whole house has closed cell spray foam now that the addition got done, so we're pretty well sealed.

    We are planning to use a mini split for heat in spring and fall, but when the temperature outside goes below freezing we'll use the wood stove, which is working fine and seems like it would be able to heat the whole house even in cold spells. So far we've only had to have a fire a few hours a day, even with lows in the mid 20s. The mini split would have to be able to survive to -40 but we wouldn't be using it when it's cold. I'm looking at some kits that say they are DIY, like Mr Cool, which I have heard folks on here speak highly of. I'm also wondering how hard it would be for a non-HVAC person like me to buy or rent a vacuum pump and learn to do the lines myself. It seems like there are a lot more mini-split options if I was able to do that. I'll be grateful for any advice.

  2. #2
    Join Date
    Jan 2017
    Location
    MT
    Posts
    699
    I bought two units a couple of years ago and kept putting off professional installation until I had them both ready to fire up. I wanted to take advantage of a professional install to maintain the 7 year warranty. I realized I was already 2 years into the warranty period with no benefit of the units. Bit the bullet earlier this summer and installed the one in the shop by myself. It was pretty easy. If you are looking at a single-zone system then it is pretty straight-forward. I don't know anything about multiple-zone systems but can't imagine it would be that complicated. The units I purchased are Daikin they came pre-charged and I believe the charge is good up to about 25 ft. of line set if I remember correctly. If going beyond the pre-charged length you would have to add refrigerant which complicates things, I believe.

    Anyway, I got the pump and gages for less than $200 (the same set is not $146 on Amazon). I also bought an eccentric flaring tool and a set of crow's feet so I could use my standard torque wrench. I can share the components if you are interested.

    There are others on here with more experience and hopefully they will chime in.
    Regards,

    Kris

  3. #3
    Join Date
    Mar 2018
    Location
    Piercefield, NY
    Posts
    1,695
    Thank you, that's great to know that it worked for you. Good for you for getting it done. The deeper I dig into this the more I'm confused about which "DIY" kits require a pump and such, and how to tell them from the ones that don't.

  4. #4
    Join Date
    Feb 2014
    Location
    Lake Gaston, Henrico, NC
    Posts
    9,076
    You need a vacuum pump to evacuate the lines, I expect even with the precharged units, but I have no experience with them, so really don't know.

    The system operates under high pressure, so the flare fittings are critical. Even pros have trouble with them leaking. Use these: https://www.amazon.com/dp/B07M81FBF9...v_ov_lig_dp_it

    and torque the fittings properly with a flare nut crows foot on a torque wrench.

    Even with a vacuum pump to evacuate the system, and a pressure gauge to see if it's holding vacuum, I still don't want to put refrigerant in a system without pressure testing it first with Nitrogen. No refrigerant should be released into the atmosphere, and guesswork has a high probability of that as a result.

    It takes a grand or two to get set up good to work on HVAC systems, and you can easily spend way more.

    I do business with, and recommend: Supplyhouse.com and Trutechtools.com

  5. #5
    Join Date
    Mar 2014
    Location
    Iowa USA
    Posts
    4,484
    As a guy who worked in the commercial HVAC/R field and then after being retired for a few years and installed my own Mini Split HP. My son who is still in the business recommends Mitsubishi as that is what his commercial Co used and had next to zero issues. Made in Japan all mini splits are not the same quality.

    #1 Buy a good flaring tool, I used Rol Aire as I used for many, many years to make a leakproof flare on the first try and they make the flare with a segmented flaring cone above the flaring bar and then also polishes it, the tool is expensive!

    #2 Since the flares are subject to cold and hot use either Leak Lock or Blue Loctite behind the flare nut and on the threads... it stops the loosing of the flare.

    #3 Use a torque wrench, I never did but I have been doing this for over 30 years.

    #4. Leak check first with either dry nitrogen or refrigerant that does not require recovery, I used a tank of R134a for pressure. Think, if you pull a vacuum before pressure checking, your just sucking in air and moisture in from any leak. Vacuum leak checking is only at 14.7 psig, think why?

    #5 Use a good vacuum pump to pull down to at least 500 microns.

    #6 Open those service valves slowly and you do have gauges for R410a? Recheck those fittings again.

