    Adding A Switch To The Neutral Line Of A Magnetic Starter

    I recently installed a 60 amp sub panel with several dedicated 240 volt circuits in my garage.

    One of the dedicated circuits is a 30 amp line for my air compressor!
    The compressor is wired to an old AB magnetic starter that has a 120volt coil & uses the old style overload heaters. On these old AB starters (and a lot of newer ones) the overload relay is normally connected to the neutral wire, If the relay is overloaded it breaks the neutral connection to the coil & this results in disconnecting both of the 240 volt power lines.

    I know that switching the neutral is a no no & a code violation with normal wiring, But I believe there's a special provision for motor starters that disconnect all power when the neutral wire is disconnected?

    Assuming that there is some sort of special provision for motor starters, Would adding a switch to the control circuit of a magnetic starter be allowed?

    Basically what I would like to do is replace my garage's main light switch with a double pole switch & connect the compressor's neutral line to the other side of the light switch. This would prevent the compressor from running after I leave the garage for the day, "Providing I remember to turn the lights off"


    Doug
    Attached Images Attached Images

  2. #2
    Join Date
    Sep 2016
    Location
    Modesto, CA, USA
    Posts
    10,044
    Not sure why you can't switch the control wiring so the hot is switched instead of neutral. The contactor will switch both hots off so the neutral has no where to go anyway. Ground should never be switched, ever.
    Bill D

  3. #3
    Join Date
    May 2018
    Location
    Lancaster, Ohio
    Posts
    1,375
    My recommendation would be to series the wiring for the existing pressure switch thru a new two pole 24vac relay with a 24 vac ,< 40 va transformer wired to lights. When lights are on the relay is enabled and the air compressor can run. Never good to have multiple circuits thru a switch. Someone will kill power to lights and Not realize power is still on at the switch

  4. #4
    Join Date
    Apr 2013
    Location
    Okotoks AB
    Posts
    3,501
    Blog Entries
    1
    Having the OL relay disconnect the neutral is standard practice and is a matter of internal wiring at the starter. The OL relay is the only contact that should be between the neutral and the coil. All other control devices are to switch the line conductor that connects to the coil.

    Switching the neutral to the compressor outlet with a wall switch is quite another. What you would be doing is creating the appearance of a disconnect switch that actually leaves the the line conductor hot. Major hazard.
    Last edited by Frank Pratt; 09-03-2020 at 9:46 AM.

  5. #5
    Join Date
    Jan 2011
    Location
    Southeast MI.
    Posts
    374
    Quote Originally Posted by Bill Dufour View Post
    Not sure why you can't switch the control wiring so the hot is switched instead of neutral.
    I guess that could be done, But as "Frank Pratt" stated
    Quote Originally Posted by Frank Pratt View Post
    Having the OL relay disconnect the neutral is standard practice and is a matter of internal wiring at the starter.
    To be able to have the light switch next to the side door of my garage also control the compressor's starter control circuit through the hot lead, I would need to run a separate line through the conduit which is about a 45 foot run.

    Doug

  6. #6
    I don't understand where the 120 volt control power comes from. It looks like it's tapped off of L1. I would just refeed the control circuit from the lighting circuit.

  7. #7
    Join Date
    Jan 2011
    Location
    Southeast MI.
    Posts
    374
    Quote Originally Posted by Frank Pratt View Post
    Switching the neutral to the compressor outlet with a wall switch is quite another.
    Just to clarify things, I'm not intending to switch a neutral line that goes to an outlet!
    The main circuit to my compressor is a 30 amp 240 volt line (Red/Black/& Green 10ga. wire) Being the AB Starter has a 120V coil, I also ran a 14ga. White wire for the neutral wire needed for the 120V coil. It's this 14ga. neutral line that goes to the starters overload relay that I was thinking of adding the DPST light switch to.

    Quote Originally Posted by Frank Pratt View Post
    The OL relay is the only contact that should be between the neutral and the coil. All other control devices are to switch the line conductor that connects to the coil.
    Ok it sounds like I may have my pressure switch & coil wired wrong?
    I used a old 16ga. power cord Black & White wire to connect both the 120V hot & neutral wires to the pressure switch "Line" side & then I ran a second piece of the power cord from the "Motor" side to the starters coil!

