    Help with 3-phase jointer wiring

    I recently acquired a Griggio PF430 jointer. It is three phase and I'll be powering it with a VFD. The gentleman that I purchased it from said that besides the three phase power it also used 110V, perhaps for a starter? He wasn't sure of the details because his electrician took care of the hookup. I've attached a picture of the terminal block for the power. I think the one screw broke off when it was removed from service? Does anyone have suggestions on the wiring?

    Thanks,
    Dave

    PXL_20210208_022022691.jpgPXL_20210131_012233851.jpg

  2. #2
    have a 500 and it starts in Delta then switches to Wye I think. Not sure my terminal block would be the same in case anyone has worked on the motor and use a Roto so the stakes go up. If you post a wiring diagram for it there are a number of smart people here. These were the wires on it but it was in a commercial shop 3 phase so no concerns other than direction of travel.

    P1940316A.jpgP1940299A.jpg
    Last edited by Warren Lake; 02-07-2021 at 10:38 PM.

  3. #3
    Well, I deleted my post trying to edit it. Here goes.

    I assumed the OP's picture was of the motor. At second look it's not. What are the terminals marked? L1, L2, L3, and N?


    Post pictures or any other information you have.
    Motor nameplate
    Machine nameplate
    Wiring skematic
    Control cabinet

    Delta/ Wye motors:
    Always have at least six leads (3 wires for each set of windings)
    Always have a start circuit, usually time controlled. This would include an extra contactor and the motor starter.

    Warren,
    How many wires go to your motor?

  4. #4
    Join Date
    May 2017
    Location
    Little River, Australia
    Posts
    42
    If your motor is delta connected, and the right voltage rating, the VFD goes directly to the motor windings and all of the control (starting/stoping/speed etc) is via the VFD.

  5. #5
    Stan I didnt have the cover off on the motor so not sure. Im not 100 percent sure its the original motor but likely,. Cover has been off one end where the fan is and see it was damaged so its been out before.

    P1510592A.jpg

  6. #6
    Join Date
    May 2013
    Location
    Northern Virginia
    Posts
    1,370
    Blog Entries
    3
    Quote Originally Posted by Warren Lake View Post
    Stan I didnt have the cover off on the motor so not sure. Im not 100 percent sure its the original motor but likely,. Cover has been off one end where the fan is and see it was damaged so its been out before.

    P1510592A.jpg
    That V 550 stamped there is a concern. Was the original owner running it on 240v 3ph?

    The vfd is connected directly to the motor, bypassing the contactors and terminal block.
    Last edited by Jared Sankovich; 02-08-2021 at 8:13 AM.

  7. #7
    Join Date
    Jul 2007
    Location
    Inkerman, Ontario, Canada
    Posts
    1,406
    Jared, Warren is in Canada; 550, 575 and 600 volts are common 3phase industrial motor voltages here.

    Quote Originally Posted by Jared Sankovich View Post
    That V 550 stamped there is a concern. Was the original owner running it on 240v 3ph?

    The vfd is connected directly to the motor, bypassing the contactors and terminal block.

  8. #8
    Join Date
    Mar 2003
    Location
    Central PA
    Posts
    83
    Thanks for all the replies. The terminals in the picture that I posted are in a box on the back of the machine. I've attached a picture of the motor and the control panel.

    The jointer is setup for 220V three-phase operation but I don't know if it is delta or wye.

    PXL_20210124_194541218.jpgPXL_20210125_193124350.jpg

  9. #9
    Join Date
    May 2013
    Location
    Northern Virginia
    Posts
    1,370
    Blog Entries
    3
    Quote Originally Posted by Mark Hennebury View Post
    Jared, Warren is in Canada; 550, 575 and 600 volts are common 3phase industrial motor voltages here.
    Sorry for adding confusion. It would help if I paid more attention to who made the post..lol.

  10. #10
    Join Date
    Nov 2019
    Location
    Boulder Creek, Ca
    Posts
    10
    Your motor is Delta only. For Wye Delta you need three contactors and a timer to switch between Wye and Delta. You only have one contactor, one overload and a three wire motor. Your machine is too small for a Wye Delta starting circuit.

  11. #11
    Join Date
    Sep 2016
    Location
    Modesto, CA, USA
    Posts
    10,005
    Green with a yellow stripe should be ground. Confirm with a meter to the machine bare metal, like a screwhead near the terminal block.
    If it has 120 volt the white wire may be the incoming neutral,. All the other colors will be the three phases. Confirm by checking ohms between each. They should all be the same. Neutral will be different .
    Since it is broken you can wire nut the blue and white wire together if there is room.
    I am not really sure if European neutral is the same meaning as USA. I think they use only three phase.
    Bil lD

    https://www.allaboutcircuits.com/tex...g-color-codes/
    Last edited by Bill Dufour; 02-08-2021 at 5:23 PM.

  12. #12
    Join Date
    Mar 2003
    Location
    Central PA
    Posts
    83
    Ok, I think the three black/brown (is one of them grey?) wires are the three phases for the motor. The blue is likely neutral and the green is ground. So do I wire directly from the VFD to the motor like Jared mentioned above?

    -Dave

  13. #13
    Join Date
    May 2013
    Location
    Northern Virginia
    Posts
    1,370
    Blog Entries
    3
    Quote Originally Posted by David Miller View Post
    Ok, I think the three black/brown (is one of them grey?) wires are the three phases for the motor. The blue is likely neutral and the green is ground. So do I wire directly from the VFD to the motor like Jared mentioned above?

    -Dave
    The vfd must be connected directly to the motor. Any disconnect under power will smoke the vfd. You will bypass all the contactors and run the original start/run and stop switch to the low voltage control terminals on the vfd.

    You may need to program the vfd for 3 wire control as well.

    What model vfd?

  14. #14
    Join Date
    Dec 2006
    Location
    Toronto Ontario
    Posts
    11,277
    Quote Originally Posted by David Miller View Post
    Thanks for all the replies. The terminals in the picture that I posted are in a box on the back of the machine. I've attached a picture of the motor and the control panel.

    The jointer is setup for 220V three-phase operation but I don't know if it is delta or wye.

    PXL_20210124_194541218.jpgPXL_20210125_193124350.jpg
    Looking in the motor connection box will tell you.

    Delta will have three incoming leads with 2 motor wires per lead.

    Wye will have 3 incoming leads with one motor wire per lead and 3 wires that are connected together and to nothing else...Rod

  15. #15
    Dave,
    On low voltage your motor is delta wound. It's on the name plate. I don't see why it would matter unless it's programming in your VFD.

    Bohdan is correct. If using a VFD, nothing can be between it and the motor. Start/ Stop must be done through the VFD.

    Back to your question about the 120 volt, you need to find out why you have 4 wires landed on the termination block (we don't count ground). Post the schematic if you have it, also pictures of the electrical controls (the box with all the components inside, not the Start/ Stop).

    Warren,
    Is that a 950 volt motor? I understand the 550 volt winding. That would be a first for me. Is that a standard voltage somewhere? I don't know what the big black box is in your picture. Could you post a picture looking down on it?