    #7 I did have a minor leak on the liquid line I needed to repair, but all is fine now. Works down to say -12 or so heating very low energy costs! This is going to be my 4th heating season.
    Last edited by Bill George; 10-28-2022 at 7:29 PM.
    Retired Guy- Central Iowa.HVAC/R , Cloudray Galvo Fiber , -Windows 10

  6. #6
    Join Date
    Nov 2021
    Location
    Mid West and North East USA
    Posts
    2,933
    Blog Entries
    2
    If you can make stock line sets work you can skip DIY flaring and avoid potential problems. Pioneer caters to DIY but there is a "Certified Installer" line on the warrantee form. Pulling a vacuum can also be bypassed with a line flushing kit. I think a deep vacuum that holds for a day or two is the best leak test.
    Last edited by Maurice Mcmurry; 10-28-2022 at 7:38 PM.
    Best Regards, Maurice

  7. #7
    Join Date
    Mar 2003
    Location
    SE PA - Central Bucks County
    Posts
    65,892
    Mr Cool DIY systems can be installed without a vacuum pump as the line-sets are pre charged. The current range is broad and multi-air handler units are available which is typically what you want for a home. I'll be using one of these units in my new shop building, but likely with just a single air handler since it's an open space. (Buying mine through Costco)

    Do note that many mini splits available today can handle outside temps down to as much as -5º F. Check the specifications if that's important to you.
    --

    The most expensive tool is the one you buy "cheaply" and often...

  8. #8
    Join Date
    Mar 2018
    Location
    Piercefield, NY
    Posts
    1,695
    Thank you all for the advice. Jim Becker, I think that the house here is more analogous to a typical workshop in some ways, since it's an open rectangular area that we want to heat and cool, and the bedrooms can take care of themselves at least for now. It's not important to me to be able to use a mini-split at -5, as I imagine the stove will keep up with that if we keep it stoked steadily, but I haven't found much information about what temps the outside unit can withstand without a problem, and it can get pretty cold here at times.

  9. #9
    Join Date
    Mar 2010
    Location
    Somewhere in the Land of Lincoln
    Posts
    2,564
    I put two Mr Cool mini splits in my shop this summer. Home Depot was the best price and almost immediate availability. I think they were in store in three days. Mine weren't DIY as far as the lines weren't pre-charged. I had my local HVAC guy assist and when we were finished it was about $500 for his labor. He recommended Mr Cool. The price is definitely competitive. Ther were $1,100+ each. They worked great as cooling units. I have radiant floor heat for cold weather. They also have ducted mini splits as I understand it. I can look at the manual and see what temperature range it lists.

  10. #10
    Join Date
    Mar 2014
    Location
    Iowa USA
    Posts
    4,484
    For a system that runs 400 plus psig on the high side, leak testing should be done at pressures 300 psig or more. Dry nitrogen is best because it is stable temperature wise and much cheaper and legal compared to refrigerant.

    Removing all the air and then down into a deep vacuum means you pressure checked at 15 (14.7) psig Which is better?


    BTW my Mitsubishi Hi HP works and heats down to -12 and the compressor, outside and inside fan motors all modulate speeds according to the load.
    Last edited by Bill George; 10-29-2022 at 8:24 AM.
    Retired Guy- Central Iowa.HVAC/R , Cloudray Galvo Fiber , -Windows 10

  11. #11
    Join Date
    Feb 2014
    Location
    Lake Gaston, Henrico, NC
    Posts
    9,076
    There are cheap nitrogen regulators, but I bought a good one. Buying a filled 40 cu. ft. tank cost $140. Refilling it costs a few cents less than $25. Now that I own the rig, I can pressure test as much as I want to, and purge the inside of the lines if I want to braze. Total rig cost cheaper than one service call around here.

    This is the regulator I bought, and it works like a charm. You can buy cheaper ones, but the reviews don't sound so great.

    https://www.trutechtools.com/victor-...r-cga-580.html
    Last edited by Tom M King; 10-29-2022 at 8:34 AM.

