Thread: 240 volt extension cord.

  1. #1
    Join Date
    Jan 2005
    Location
    Harrisburg, NC
    Posts
    2,255

    240 volt extension cord.

    Will this work? I have a barn 80' from my laundry room dryer outlet. I would like to use my Sawstop in the barn but I don't have 240 available. Doing it the right way with a sub box and buried cable is not an option at this time. Can I make an extension cord to plug into my 3 prong dryer outlet when I want to use the saw? What size wire? Help.
    Richard

  2. #2
    Join Date
    Mar 2003
    Location
    SE PA - Central Bucks County
    Posts
    65,881
    Richard, for that kind of distance, you'll want to seriously upsize any "extension cord" you use and it's not going to be pretty cost-wise. If the saw runs on a 20 amp circuit normally, upsizing to 10 gage probably will work, but hopefully the "sparky folks" here can confirm or deny that. HD carries heavy rubber coated 10 gage cord-stock (I use it for machine specific cords/extensions in my shop). I don't know if they have heavier.
    --

    The most expensive tool is the one you buy "cheaply" and often...

  3. #3
    Join Date
    Jan 2005
    Location
    Harrisburg, NC
    Posts
    2,255
    Thanks Jim, I was hoping to use 10 gage or maybe even 8 if necessary. Just hoping for some insight about about doing it. The dryer plug is only a 3 prong, I assume 2 hot and a neutral/ground, do I need 10/2 or 10/3 wire?
    Richard

  4. #4
    Join Date
    Feb 2008
    Location
    E TN, near Knoxville
    Posts
    12,298
    Quote Originally Posted by Richard Wolf View Post
    Thanks Jim, I was hoping to use 10 gage or maybe even 8 if necessary. Just hoping for some insight about about doing it. The dryer plug is only a 3 prong, I assume 2 hot and a neutral/ground, do I need 10/2 or 10/3 wire?
    You should look at the current requirements of the saw under load and base the wire size on the maximum voltage drop you want to tolerate for that distance. There are online calculators. I don't like dropping the voltage much (which causes even more current draw in motors) so I tend to oversize the wire. The last 220v extension cord I made was 20' long for a welder on a 50amp circuit to weld outdoors. Probably 8/2 with ground - can't remember. Stranded wire, bought from an electrical supply house.

    JKJ

  5. #5
    Join Date
    Sep 2006
    Location
    Deep South
    Posts
    3,970
    Here is a little arithmetic you may find useful. A 10 gauge wire has a resistance of about 1 ohm per thousand feet. You are talking about a wire that is 160 feet (80 feet there and back). Therefore, the resistance in the wire will be about 160/1000 or 0.16 ohms. If your saw draws 20A, which I suspect is a significant overestimate, then you will lose 20 X 0.16 or 3.2 volts under full load. That isn't enough to make any difference unless your house voltage is already critically low or has an unusually high inherent resistance for some reason.

    There is one other thing I want to mention. "Ground" and "neutral" are absolutely not the same thing and it is vital that you know the difference. Ground is a safety connection and is never intended to carry any current unless you have a fault condition. The neutral wire carries the return current from a 120VAC load and carries the imbalance current in a complex 120/240VAC circuit. Your load is one simple 240VAC element so you only need a safety ground and not a neutral.

  6. #6
    Join Date
    Feb 2014
    Location
    Lake Gaston, Henrico, NC
    Posts
    9,057
    By the time you buy type no. 8 SO wire, and Hubbell plugs for the ends, you're into the buried wire, and subpanel cost fairly substantially.

  7. #7
    Join Date
    Sep 2012
    Location
    Tampa Bay area
    Posts
    1,099
    My opinion is 10 gauge is probably okay for your distance if you are just doing hobby work. If you are going to run production then you should go 8 gauge. You can get 10/3 100' extension cords at Home Depot.
    https://www.homedepot.com/p/American...0002/204667740
    Cut the ends off and put on whatever 220 plugs you need.
    If you want to do it by the book follow John and Jim's advice. My opinion is based on what has worked for me over the years.

  8. #8
    Join Date
    Aug 2013
    Location
    Princeton, NJ
    Posts
    7,298
    Blog Entries
    7
    The wire in the wall may not be heavy enough.
    Bumbling forward into the unknown.

  9. #9
    Join Date
    Feb 2014
    Location
    Lake Gaston, Henrico, NC
    Posts
    9,057
    Good point, and also the length of the no. 10 wire from the breaker to the dryer outlet.

  10. #10
    Join Date
    Sep 2006
    Location
    Deep South
    Posts
    3,970
    Dryer outlets are typically wired for 30A so there is no problem with the wire size in the wall unless the house was wired wrong. If that is true then all bets are off. That does bring up a good point though. The extension cord needs to be sized at 10AWG or larger if the original poster expects the dryer breaker to protect it.

    I don't see why being a hobbyist or professional has anything to do with wire size. Either the wire is large enough for the saw or it isn't, regardless of how much it is used.

  11. #11
    Join Date
    Sep 2007
    Location
    Upstate NY
    Posts
    3,789
    IIRC a 3hp SS is 13a.
    If the current wiring is for an electric dryer, it will be heavy enough that it can be ignored for this purpose, though it is prudent to confirm what it is.
    A voltage drop calculator is found at https://www.calculator.net/voltage-d...s=13&x=56&y=17
    It is considered proper to have 3% voltage drop to your tool.
    As you will find, you don't need that much of a cord.

    Over the July 4th our neighborhood was getting 102v. I shut everything off, but I didn't hear of anyone else suffering any damage.

  12. #12
    I don't really worry about voltage drop until I am pushing 200 feet from my panel.

  13. #13
    Join Date
    Jan 2005
    Location
    Harrisburg, NC
    Posts
    2,255
    Thanks every one for your help. The dryer is about 10' from the breaker box. My saw is 5hp and draws about 20 amps. Maybe I'll see if I have enough room in the box to wire a dedicated outlet.
    Richard

  14. #14
    Join Date
    Mar 2008
    Location
    Beantown
    Posts
    2,831
    Hmmm, if your going to go through the trouble to wire in an additional outlet, (which is probably a good idea BTW), maybe think about slapping an exterior receptacle box on the side of your house so your not constantly going in an out to plug your extension cord in? Not much more work or expense and very likely well worth once you start using it

    Oh and if you don't currently have room in your panel, you can get double single pole breakers to open up some space. They're basically two breakers that take up the space of one. A couple of those will open up space for your new outlet.

    For what its worth I use a 60' - 10 gauge extension cord to run 3 phase machines I haven't gotten around to wiring up yet. Been doing it for years on motors up to 7-1/2 hp and it gets the job done.

    good luck,
    JeffD

  15. #15
    Join Date
    Nov 2012
    Location
    North Dana, Masachusetts
    Posts
    491
    It's worth getting an electrician in to set you up right. Once that's done, adding on is easy. Wires will also be grounded as they enter the buildings. I have had lightning problems.

    You could run the saw on a portable generator for a while, until you are wired up. It never hurts to have a portable generator, or two, around. I ran my shop on a portable generator for two weeks when we had a bad storm take the wires down a few years ago.