    Grounding ethernet

    I am installing a camera outside the door to my shop, due partly to lots of break-ins in my area over the past year. The camera will be POE (power over ethernet) and I have a POE switch and other necessary equipment. I have done this before, so no questions about the install, except that I need to ground the ethernet cable in case of lightning strike. I lost some equipment to ungrounded ethernet cabling a couple of years back in a different location and I don't want to have it happen again.

    I have some (Ubiquiti) ethernet surge protectors but there is no real information about how best to ground them. They do not plug in to anything other than the ethernet cable and are therefore not connected to the house's grounding system. There is a screw for attaching a ground wire, which is easy enough, but I don't know where to attach the other end of this wire.

    Should I attach the ground wire to my house's electrical system by, for example, opening up an outlet and grounding the ethernet surge protector to the ground wire in the outlet box? If not, where should this wire go?

    Thanks.


  2. #2
    Join Date
    Sep 2009
    Location
    Medina Ohio
    Posts
    4,534
    I would get a ground rod and drive it in and ground to that all my phone and cable grounds to a ground rod below my service entrance

  3. #3
    Join Date
    Jul 2007
    Location
    NE OH
    Posts
    2,628
    First, know that e-net surge protector will be a little help in the case a direct strike to the camera, or even a close strike. You would be better protected if you went with a wireless camera with a beefy surge protector on the power source to the camera. It will still be destroyed in the case of a direct or close strike, but at least won't necessarily take out all your other network stuff as it is isolated by the wireless link.

    If you need/want to go wired, then your best grounding strategy would be a ground rod near the surge protector. If you connect to the house wiring, you will simply be channeling the surge energy through your house wiring where it can blow up other stuff in the case of a near strike. Still, it would be better than nothing and would provide some protection in the case of a strike that is nearby but not really close.
    --I had my patience tested. I'm negative--

  4. #4
    Join Date
    Mar 2003
    Location
    SE PA - Central Bucks County
    Posts
    65,885
    You need to determine if "grounding"/surge suppression is going to interfere with the PoE before you take that step...I've been out of the business for a couple of years and don't recall grounding ever come up for Ethernet, at least in the commercial environments I was catering to.
    --

    The most expensive tool is the one you buy "cheaply" and often...

  5. #5
    Join Date
    Feb 2008
    Location
    NE Connecticut
    Posts
    695
    Quote Originally Posted by Jim Becker View Post
    You need to determine if "grounding"/surge suppression is going to interfere with the PoE before you take that step...I've been out of the business for a couple of years and don't recall grounding ever come up for Ethernet, at least in the commercial environments I was catering to.
    The surge supressor I have is just a pass-through and is made for POE devices. As I said, I've had a problem with this before and lost a switch and a router to it.

    Quote Originally Posted by Paul F Franklin View Post
    First, know that e-net surge protector will be a little help in the case a direct strike to the camera, or even a close strike. You would be better protected if you went with a wireless camera with a beefy surge protector on the power source to the camera. It will still be destroyed in the case of a direct or close strike, but at least won't necessarily take out all your other network stuff as it is isolated by the wireless link.
    I know that a direct strike to the camera is a difficult thing to mitigate but I would like as much protection as possible for my switch and the things attached to it in case of some transient voltage. The camera will be attached to the house, so I don't think it will be more likely to be hit by lightning than my flood lights, for example. For various reasons I am going to stick with the POE camera instead of wireless, so grounding of some kind will be a necessity.

    I guess a ground rod might be the best solution, although it will have to wait until spring.

    Thanks for the advice.


  6. #6
    Join Date
    Aug 2005
    Location
    Midwest
    Posts
    2,043
    Maybe you can put the Ethernet cabling in metal conduit extending close to the camera (or possibly mount the camera directlly to a metal junction box) and connect the other end of the conduit to a separate dedicated ground rod. This way you might give a lightning strike an easy path to ground that doesn't include your house or equipment.

  7. #7
    Join Date
    Nov 2015
    Location
    Pepperell Ma.
    Posts
    93
    I apologize if this isn’t directly related to the info you seek. I am an electrician for a municipality in Mass. We have approximately 250 exterior cameras on the towns 15-20 buildings we maintain. Of those at least 100-150 are digital (as opposed to analog). They are just wired directly from the switch on cat5-cat6 cables (depending on when they were installed). Some of the more recent have a fusable link installed at the camera where the cat6 cable plugs into the link, then a patch cable, exits out the other side and snaps into the camera. In the 2 years I have been working on the cameras we have not had any losses due to lightning. I think the brand name for the usable links is Ditek.

