    Wire Breaker, Plug for new T/S

    Ordering a new 5 hp table saw (Jet) -- I'm thinking a 30a breaker with #10 wire from the box to the twist plug. Sound right? Anything else I need to consider? I really appreciate the expertise available here - thanks. Vince
    Last edited by Vince Shriver; 04-21-2018 at 3:19 AM.

  2. #2
    Join Date
    Sep 2016
    Location
    Modesto, CA, USA
    Posts
    10,004
    240 volt, single phase?
    Bil lD

  3. #3
    Yes, I should have included that. 240/single phase. Thanks Bill

  4. #4
    Join Date
    Feb 2008
    Location
    E TN, near Knoxville
    Posts
    12,298
    Quote Originally Posted by Vince Shriver View Post
    Ordering a new 5 hp table saw (Jet) -- I'm thinking a 30a breaker with #10 wire from the box to the twist plug. Sound right? Anything else I need to consider? I really appreciate the expertise available here - thanks. Vince
    Consider the length of the run too, probably not far for inside a shop. I have no electrician credentials but when I wired my shop and did the voltage drop calculations I decided to run #8 wire to the 5 hp motors on the far end of my shop, an air compressor and a cyclone DC, and #10 for 3 hp and smaller 230v motors.

    JKJ

  5. #5
    Join Date
    Sep 2004
    Location
    Jacksonville, FL
    Posts
    859
    I wont go smaller than #10 even for extension cords. Bigger is better in my book.

    Depending on the distance I would go at least the #10 but for a longer run I would prefer #8.

    Check the specs on your Jet and it should say what to use.
    Marshall
    ---------------------------
    A Stickley fan boy.

  6. #6
    Join Date
    Mar 2003
    Location
    SE PA - Central Bucks County
    Posts
    65,887
    "Most likely" the 5hp saw requires a 30amp 240v circuit with appropriate wire and terminations. It's a best practice to confirm with the manufacturer's specifications before your install your circuit, but "in general", you should be fine with 10 gage wire, a 30 amp breaker and 30 amp rated terminations, the latter are typically twist locks.
    --

    The most expensive tool is the one you buy "cheaply" and often...

  7. #7
    Join Date
    Feb 2007
    Location
    Oglesby,Il.
    Posts
    73
    Usually you use an 80% factoring when sizing feeds to motors.....A 5hp 240v single phase motor has a full load amp rating of 28 amps.......80% of 30a is 24a.....So I would go with a 40a breaker and #8 wire
    I can sure make a mean pile of Saw Dust !!!

  8. #8
    Join Date
    Nov 2015
    Location
    Pepperell Ma.
    Posts
    93
    Quote Originally Posted by Terry Kelly View Post
    Usually you use an 80% factoring when sizing feeds to motors.....A 5hp 240v single phase motor has a full load amp rating of 28 amps.......80% of 30a is 24a.....So I would go with a 40a breaker and #8 wire
    Terry is correct, if the full load amp reading is over 24 amps it needs to be on a breaker/fuse over 30 amps. Maybe Jet will give you a straight answer, but I would expect one that says wire it in full compliance of all local/national codes yada yada yada. While there certainly are negative consequences of over sizing a breaker, there really are none for over sizing the wire, as long as it will fit on the breaker, and receptacle/cord cap.

  9. #9
    Join Date
    Sep 2007
    Location
    Upstate NY
    Posts
    3,789
    Without knowing how many amps it draws, and the manufacturer's recommendation, any advice is meaningless.
    3hp motors are anything from 13 to 22a; I presume 5hp are similar.