  12. #12
    Join Date
    Mar 2003
    Location
    SE PA - Central Bucks County
    Posts
    65,892
    Quote Originally Posted by Zachary Hoyt View Post
    Thank you all for the advice. Jim Becker, I think that the house here is more analogous to a typical workshop in some ways, since it's an open rectangular area that we want to heat and cool, and the bedrooms can take care of themselves at least for now. It's not important to me to be able to use a mini-split at -5, as I imagine the stove will keep up with that if we keep it stoked steadily, but I haven't found much information about what temps the outside unit can withstand without a problem, and it can get pretty cold here at times.
    I think you'll be pleased with the performance. The temperature floor should be in a unit's specifications, but having the woodstove is certainly a boon for when things are blowin' up there in the sticks. With the house being somewhat open as you describe, the simpler units should work fine. A 24K BTU unit covers up to about 1000 square feet, and with good insulation and infiltration sealing, things can be pretty comfortable. If you are doing through-floor vents so your woodstove heat can circulate upstairs, you will likely get similar benefit with the split when using it. Going with the mini split also gives you AC, so that's a win-win, IMHO. You may not need it as often as farther south, but it will cover "those times" when things get sticky and that's unfortunately very likely to be more frequently going into the future.
    --

    The most expensive tool is the one you buy "cheaply" and often...

  13. #13
    Join Date
    Nov 2007
    Location
    Rockingham, Virginia
    Posts
    338
    Put a Mitsubishi mini-spit into the garage part of our lower level where I have my shop - perhaps 1400 SF. I did not do it. I had the local pros who maintain my heat pump do it. It was put in under almost ideal conditions - close to the 400 A circuit boxes, good access for the lines, good place for the condenser, etc. Based upon my previous HVAC experience, which is significant, this is not a job for anyone other than certified techs, so this is something I may disagree with others about. We have a saying, a bad install can ruin a great system or the HVAC is only as good as the installer. Have to be honest - it was not cheap - around 6K, but it has a 10 year warranty, is as quiet as a church mouse, and the work outside through the brick looks terrific, plus even with my experience, this was not something I was going to do when you see the need for double lines, wiring, and the condensate line. These guys had done many of these and they did a super job and they told me if I wanted another inside unit, the outside unit could carry it. My wife was a bit grouchy about it, but part of the upper floor will be warmer (the front of the house is 13’ higher that the back where the second driveway and what used to be a 4 car garage is - it is a shop now) and she is fond of that thought. Critical thing for me is humidity control in the summer (has a drying function) so I can dry lacquer and varnish and apply finishes and work more safely in the winter.

  14. #14
    Join Date
    Feb 2018
    Location
    N CA
    Posts
    1,290
    Bill, with respect, I was reluctant to challenge your experience. Why, well because I don’t have it I’m not sure how other manuf will handle it but Fujitsu, while an excellent line had hard and fast rules on any type of dope on the unit connections.
    Last edited by Jack Frederick; 10-30-2022 at 10:07 AM.

  15. #15
    Join Date
    Nov 2009
    Location
    Alaska
    Posts
    711
    Quote Originally Posted by Zachary Hoyt View Post
    I've been waiting for months for someone who is supposedly going to install a mini split, and today when he returned my last call he said that he would be getting a quote to me soon, but it would be higher than the $2-3k range he had guessed at an earlier time. He doesn't design the systems, just installs them. I'm thinking more seriously about doing it myself instead. The plan is to install it on the ground floor, which is open, 15' wide and 31 feet long for the kitchen and living room. There is also an added guest bedroom on one side but I am not worried about that for now. The whole house has closed cell spray foam now that the addition got done, so we're pretty well sealed.

    We are planning to use a mini split for heat in spring and fall, but when the temperature outside goes below freezing we'll use the wood stove, which is working fine and seems like it would be able to heat the whole house even in cold spells. So far we've only had to have a fire a few hours a day, even with lows in the mid 20s. The mini split would have to be able to survive to -40 but we wouldn't be using it when it's cold. I'm looking at some kits that say they are DIY, like Mr Cool, which I have heard folks on here speak highly of. I'm also wondering how hard it would be for a non-HVAC person like me to buy or rent a vacuum pump and learn to do the lines myself. It seems like there are a lot more mini-split options if I was able to do that. I'll be grateful for any advice.
    I have no experience or brilliant suggestions to offer, but you might find a couple episodes on YouTube helpful. I watched the entire series, and learned quite a bit (I am a self taught framer/builder). He installed a split system in a spec house he was building. He did not go into the minutia, but you'll at minimum, get to see the system installed and know what you are getting into if you DIY. Episode #34 is where they start installing duct work in the crawl space. 107 they start the split system install. https://www.youtube.com/playlist?lis...JWmBPeX1hGhyLi