    Quote Originally Posted by Jim Becker View Post
    The same amps are spread over two conductors...
    That's not true Jim, a 20 ampere load at 120 volts is a 10 ampere load at 240 volts.

    In one case there is 20 amperes flowing in the circuit, in the other case 10 amperes. Both loads are single phase, so 2 conductors per circuit........Rod.

  2. #32
    Join Date
    Oct 2007
    Location
    Falls Church, VA
    Posts
    2,345
    Blog Entries
    1
    Good hint Bernie. I've never seen those before.

    I wonder if there are any that will automatically turn on my overhead dust filter and then turn it off when the dust subsides.

  3. #33
    Join Date
    Mar 2003
    Location
    SE PA - Central Bucks County
    Posts
    65,918
    Quote Originally Posted by Rod Sheridan View Post
    That's not true Jim, a 20 ampere load at 120 volts is a 10 ampere load at 240 volts.

    In one case there is 20 amperes flowing in the circuit, in the other case 10 amperes. Both loads are single phase, so 2 conductors per circuit........Rod.
    I stand corrected...I wasn't thinking when I replied.
    --