    Advice needed for my table saw

    I’m setting up a shop in my basement and have a 20V circuit dedicated to my table saw. I rewired my Delta 36-477 table saw to 230V many years ago and will need a longer power cord so I was going to shorten and use a 12 AWG extension cord with a 230V plug, but when I opened up the switch I found that the current wiring is 14 AWG. Solder 12 AWG to 14 AWG connector wires? That doesn’t make sense to me. Get a new switch and run new wire to the new switch and motor? What do you folks suggest?

  2. #2
    Join Date
    Jan 2010
    Location
    LA & SC neither one is Cali
    Posts
    9,447
    That's a 2hp contractor saw correct? If so it probably isn't even pulling 10 amps on 240v.
    Of all the laws Brandolini's may be the most universally true.

    Deep thought for the day:

    Your bandsaw weighs more when you leave the spring compressed instead of relieving the tension.

  3. #3
    Join Date
    Mar 2006
    Location
    SoCal
    Posts
    22,512
    Blog Entries
    1
    The manual states 1-1/2 HP. Extension cord info from your manual:

    temp.JPG

    Remember this is a job site saw and is designed to be run on temp power wherever you may be using it. In a relatively fixed position in a home shop, 14 gauge should be fine at 220v.
    "A hen is only an egg's way of making another egg".


    – Samuel Butler

  4. #4
    Join Date
    Nov 2003
    Location
    Central North Carolina
    Posts
    1,830
    Is your saw a an older Delta Contractor saw?

    If so, you need to look closely at the motor label as it's likely not a normal 120/240 volt motor, since most of these saws had a specially designed motor that only produced 1 1/2 hp when wired and connected to a 120 volt 15 amp power circuit, so the contractor could take it to the job site and plug it into any home 120 volt circuit in the house without drawing so much current that it would trip the 15 amp breaker. To make it not overload the 120 volt circuit the motor hp is limited to 1 1/2 hp when wired for 120 volts. But when the saw is wired for 240 volt power and used back in the contractor's shop, the motor will produce a full 2 hp on 240 volts at considerably less than 15 amps. So in either configuration the saw draws less than 15 amps when running at full load and 14 gauge wire within the saw is acceptable. If the saw is run from a long extension cord, it's best to use a heavier gauge like 12 ga extension cord to reduce the voltage drop in the long extension cord, because voltage drop in this cord and poor starting and less than maximum horsepower of the saw will be reduced. Still, the short wires within the saw and it's power cord do not need to be replaced, because they will never see more than 15 amps of load and their length is so short that voltage drop in them will not be a problem. Leave the wiring within the saw 14 gauge.

    I found one of these Delta Contractor saws, a model 34-444 (but most of this series are basically the same) for my son and tuned it up for him. We have found it to be very satisfactory in performance for most of his woodworking needs with one major exception. Saw dust control is almost impossible because the bottom and back of the saw is completely open. Another exception is that the trunnion of the saw is attached to the bottom of the saw table, making alignment of the blade to the miter slots a bit more difficult to perform, but once aligned and adjusted properly the saw cut every bit as accurately as the Delta Unisaw that's in my shop. No, a contractor saw isn't a Unisaw in many ways, but it can be adjusted to cut just as accurately, although with less horsepower and no control over where the sawdust goes.

    Charley

  5. #5
    The motor is dual voltage- 1.5hp at 115 V, and 2hp at 230V. I need a longer cord.

  6. #6
    Should I clip a different extension cord and use it for my power cord, or better off going to the store and get a new cord cut to length off one of their big reels? I put 2 twist lock receptacles on the ceiling- 1 above each end of the table saw so I can turn my saw 180 degrees to avoid interference when cutting larger pieces of wood- so I will need a long enough cord to drop from my 8’ ceiling and leave me some room so it doesn’t get hit by wood. How long a cord should I use?

  7. #7
    Join Date
    Mar 2003
    Location
    SE PA - Central Bucks County
    Posts
    65,885
    Colin, I build machine cords from component stock...such as the rubber coated wire "on the spool" at the store combined with appropriate terminations, rather than doctoring an off-the-shelf extension cord. For your specific application, I'd use the 12 gage wire.
    --

    The most expensive tool is the one you buy "cheaply" and often...

  8. #8
    I’m good with buying off the spool. The problem I face is that the wires from the switch to the motor is 14 AWG, and the connectors at the switch where the wire would come in from the power switch (from the ends of the OEM power cord are also 14 AWG. What method would you use to adopt 12AWG? The connectors are small.

  9. #9
    They are female flag connectors.

  10. #10
    Put a short 14 gauge cord on the saw and use your 12 gauge cord as is.

  11. #11
    Join Date
    Mar 2003
    Location
    SE PA - Central Bucks County
    Posts
    65,885
    Quote Originally Posted by Bradley Gray View Post
    Put a short 14 gauge cord on the saw and use your 12 gauge cord as is.
    Agree with this. In fact, it's my normal way of doing things...a pigtail on the tool and an appropriate length "extension" cord to the wall.
    --

    The most expensive tool is the one you buy "cheaply" and often...

  12. #12
    Quote Originally Posted by Bradley Gray View Post
    Put a short 14 gauge cord on the saw and use your 12 gauge cord as is.
    Can you please expand? Short 14 from where to where? 12 AWG cord attached where?

  13. #13
    Join Date
    Mar 2003
    Location
    SE PA - Central Bucks County
    Posts
    65,885
    Quote Originally Posted by Colin Tanner View Post
    Can you please expand? Short 14 from where to where? 12 AWG cord attached where?
    The existing cord is cut off close to the saw and re-terminated with a 240v plug. You then use a 240v extension cord with the same connector type(s) to extend to the outlet.
    --

    The most expensive tool is the one you buy "cheaply" and often...

  14. #14
    Join Date
    Nov 2003
    Location
    Central North Carolina
    Posts
    1,830
    If your existing power cord on your saw isn't damaged you can just replace the plug with the twist lock male plug, however, you should keep in mind that going with twist locks will make your saw unusable anywhere else but where you have installed the twist lock receptacles. Why not just use the standard 240 volt three prong straight pin 20 amp plugs and receptacles instead of the twist lock (for 240 volts the pins are the same size, but sideways. They won't unplug from gravity. I have both 120 and 240 receptacles on the ceiling of my shop and the mating plugs never all out, unless they are pulled out. BTW, the code requires the use of Kellums grips at your ceiling box and at your pendant receptacle on the hanging pendant power cord. A Kellums grip is a kind of metal version of a Chinese finger trap and it grips the power cable better than the two screw grips on both ends of the power cable hanging down from the ceiling (it's called a pendant in the code book). This piece of cable is part of the building wiring, so the code fully applies. For the plug on the saw, it's considered temporary and does not require the Kellums grip, but I would add one if you remove the existing molded on plug and replace it with a 240 volt 3 straight prong or twist lock plug because the normal clamps don't hold well in a constant vertical pulling direction.

    If you don't fully understand this you need to hire an electrician or find a friend who knows the NEC (National Electric Code) and can follow it. You are risking a shop fire or electrocution if you don't do this right.

    Charley

  15. #15
    Got it. Thanks everyone for your suggestions.