    Quote Originally Posted by Curt Harms View Post
    Then why did AC win over DC? I thought the primary reason is that AC can be sent over long distances, DC can't. Or is that only true at low voltages?
    High voltage is the key to reducing losses in transmission. Back in the day, there was no easy, economical way to boost DC to a higher voltage for transmission & than back down to a safer voltage for consumer use. AC used simple transformers to do that. That's why AC won out in for utility distribution.

  2. #47
    Quote Originally Posted by Warren Lake View Post
    Here is my post. Out of my scope to understand it but heard the buzzing loud and clear, likely more in tune to it from an audio past. Power talk makes me remember seeing a gaggle of birds come down to land on huge towers and lines and the big bang that blew out all the street lights for miles. Roasted a lot of birds. That was a day I wish I had a dash camera then I saw them come down to land and by the time the bang happened would have been too much beside me to capture it.


    Attachment 451474 Attachment 451475
    In the second picture, the wire that looks like it burned the pole is a ground. It goes to the Lighting Arrestor, H1 is tied to the LA's primary. If there is a lighting strike on the primary, the LA bleeds it to ground before it gets to the transformer. It's sort of a big spark plug. Why it flashed to the pole is anyone's guess.

  3. #48
    Join Date
    Feb 2010
    Location
    Mt Pleasant SC
    Posts
    721
    2A9253EF-C1D7-4CDD-95E2-71905DA7A0AC.jpgAttachment 451507
    Quote Originally Posted by Doug Dawson View Post
    On a 20amp circuit with 12ga wire with a nominal 120V, it’s not unusual to see an 8 or 9 percent voltage drop at the receptacle when running a 15amp load, which would put the voltage at the receptacle to roughly 110V, which is what the device would see. Even 5 percent is common in new construction. Something to think about. Machines have to be able to handle this.
    I tested a 20 amp circuit, 12 gauge wire, about 50 feet using the third/last receptacle in the run.
    120.2 volts with no load
    added an 18 amp load
    116.5 with 18 amps.
    About a 3 percent voltage drop.
    Attached Images Attached Images
    Last edited by Bruce King; 02-07-2021 at 1:00 PM.

  4. #49
    Join Date
    Feb 2008
    Location
    E TN, near Knoxville
    Posts
    12,298
    Quote Originally Posted by Randy Heinemann View Post
    One thing . . . I was told by Jet (JPW) Support, when I was having a bit of trouble with my jointer, that I should check the actual voltage at the outlet because Jet's requirements were to have a full 240 volts at the outlet. Mine was OK, but it's my understanding that, for various reasons, the actual voltage at the outlet could be less than 240 V. I'm no expert on electrical issues but that seemed to be important to the Jet tech support guy.
    Many single phase AC motors will run on somewhat lower voltage. The potential problem is, they will then draw more current to generate the same output power. A little of this is usually not a problem unless the voltage is so low that the current it draws is so high the feed wires and motor windings also overheat. (Heated wires have higher resistance which further reduces the voltage making things worse.) At some point the motor is damaged. This can happen from a voltage drop from a wire that is too long.

    Many years ago my brother-in-law burned up three motors by running 110v through long wires to the pump in his spring. Instead of running a larger wire, he solved the problem by supplying 220 volts and switching the new motor to run on 220v instead of 110, cutting the current draw in half. He never burned up another pump motor.

    I don't know how this applied to 3-phase motors driven by a VFD.

    JKJ

  5. #50
    Quote Originally Posted by Bruce King View Post
    2A9253EF-C1D7-4CDD-95E2-71905DA7A0AC.jpgAttachment 451507

    I tested a 20 amp circuit, 12 gauge wire, about 50 feet using the third/last receptacle in the run.
    120.2 volts with no load
    added an 18 amp load
    116.5 with 18 amps.
    About a 3 percent voltage drop.
    It would be interesting to run that same test on the closest outlet - with the shortest wire run - and see what drop you get.

    Mike
    Go into the world and do well. But more importantly, go into the world and do good.

