Thread: Quick circuit breaker question for sparkies

Hybrid View

Previous Post Previous Post   Next Post Next Post
  1. #1
    Join Date
    Jan 2010
    Location
    Tampa Bay, FL
    Posts
    3,895

    Quick circuit breaker question for sparkies

    This is a picture of two sets of two circuit breakers for one of my 5-ton HVAC units. It's the top to breakers on the left and right that I'm referring to.
    Left Circuit Breaker Panel - Cropped.jpg

    I'm assuming the unit is 230V, and the two top breakers are tandem, so my understanding is that it's a 230V 45amp load for the left condenser, and the same for the right Air Handler, but there is no plastic handle tie connector between the two of them. Does this appear to be true, and should I be picking up a handle tie like this one to tie them back together:
    https://www.amazon.com/Eaton-cutler-...y&sr=8-1-fkmr0
    - After I ask a stranger if I can pet their dog and they say yes, I like to respond, "I'll keep that in mind" and walk off
    - It's above my pay grade. Mongo only pawn in game of life.

  2. #2
    Join Date
    Feb 2003
    Location
    Lafayette, IN
    Posts
    4,563
    Can't see the pic, but at 5 tons, the air handler blower motor could still be 120V, maybe it's a separate circuit from the controls. But, if the blower motor is indeed 240V, then by all means the circuit breaker feeding it should be a bonded double.
    Jason

    "Don't get stuck on stupid." --Lt. Gen. Russel Honore


  3. #3
    Join Date
    Feb 2014
    Location
    Lake Gaston, Henrico, NC
    Posts
    8,973
    Take the cover off the panel, and look to see if each breaker has a black wire on it, or if one is black, and the other is White, or Red.

  4. #4
    Join Date
    Mar 2003
    Location
    SE PA - Central Bucks County
    Posts
    65,675
    Could be two circuits...one for the interior unit and one for the exterior unit. That's how both of my HVAC systems are setup.
    --

    The most expensive tool is the one you buy "cheaply" and often...

  5. #5
    Join Date
    Sep 2016
    Location
    Modesto, CA, USA
    Posts
    9,876
    For five tons I would guess 25amps at 240V. I would guess your compressor is 120V? But I would expect any compressor over 1.5 tons to be 240 volt.
    That breaker could be a double with only one handle I suppose.
    BTW does your utility offer a discount if they install a load controller on your ac? At 5 tons I would expect a 10-20 dollars a month off your bill.
    Bill D

  6. #6
    Join Date
    Jun 2015
    Location
    Sacramento, CA
    Posts
    2,005
    Yea ya really gotta get the cover off that panel to know/see for sure. Be careful though man, make sure you have that main off before you touch ANYTHING. In fact, Id suggest you turn that main off before you take that cover off too. Better safe than sorry. And keep in mind even with the main off, unless youve called the electrical company and had them come out and kill the main to your house, that main is still live, exposed and will most definitely shock you out of this world if you happen to come in contact with it.
    If at first you don't succeed, redefine success!

  7. #7
    Join Date
    Jan 2010
    Location
    Tampa Bay, FL
    Posts
    3,895
    Quote Originally Posted by Ben Rivel View Post
    Yea ya really gotta get the cover off that panel to know/see for sure. Be careful though man, make sure you have that main off before you touch ANYTHING. In fact, Id suggest you turn that main off before you take that cover off too. Better safe than sorry. And keep in mind even with the main off, unless youve called the electrical company and had them come out and kill the main to your house, that main is still live, exposed and will most definitely shock you out of this world if you happen to come in contact with it.
    Not gonna open the cover. I don’t like electricity that much.

    Here’s a closeup of one of the breaker pairs. I think these must be just missing that bar. The second breaker says “Common trip” on it. No other breakers say that. Does that indicate that it’s a tandem breaker with the top one, 230V pair?

    4C26E1EB-32EE-42B9-ADF7-3BE2B6377CBE.jpg
    - After I ask a stranger if I can pet their dog and they say yes, I like to respond, "I'll keep that in mind" and walk off
    - It's above my pay grade. Mongo only pawn in game of life.

  8. #8
    Join Date
    Jun 2015
    Location
    Sacramento, CA
    Posts
    2,005
    Quote Originally Posted by Alan Lightstone View Post
    Not gonna open the cover. I don’t like electricity that much.

