    Breaker Question

    H Folks,

    I am replacing a hot tub. The old setup had a 60 amp 220 breaker at the main panel wired with 8 guage wire to an outside disconnect that did have a 40 amp 220 gfci, then on to the tub.

    The new tub calls for a 50 amp breaker at the main, then a 30 amp double pole gfci and and a 20 amp single pole gfci breaker.


    I installed the two gfci at the disconnect. Is it necessary to swap out the 60 amp for a 50 amp in the main panel?

    thanks,

    Stevo

  2. #2
    Join Date
    Jun 2022
    Location
    Tracy, CA
    Posts
    649
    I would probably say that you can still run 60A breaker at your main panel as long as the electrical line from the main panel to the hot tub sub-panel is spec'd to support 60A. I'm assuming 8 awg would still be fine here. The sub-panel breakers for double-pole 30A and single-pole 20A should have adequate wire after them (i.e. 10awg).

    The callout for 50A at the main is likely minimum recommended/required.

  3. #3
    Join Date
    Mar 2003
    Location
    SE PA - Central Bucks County
    Posts
    66,016
    I agree with Aaron. The supply to the hot tub subpanel can be heavier than the 50a required which is a minimum. No need to change it. The two circuits at the hot tub end in that subpanel take things from there.
    --

    The most expensive tool is the one you buy "cheaply" and often...

  4. #4
    Join Date
    Sep 2016
    Location
    Modesto, CA, USA
    Posts
    10,105
    #8 wire is undersized for 60 amps. I have no idea if a hottub is considered a hot service area ,like an attic; and needs further ampacity derating?
    Bill D.

    #8 NM-b is 40 amps. THHN is 50 amps

    https://www.cerrowire.com/products/r...pacity-charts/
    Last edited by Bill Dufour; 10-15-2022 at 2:58 PM.

  5. #5
    I agree with Bill Dufour above- the current set up does not meet code, and the proposed set up does not either.

    In practice, the risk is low IMO, since any issue at the tub would trip the lower rated breaker, and a problem with the wire going to the tub disconnect would most likely be a direct short i.e. conduit cut by digging, that would trip the panel breaker anyway.

    If it was my personal situation, I might leave it, but as a contractor, I would not.

  6. #6
    Join Date
    Apr 2013
    Location
    Okotoks AB
    Posts
    3,501
    Blog Entries
    1
    Yep, #8 is too small for a 60A circuit. That's on whoever did the initial installation, but you need to change out that breaker because it's a fire hazard as it is now.

  7. #7
    Quote Originally Posted by Frank Pratt View Post
    Yep, #8 is too small for a 60A circuit. That's on whoever did the initial installation, but you need to change out that breaker because it's a fire hazard as it is now.
    Actually the wire would need to be changed to use a 50 amp breaker...

  8. #8
    Quote Originally Posted by Cameron Wood View Post
    Actually the wire would need to be changed to use a 50 amp breaker...

    That depends on the conductors currently in use, as said already NM sheathed cable is sized in the 60°C column of table 310.15(B)(16) so 8 AWG is 40A, but if THHN/THWN 8 AWG is 50A, THWN is required for wet locations.

  9. #9
    Quote Originally Posted by Rollie Meyers View Post
    That depends on the conductors currently in use, as said already NM sheathed cable is sized in the 60°C column of table 310.15(B)(16) so 8 AWG is 40A, but if THHN/THWN 8 AWG is 50A, THWN is required for wet locations.

    You're right. If the wiring is modern, it's probably THHN, so that would work.