  6. #51
    Join Date
    Feb 2010
    Location
    Mt Pleasant SC
    Posts
    721
    Quote Originally Posted by Mike Henderson View Post
    It would be interesting to run that same test on the closest outlet - with the shortest wire run - and see what drop you get.
    Mike
    With good connections it’s all going to be pretty close to this calculator. The length of the wire is not always known if it’s behind drywall.
    https://www.calculator.net/voltage-d...s=15&x=63&y=27

  7. #52
    Quote Originally Posted by Bruce King View Post
    2A9253EF-C1D7-4CDD-95E2-71905DA7A0AC.jpgAttachment 451507

    I tested a 20 amp circuit, 12 gauge wire, about 50 feet using the third/last receptacle in the run.
    120.2 volts with no load
    added an 18 amp load
    116.5 with 18 amps.
    About a 3 percent voltage drop.
    That’s not a load tester.

    Over the past five years I’ve checked out over a hundred homes with mine, and the voltage drop is typically in the 3 to 7 percent range with a 15amp load, with some variation outside of that. That’s an observed reality.

    Most of this was while looking for a new home that I would be satisfied with, given that I’m very particular about some stuff (that might touch on electrical, which would inevitably require some modifications.) Finally found one, BTW.

  8. #53
    Join Date
    Mar 2003
    Location
    SE PA - Central Bucks County
    Posts
    65,879
    I had to put a buck/boost transformer on my slider because for a time period the voltage from the street was either too high or too low...I don't recall at this point and it was tripping the circuitry that monitored for that. The saw would just stop working until I did the labor to get inside and reset things. My point here is that some tools are designed to support a very specific range of voltage fluctuation and if the "line steps over the line"...you get no sawdust. Sam Blasco helped me diagnose that back when it happened. The power company later found a degrading transformer feeding our property and rectified it.
    --

    The most expensive tool is the one you buy "cheaply" and often...

  9. #54
    Join Date
    Feb 2010
    Location
    Mt Pleasant SC
    Posts
    721
    Quote Originally Posted by Doug Dawson View Post
    That’s not a load tester.

    Over the past five years I’ve checked out over a hundred homes with mine, and the voltage drop is typically in the 3 to 7 percent range with a 15amp load, with some variation outside of that. That’s an observed reality.

    Most of this was while looking for a new home that I would be satisfied with, given that I’m very particular about some stuff (that might touch on electrical, which would inevitably require some modifications.) Finally found one, BTW.
    That’s a current meter. I also had a load and a volt meter. Your load tester combines all that in one tool. My measurements and technique is perfect and agrees with published data. Your load tester is probably using a higher load than the 15 amps you posted or the cable length is very long or loose connections.
    Last edited by Bruce King; 02-07-2021 at 4:02 PM.

  10. #55
    Quote Originally Posted by Curt Harms View Post
    Then why did AC win over DC? I thought the primary reason is that AC can be sent over long distances, DC can't. Or is that only true at low voltages?
    The major reason back then was that AC voltage could be stepped up and stepped down with a simple transformer. So you could step up the voltage to a very high level for long distance transmission and then step it down to a voltage for local transmission and finally to residential voltage.

    You couldn't do that with DC back in the early days so DC had to be carried at the user voltage level which implied very high currents and high losses.

    Today, we have the technology to convert between AC and DC at a reasonable cost and efficiency so DC can be used for long distance transmission at very high voltage levels.

    Mike
    Go into the world and do well. But more importantly, go into the world and do good.

  11. #56
    Quote Originally Posted by Bruce King View Post
    That’s a current meter. I also had a load and a volt meter. Your load tester combines all that in one tool. My measurements and technique is perfect and agrees with published data. Your load tester is probably using a higher load than the 15 amps you posted or the cable length is very long or loose connections.
    I have both the Extech and the Ideal SureTest, and they’re consistent with one another. (The Ideal is good for bootleg grounds, but I prefer the Extech because it plays nice with AFCI.) It sounds like you’ve got a lot of connections there, and a few data points. I have many more data points, across a broad range of structures. You seem to be indicting the whole of the residential wiring trade, across many decades. :^)

    Anyway, the point is that what appears at the receptacle is not always what you think it should be.