    Doug
    Attached Images Attached Images

  8. #8
    Join Date
    Jan 2011
    Location
    Southeast MI.
    Posts
    374
    Quote Originally Posted by Stan Coryell View Post
    I don't understand where the 120 volt control power comes from. It looks like it's tapped off of L1.
    Yeah the hot line is connected to L1 & goes into a 4amp in-line fuse before heading to the pressure switch.
    IMG_6692.JPG
    The neutral wire comes into the overload relay & then goes to the pressure switch.

    Quote Originally Posted by Stan Coryell View Post
    I would just refeed the control circuit from the lighting circuit.
    I thought about that, But wondered if having the control wiring on another circuit would create a code problem!

    Doug

  9. #9
    Join Date
    Apr 2013
    Location
    Okotoks AB
    Posts
    3,501
    Blog Entries
    1
    If the compressor is on a 30A circuit, then you should be fusing the control circuit if the wiring extends beyond the actual compressor starter. As it is now, you have 16 ga. wire on a 30A breaker. A short circuit in part of the coil winding (not unheard of) could cause catastrophic overheating of the control wires.

    Code rules differ, so check with your AHJ.

  10. #10
    Join Date
    Jan 2011
    Location
    Southeast MI.
    Posts
    374
    Quote Originally Posted by Frank Pratt View Post
    If the compressor is on a 30A circuit, then you should be fusing the control circuit if the wiring extends beyond the actual compressor starter.
    As mentioned in my previous post, The hot lead for the control circuit coming off of the L1 side of the starter is fused with a 4amp in-line fuse.

    Doug

  11. #11
    Join Date
    Jan 2011
    Location
    Southeast MI.
    Posts
    374
    Quote Originally Posted by Frank Pratt View Post
    As it is now, you have 16 ga. wire on a 30A breaker. A short circuit in part of the coil winding (not unheard of) could cause catastrophic overheating of the control wires.
    I just realized that I posted an older pic. of the starter in my original post!
    In that pic. I hadn't installed the fuse holder & 4amp fuse yet.

    Sorry for any confusion!

    Doug

  12. #12
    No, problem. The control circuit can come from anywhere. I would just make a note in the starter box.

  13. #13
    I got a DPDT contactor with a 120V coil. I wired the 240 volts to the tool through the contactor and put a sensor on the 120V line. So when I go into the shop, the sensor detects me and turns on the 240V to my compressor. I put a switch across the sensor so that I can bypass the sensor when I want to.

    The sensor is one of those that are used to turn lights on when you walk into a room. That way, when you walk out of the shop, the sensor will time out and the voltage will be turned off to your compressor.

    A DPST contactor would work but I think most of what you'll find will be DPDT.

    Mike
    Go into the world and do well. But more importantly, go into the world and do good.

  14. #14
    Join Date
    Dec 2006
    Location
    Toronto Ontario
    Posts
    11,284
    Switching the neutral is fine if it doesn’t extend beyond the starter enclosure.

    If the starter is factory approved without a control fuse, do not add one as modifying the starter negates the approval for it.....Rod

  15. #15
    Join Date
    Jan 2011
    Location
    Southeast MI.
    Posts
    374
    Quote Originally Posted by Rod Sheridan View Post
    Switching the neutral is fine if it doesn’t extend beyond the starter enclosure.
    Thanks!
    That makes things a little easier, And it will work with what I had already planed on doing.

    Quote Originally Posted by Rod Sheridan View Post
    If the starter is factory approved without a control fuse, do not add one as modifying the starter negates the approval for it.....Rod
    I'm not sure if I understand this correctly!
    Are you saying that the in-line 4amp fuse I added to the coil's feed connection that's tapped at the L1 terminal should be removed?

    Doug
    Last edited by Doug Walls; 09-06-2020 at 11:48 AM. Reason: Correction