If you think about it, the electronics that go into a VFD, the circuit boards, the injection molded plastic enclosures, the microprocessor programming, the user interface, the manual, the safety testing and certifications....that's a big chunk of engineering. It's multi-millions of dollars worth of work. Obviously, you don't sell 800 VFDs for ~$500/ea and make money. So, logically, no, he's not building VFDs.
He may be taking commercial VFDs, putting them inside a secondary enclosure, maybe adding some different buttons, and providing technical support.
Well I dont know what you fellas are going on about with podcasts and this Jack guy but I digress. So turns out the motor does run on 220 3 phase. At least thats what the guy I bought it from tells me. So I rigged up a vfd I have hooked to my Supermax drum sander that uses 120v 1phase input and has 220v 3phase output at 1hp and it worked good. Seemed to be pretty fast cranked up to max also. Im going to order that Temco Vfd from factorymation for $130 and I'll report back if anyone would like.
Thanks for the help, Neil
I fully understand the advantages, I have a DIY rotary phase convertor and a VFD on my Oneway lathe. What I don't understand is how more than 7 VFDs compares to a hardwired 3 phase shop. I feel a rotary phase convertor will outlive cheap VFDs by a long shot. If the rotary phase convertor will last twice as long, then we are talking about more than 14 VFDs in the equation.
There is one VFD that will convert 220 volts to 415 volts that I know of and it ain't cheap. It was sourced out of the UK but I can't find a link to it at the moment.
Chris
Everything I like is either illegal, immoral or fattening
I got the machines one at a time over the course of several years. Some came with starters, some with pieces of starters, some in pieces. With a VFD I don't need to buy and set up a separate three phase panel, three phase distribution, fool around with magnetic starters, heaters, etc, or mess around with an RPC and listen to it run.
We do have a tendency to digress
Huh. So you hooked that motor to 240 and it worked? Based on the nameplate you posted, it doesn't appear to be a dual-voltage motor, so it's possible you're just running it at half voltage? That is actually not good for it - it will potentially overheat (the technical reason is that the V/Hz ratio is incorrect and it could saturate the magnetic core of the motor). It may be possible to compensate for this by programming the VFD with a different "base frequency".
I would consider replacing the motor with a 208 three phase and supplying it from a vfd. I think the variable speed is worth keeping for this machine. Or go ahead and use a single phase motor.
What kind of switch controls the motor? If it has a contactor control voltages will be off unless it has a transformer that can be rewired for lower inputs. Good luck finding a European coil of the new correct voltage.
Bill D
And, Neil, the speed of an induction motor doesn't depend on the voltage. So saying that it seems to be going "fast enough" is not an indication that you're running it at the "correct" voltage and not overheating it.
I agree with what has been said about VFDs, I use 3 in my shop and am planning on adding more to replace old static phase converters. There are many advantages of VFD's over rotary converters, soft starting (which reduces start up current, especially on machines with a lot of inertia, like my 30" band-saw), variable speeds, no waiting for the rotary converter to start first, and lower power consumption. Regarding your 440 volt motor, I suggest you take it to a motor shop and see if they can rewire it to 230 volts. I have never seen a 3 phase motor than could not be re-wired. Years ago I bought a 440 volt hollow chisel mortiser that did not have the usual dual voltage leads in the motor box, I called my local motor shop, they said I could "lift the leads" to the windings and re-configure them for the lower voltage, I did and it worked great. So just because the nameplate only says 440, does not mean it can't be re-wired. Otherwise you will need a transformer to raise your 220-230 volts to 440 volts.
I’m considering upgrading my Clearvue cyclone 1 phase to a 3 phase motor. I need my DC for shorter bursts, and doing that with the 1 phase is too hard on the motor. Very interested in hearing which way you go. Though in my research, a VFD seems the way to go.
99% of all Clearvues in Australia use a VFD, Cathryn at CV is fairly familiar with that though she does not know the technical details of course.