  12. #57
    Join Date
    Aug 2017
    Location
    Arlington, TX
    Posts
    452
    Quote Originally Posted by Curt Harms View Post
    Then why did AC win over DC? I thought the primary reason is that AC can be sent over long distances, DC can't. Or is that only true at low voltages?
    AC or DC, very high voltage (and proportionally less current) always has an advantage in long distance power transmission lines. The lower the voltage, the higher the current (and vice versa), and resistance losses in transmission lines are proportional to current, not voltage.

    The early advantages of AC over DC had to do with the difficulty (= cost), in that era, of efficiently changing DC voltages, compared to using a simple transformer to change AC voltage. Since DC voltage could not easily be raised for efficient transmission voltages (or reduced for safe consumption at the end users), transmitting it over long distances was cost-prohibitive.

    Modern electronics have drastically reduced the cost of changing DC voltages at very high power levels, though only enough to make long distance DC transmission more cost effective overall. It is still cheaper to change AC voltages with a transformer, especially at high power, but when the combined conversion and transmission costs are considered, DC now wins for very high power and/or very long distance applications.

    As an illustration of the relentless pursuit of efficiency, high power generator armatures are spun in hydrogen atmospheres, to reduce mechanical resistance losses. Helium, while advantageously inert, would have twice the viscosity of hydrogen. A vacuum is not practical because of the lack of an insulating atmosphere (electrons at the potential in these generators can fly around rather easily in a vacuum.) So they just have to make sure there is no oxygen mixed in with the hydrogen. At those power levels, even small percentage losses are still big losses, and seemingly extreme measures are cost-effective.

    -- Andy - Arlington TX

  13. #58
    Join Date
    Feb 2016
    Location
    NE Iowa
    Posts
    1,245
    Quote Originally Posted by Andy D Jones View Post
    As an illustration of the relentless pursuit of efficiency, high power generator armatures are spun in hydrogen atmospheres, to reduce mechanical resistance losses. Helium, while advantageously inert, would have twice the viscosity of hydrogen. A vacuum is not practical because of the lack of an insulating atmosphere (electrons at the potential in these generators can fly around rather easily in a vacuum.) So they just have to make sure there is no oxygen mixed in with the hydrogen. At those power levels, even small percentage losses are still big losses, and seemingly extreme measures are cost-effective.

    -- Andy - Arlington TX
    Hydrogen atmosphere is used in large dynamos to cool the windings, not to insulate them. There is no practical difference in the electrical insulating effect of hydrogen vs air vs vacuum - the hydrogen being only .025% more dielectric than a vacuum. Hydrogen is, however, a significantly more efficient thermal medium than either air (or Helium) - easier to move with fans, and much better thermal conductivity. That's why it's used to cool dynamos.

  14. #59
    Join Date
    Nov 2009
    Location
    Ellsworth, Maine
    Posts
    1,809
    Quote Originally Posted by Steve Demuth View Post
    Hydrogen atmosphere is used in large dynamos to cool the windings, not to insulate them. There is no practical difference in the electrical insulating effect of hydrogen vs air vs vacuum - the hydrogen being only .025% more dielectric than a vacuum. Hydrogen is, however, a significantly more efficient thermal medium than either air (or Helium) - easier to move with fans, and much better thermal conductivity. That's why it's used to cool dynamos.

    You both are correct BTW!! Andy is not necessarily correct about the insulating properties of hydrogen but one of the reasons it's used is definitely because of the viscosity of the gas not just the efficiency of it's thermal conductivity. There is much less drag in hydrogen than in air therefore Andy is correct in that there is much less mechanical resistance! But Steve is also correct in that hydrogen is much better at dissipating heat.

  15. #60
    Join Date
    Feb 2003
    Location
    Griswold Connecticut
    Posts
    6,933
    Quote Originally Posted by jeff friedman View Post
    All - I have seen some cabinet saws advertising 220 v 3 hp and others 240 v up. Do I need to wire my shop differently or does both get treated the same?
    Jeff
    I don't know if you're still keeping track of your post, but after 4 pages of academic discussion the simple answer is, yes, treat them the same, as long as you live in the continental US.