You can do some tests with your voltmeter that would help. Test the voltage before the 40A breaker. If it's in the house panel, remove the cover and put the test leads across the main lugs. Then check the voltage on the load side of the breaker (the lugs on the breaker). Then test the voltage where it enters the shop. If you see any unusual voltage drop, more than a couple of volts or so, you may have a bad breaker (if the drop is at the lugs of the breaker) or bad connection somewhere or open insulation underground that's bleeding to ground.
It could very well be there was a spike and that breaker picked it up. I once had a 2000A, 480V disconnect fail to trip and it went through every current protection device upstream until it finally tripped a 112kV transformer and shut the whole site down. There were some very angry people that day.
Anyway, if you can't find anything unusual, you'll have to wait and see if it happens again. It may not.