    Do cheap natural gas leak sniffers work?

    I just put in a new gas fireplace burner and log set. My family says there is a smell. The manual says that the logs will offgas until after a burn in period of about 6 hours. I’m running the logs on low and they have run for 10 or 12 hours. And, I don’t think the smell is natural gas.

    so, my wife wants me to buy a cheap natural gas sniffer on amazon. My question is whether they work.

  2. #2
    Quote Originally Posted by Roger Feeley View Post
    I just put in a new gas fireplace burner and log set. My family says there is a smell. The manual says that the logs will offgas until after a burn in period of about 6 hours. I’m running the logs on low and they have run for 10 or 12 hours. And, I don’t think the smell is natural gas.

    so, my wife wants me to buy a cheap natural gas sniffer on amazon. My question is whether they work.
    Sometimes, the smell can be caused by an improperly adjusted air valve on the burner. When everything else fails, read the manual

  3. #3
    Join Date
    Apr 2013
    Location
    Kansas City
    Posts
    2,671
    Is it vented? Some of them are not.

  4. #4
    Join Date
    Sep 2006
    Location
    Deep South
    Posts
    3,970
    Yes, natural gas leak detectors work.

  5. #5
    Natural gas detectors work, but, like everything else the good ones are expensive and the cheap ones are not something to bet your life on and that is exactly what you might be doing. I would suggest you turn the gas off at the source, or their should be a shutoff valve in the back of the fireplace. Cut it off and leave it off for a day or so and see if the smell goes away. Turn it back on and if the smell returns you got a leak that needs to be addressed. By any chance is it plumbed with CSST {corrugated stainless steel tubing}??? That is usually wrapped in yellow plastic. I ask because I have had considerable trouble with CSST having little tiny pin holes in the tubing itself. They are so small that unless it has been on a few days and/or it is in a tight location you will only pick up a very faint smell. Really it is best to have the gas company check it and make sure it is okay...you can be playing with a bomb there. To say the fireplace can "outgas" is like saying it will leak some...that is not right. You should not smell unburned gas with any appliance.

  6. #6
    Around here, if you call the gas company and tell them you think you smell gas, they will have somebody there with a leak detector pretty quick.

    Mike
    Go into the world and do well. But more importantly, go into the world and do good.

  7. #7
    soapy water applied to all gas connections and the regulator will find any leaks...Hardest to find gas leak I ever had turned out to be a hairline crack in a black pipe elbow. It barely even made a bubble with the soapy water, but plenty of that awful smell got out...

    do you have a propane torch? Open it and smell-- if what you're smelling around the fireplace smells anything like the propane, it's likely natural gas. Usually NG smells worse, more putrid.

    I've installed many a gas log, stove, wall fireplace, and several times there was a smell-- it was ALWAYS gas. I've never had gas logs smell. And most 'break in' heat related smells simply smell 'hot' to me. Gas smells like sulfur, rotten eggs, sewage even...
    ========================================
    ELEVEN - rotary cutter tool machines
    FOUR - CO2 lasers
    THREE- make that FOUR now - fiber lasers
    ONE - vinyl cutter
    CASmate, Corel, Gravostyle


  8. #8
    Most NG is delivered (at 38 to 40 PSI in some rare situations +++70 psi) after the meter, this gets water down into water column. For example, I have a 3/8 pipe feeding my meter. After my metre I have 1.5 inch pipe. On a good day, I have 8 inch water column pressure. Most interior pipes are tested to 20 psi for leaks. One of my buildings was pressure tested to 15 psi for one hour to grant certification.

    1 Water column and 1 psi is a huge difference.

    Yeah, most cheap sniffers work in parts/million specified. But… Unburnt fuel it is ordered. This can be picked up by the human nose (or with pressure testing techniques). The burnt fuel can be picked up by most carbon monoxide detectors in the parts per million too.
    Last edited by Matt Mattingley; 01-30-2019 at 12:21 AM.

  9. #9
    Join Date
    Oct 2007
    Location
    Falls Church, VA
    Posts
    2,345
    Blog Entries
    1
    I see that I neglected to include some pertinent information.

    the system is ventless.
    we only smell something in the upstairs hallway. The system is located on the first floor.
    the outgassing in the manual refers to the curing of the paint on the logs.
    we only smell something if the system is running

    so I think I can rule out the plumbing to the unit.

  10. #10
    Join Date
    Dec 2004
    Location
    Boston, MA
    Posts
    919
    I would sometimes smell gas when I walked into my sisters house so I bought a $50 gas leak detector on Amazon and headed for the basement. I found 3 leaks for the plumber to fix.

  11. #11
    Join Date
    May 2005
    Location
    Highland MI
    Posts
    4,526
    Blog Entries
    11
    Just finished adding a bunch of black iron pipe to my son's home for future gas connections (BBQ, future outbuilding, garage). Tested everything with a small spray bottle filled with dish soap and water. No leaks no smell. Had a smell like a dead mouse in my RV once, turned out to be a stove burner was left on very low, no ignition. Always thought propane smelled like rotten eggs. Not so. Varies by supplier. Ventless heat always makes me nervous. Shouldn't I guess as our gas stove is ventless.
    NOW you tell me...

  12. #12
    Quote Originally Posted by Roger Feeley View Post
    I see that I neglected to include some pertinent information.

    the system is ventless.
    Get rid of it! Ventless units are not worth the trouble they can cause.

  13. #13
    Quote Originally Posted by Brad Adams View Post
    Get rid of it! Ventless units are not worth the trouble they can cause.
    Please explain your statement. We have, and have had ventless logs, ventless wall mounted heaters for the last 20 years. Other than my wife doesn't care for the smell (yes they do smell) they haven't been any problems associated with these. We mainly use them for back up heat in a power loss.

  14. #14
    Join Date
    Jun 2006
    Location
    The Hartland of Michigan
    Posts
    7,628
    Quote Originally Posted by Brad Adams View Post
    Get rid of it! Ventless units are not worth the trouble they can cause.
    What trouble would that be. Making wild statements with nothing to back it up is bad form.
    Never, under any circumstances, consume a laxative and sleeping pill, on the same night

  15. #15
    Join Date
    Sep 2009
    Location
    Medina Ohio
    Posts
    4,534
    Quote Originally Posted by Brad Adams View Post
    Get rid of it! Ventless units are not worth the trouble they can cause.
    I have had a ventless gas heater for over 30 years and have a co detector near it that has never gone off without a test we cook with a gas range also and have a ventless range hood.