    Here’s a closeup of one of the breaker pairs. I think these must be just missing that bar. The second breaker says “Common trip” on it. No other breakers say that. Does that indicate that it’s a tandem breaker with the top one, 230V pair?

    4C26E1EB-32EE-42B9-ADF7-3BE2B6377CBE.jpg
    Page 17 here: LINK
    And sold pretty much everywhere: LINK
    Looks to me like it can be used as either a 120V or 240V breaker.
    If at first you don't succeed, redefine success!

  9. #9
    Join Date
    Feb 2014
    Location
    Lake Gaston, Henrico, NC
    Posts
    8,973
    It's really no big deal taking the cover off, and no need to stick your hands in there. Hold the cover in place with one hand, as you back out the last screw, then take both hands, and pull the cover straight off. Look to see wire colors connected to those breakers.

    To put cover back on, have one or two screws in one hand, put cover back in place, holding it with one hand after it's in place, and replace the screws. It can only go back on in one position, since it has to fit around the breakers like you see it, so it's not really a balancing act.

  10. #10
    Join Date
    Nov 2003
    Location
    Central North Carolina
    Posts
    1,830
    In what is known as a split phase system (your house 240/120 volt power) you should never use two single pole breakers. Always use a two pole breaker that has the tie bar connecting the two handles together. You cannot (when I last checked) buy this bar separately from any breaker manufacturer. You need to buy the correct two pole breaker with the handles tied together. This is a safety device that forces both breakers off should there be an overload on just one of them. Without this, one breaker could stay on and even though the 240 volt appliance is no longer running, it would still have power being supplied to it through the one un-tripped breaker. It could prove deadly for someone who thinks the power is off because the appliance doesn't operate and begins servicing it. The same is true for three phase systems where all three breakers need the trip bar across all three handles, so that an overload on any one phase will turn all three circuit breakers off. It's a code requirement for a reason.

    Charley

  11. #11
    Quote Originally Posted by Charles Lent View Post
    In what is known as a split phase system (your house 240/120 volt power) you should never use two single pole breakers. Always use a two pole breaker that has the tie bar connecting the two handles together. You cannot (when I last checked) buy this bar separately from any breaker manufacturer. You need to buy the correct two pole breaker with the handles tied together. This is a safety device that forces both breakers off should there be an overload on just one of them. Without this, one breaker could stay on and even though the 240 volt appliance is no longer running, it would still have power being supplied to it through the one un-tripped breaker. It could prove deadly for someone who thinks the power is off because the appliance doesn't operate and begins servicing it. The same is true for three phase systems where all three breakers need the trip bar across all three handles, so that an overload on any one phase will turn all three circuit breakers off. It's a code requirement for a reason.

    Charley
    ^+1^

    Top/Left x2 sure look like they need to have a mechanical interlock. It's dangerous as-is. Alan, If your're not going to open it, get an electrician to verify/replace.

  12. #12
    Join Date
    Feb 2008
    Location
    E TN, near Knoxville
    Posts
    12,298
    Quote Originally Posted by Alan Lightstone View Post
    Not gonna open the cover. I don’t like electricity that much.
    Get your brother-in-law to open it. Seriously, you are wise to stay on the outside of the box if you lack experience. Ask around - you probably know someone who can not only open the box but has enough knowledge and experience to analyze what's inside and determine if you need to change anything. It's a 5-minute task. You can watch and learn a bit.

  13. #13
    Join Date
    Feb 2008
    Location
    E TN, near Knoxville
    Posts
    12,298
    Quote Originally Posted by Alan Lightstone View Post
    ... I think these must be just missing that bar. The second breaker says “Common trip” on it. ... Does that indicate that it’s a tandem breaker with the top one, 230V pair?

    I also wondered if someone simply removed the gang connection bar. A common trip breaker has two halves for 220v single phase and three sections for three phase power. I have never seen a common trip breaker without a mechanical connection on the handles.

    I understood common trip breakers would internally trip both sides on a fault on one side and the connection bar is there to insure both sides are disconnected when manually shut off. But I admit to having never seen one with the connection bar removed nor have I tried removing a connection bar and trying turning off one side at a time to see what that does. You certainly wouldn't want to be able to turn off one side and not the other. A quick test of yours with a meter or circuit tester could confirm if it was unsafe. (Test should be done by someone with knowledge and experience.)

    JKJ