  8. #8
    Join Date
    Feb 2013
    Location
    Tippecanoe County, IN
    Posts
    836
    My experience with Ditek is like Arthur's, I've had limited but good results using their equipment. There's a lot of good information on their website but you do need to register there to access much of it.

    DO NOT ever connect anything to an isolated ground rod, that is, one that is not bonded to your grounding system. It's unsafe for both you and your equipment.
    Beranek's Law:

    It has been remarked that if one selects his own components, builds his own enclosure, and is convinced he has made a wise choice of design, then his own loudspeaker sounds better to him than does anyone else's loudspeaker. In this case, the frequency response of the loudspeaker seems to play only a minor part in forming a person's opinion.
    L.L. Beranek, Acoustics (McGraw-Hill, New York, 1954), p.208.

  9. #9
    Quote Originally Posted by David L Morse View Post
    DO NOT ever connect anything to an isolated ground rod, that is, one that is not bonded to your grounding system. It's unsafe for both you and your equipment.
    +1. Don't go installing ground rods...


    Quote Originally Posted by Brian W Evans View Post
    I lost some equipment to ungrounded ethernet cabling a couple of years back in a different location
    How do you know that was the cause?

  10. #10
    Join Date
    Jul 2007
    Location
    NE OH
    Posts
    2,628
    DO NOT ever connect anything to an isolated ground rod, that is, one that is not bonded to your grounding system. It's unsafe for both you and your equipment.
    All he is connecting to the ground rod in this case is the return side of spark gaps. There is absolutely nothing wrong or unsafe with connecting to a separate ground rod.
    --I had my patience tested. I'm negative--

  11. #11
    Join Date
    Feb 2013
    Location
    Tippecanoe County, IN
    Posts
    836
    Quote Originally Posted by Paul F Franklin View Post
    All he is connecting to the ground rod in this case is the return side of spark gaps. There is absolutely nothing wrong or unsafe with connecting to a separate ground rod.
    I see, this is a spark gap device only. So he will still need some kind of protection at the other end of the cable.
    Beranek's Law:

    It has been remarked that if one selects his own components, builds his own enclosure, and is convinced he has made a wise choice of design, then his own loudspeaker sounds better to him than does anyone else's loudspeaker. In this case, the frequency response of the loudspeaker seems to play only a minor part in forming a person's opinion.
    L.L. Beranek, Acoustics (McGraw-Hill, New York, 1954), p.208.

  12. #12
    Looking at the picture, it sure looks like the metal shells are grounded to the grounding tab?

  13. #13
    Join Date
    Feb 2008
    Location
    NE Connecticut
    Posts
    695
    Quote Originally Posted by Dan Friedrichs View Post
    How do you know that was the cause?
    I never really did any serious digging into the cause, but both components - switch and router - never came back on after a power outage. I had a good surge protector for the power cords and my other equipment, connected to the same surge protector but not to ethernet, was fine. The maintenance guy told me there was some lightning damage in other units in the same building, so my assumption is that whatever killed my equipment came through ethernet cables.

    It may be that the whole surge protector thing is overkill for my application but they're cheap and I figured I would rather be safe than sorry.

    I'm clearly not an electrician, so thanks for all the advice.


  14. #14
    Join Date
    Jan 2016
    Location
    Seattle, WA
    Posts
    152
    I would be really surprised if the lightening strike took out equipment directly via the Ethernet cable and it wasn’t the AC system in that location that took a surge. Ethernet is mostly DC signal cable and runs at such a small gauge that a surge would more likely burn it than actually be transmitted. You also can’t ground Ethernet like an AC signal - they run on different concepts of grounding planes. If you were to ground *just* the PoE pair (the ground side) to ‘ground’ you would at best have a marginal DC signal to your remote device (aka, it would work unreliable). At worst it would just not power the remote device.

    If you were to somehow couple the signal pairs of the Ethernet cable to ground then nothing would work.

    The ubiquity surge protector might work - they’re a reputable brand. However IMO the ‘data line’ surge protectors built into power strips are basically junk.