Thread: Voltage too hot in shop...

  1. #1
    Join Date
    Dec 2018
    Location
    Pennsburg, PA
    Posts
    39

    Voltage too hot in shop...

    I知 not sure if anyone on here is good with the electrical side of things (i know I知 not). My shop is on an old wild leg delta system. I measure 250 phase to phase. I own a lot of euro machines that are rated for 220. Low and behold i just blew a transformer on my older sliding table saw due to what I知 assuming is the high voltage (unless it was a fluke). I called the power company out and the tech said that they only adjust if the voltage is out of their +/-10% tolerance from 240V. So they would tolerate up to 264V (wow).
    I知 about to purchase a 230V wide belt sander and i would really not like to damage this machine. Does anyone have experience with this topic? Will a 230V machine tolerate this extra 20 volts? That would be right on the cusp of +10%.
    Thanks in advance for any tips or recommendations.
    Jack

  2. #2
    Join Date
    Dec 2006
    Location
    Toronto Ontario
    Posts
    11,236
    Equipment normally is designed for +/- 10% of rated.

    Your 230 volt machine would be beyond rating at 250 volts.

    If it were me I would use either an auto or a buck transformer to reduce the line voltage.....Rod

  3. #3
    Join Date
    Mar 2003
    Location
    SE PA - Central Bucks County
    Posts
    65,638
    Buck/boost transformer on the individual tools. I had to do that for my SCM/Minimax Slider because I was getting voltage too low to my shop from the street more often than was pleasant. They are pretty adaptable and you can set things up to match what your actual need is. Please note....I'm not three phase here, but the principle still applies I believe)
    --

    The most expensive tool is the one you buy "cheaply" and often...

  4. #4
    Join Date
    Dec 2018
    Location
    Pennsburg, PA
    Posts
    39
    Thanks for the replies. So i guess i would need to find a 250V primary to 220V secondary 3 phase buck transformer? Seems like a needle in a haystack kind of scenario. Or would 240 to 220 work the same?
    Jack

  5. #5
    "Autotransformer" (as Rod said). It has multiple taps so you just pick the one you want for the voltage you've got.

  6. #6
    Join Date
    Feb 2003
    Location
    Griswold Connecticut
    Posts
    6,923
    Jack

    "220" is a "nominal" voltage value. You should be reading 230-240 across the service coming into the main breaker panel. I'm usually at ~ 238vac.
    A higher voltage would actually be better than a lower voltage, as long as it's within reason. The lower the voltage, the higher the current, for a given load, and that increase in current is generally what is responsible for damaging motors.
    Unless you have a NIST traceable, calibrated meter, it's kind of a guess as to exactly what the voltage actually is. The accuracy, or inaccuracy of your meter, could account for some of the error you're seeing.
    Addy Protocol
    I've been calibrating the instrumentation that monitors the electrical grid voltage in the north east, and frequency for 30+ years. Month in and month out.
    I think you're probably fine.
    "The first thing you need to know, will likely be the last thing you learn." (Unknown)

  7. #7
    Join Date
    Feb 2011
    Location
    Central WI
    Posts
    5,666
    When you refer to wild leg delta, do you have one leg that reads 208 to ground as in a three phase 240 delta arrangement? If that is the case, the 208 leg should not feed the transformer in your machine. Even though it reads 240+ pole to pole with any other leg, I've had small machine transformers muck up so I avoid that leg on anything but the motor. Dave

  8. #8
    Join Date
    Sep 2006
    Location
    Deep South
    Posts
    3,970
    240VAC has been the standard across the USA for at least 40 years. 220 is just an unfortunate name holdover from days long gone. So is 110. If you buy just about any new equipment, it is designed to work at 240 +/- 10%.

  9. #9
    Join Date
    Dec 2006
    Location
    Toronto Ontario
    Posts
    11,236
    Quote Originally Posted by Art Mann View Post
    240VAC has been the standard across the USA for at least 40 years. 220 is just an unfortunate name holdover from days long gone. So is 110. If you buy just about any new equipment, it is designed to work at 240 +/- 10%.
    Hi Art, the OP has European machinery, the older machines were designed for the 220/380 volt 3 phase system, modern European machines are designed for 230/400 Volts.

    In this case his machinery is actually designed for 220 volts...................Regards, Rod.

  10. #10
    Search "Transformer" on McMaster-Carr and fill out the info you need. I don't know what kind of power draw your system needs, but (if I read this table right), item number 70525K75 will do it. It can do 245V to 222V at 5,000 Va which should cover a 5 Hp motor.* It's $134.

    *I am not an electrician, please verify these numbers It APPEARS that it's a 1:1.1 transformer, so at 250 V in you should see 226 V out.

  11. #11
    Join Date
    Nov 2016
    Location
    Itapevi, SP - Brazil
    Posts
    672

    Are you sure on the 10% tolerance?

    Quote Originally Posted by Jack Hovanec View Post
    I知 not sure if anyone on here is good with the electrical side of things (i know I知 not). My shop is on an old wild leg delta system. I measure 250 phase to phase. I own a lot of euro machines that are rated for 220. Low and behold i just blew a transformer on my older sliding table saw due to what I知 assuming is the high voltage (unless it was a fluke). I called the power company out and the tech said that they only adjust if the voltage is out of their +/-10% tolerance from 240V. So they would tolerate up to 264V (wow).
    I知 about to purchase a 230V wide belt sander and i would really not like to damage this machine. Does anyone have experience with this topic? Will a 230V machine tolerate this extra 20 volts? That would be right on the cusp of +10%.
    Thanks in advance for any tips or recommendations.
    Jack
    Please do not take me wrong but 10% tolerance looks me too high. Unfortunately ANSI site requires money to download the specific norm (it looks odd) but most of Europe and Brazil specify 5% tolerance for domestic mains.

    Anyway electric motors are usually specified to support much higher variation. Again, according to Brazilian norms motors must have 15% tolerance in the voltage input - I don't think it will lower in the US.

    Electronic stuff usually are at 10% minimum tolerance.

  12. #12
    Join Date
    Sep 2006
    Location
    Deep South
    Posts
    3,970
    I tend to forget that this forum in international!

    Quote Originally Posted by Rod Sheridan View Post
    Hi Art, the OP has European machinery, the older machines were designed for the 220/380 volt 3 phase system, modern European machines are designed for 230/400 Volts.

    In this case his machinery is actually designed for 220 volts...................Regards, Rod.

  13. #13
    Join Date
    Dec 2006
    Location
    Toronto Ontario
    Posts
    11,236
    Quote Originally Posted by Art Mann View Post
    I tend to forget that this forum in international!
    LOL.................Yup, there are a lot of us "foreigners" on here.

    I was working in Virginia a week ago and really enjoyed the weather there, much nicer than at home......Rod.