I have had an Oneida 3 hp DC for about 13 yrs in a 700 sf shop. Great unit. The noise has always been an issue. I'll be building a closet around the DC within the next week but am concerned about return air. As I understand it, the duct is used to REMOVE air from the closet so the closet doesn't get pressurized from all the air being sucked through the DC and blown out the filter. I called Oneida and they said my DC produces about 1300 cfm and I need 3 sf of duct (1 sf/ 500 cfm). After thinking about it, I asked if I could use a 1300 cfm intake fan but I think it will still require 3 sf of duct to move 1300 cfm of air so no sense using an intake fan. I'm trying to reduce the size of the duct but I don't think I can, even with a fan. Is that correct? Any other ideas to reduce duct size. Thanks.