    Is it possible to buy a plug rated for 20 amps that has the normal configuration of 2 vertical prongs? All the ones I'm seeing have one vertical and one horizontal.

  2. #2
    I think that pretty much defines a 20 amp plug.

    Mike
    Go into the world and do well. But more importantly, go into the world and do good.

  3. #3
    Join Date
    Sep 2010
    Location
    New England
    Posts
    2,474
    OK. Since this is for 110 and not 220, I was hoping.

    Follow-up question- my drum sander is 110v but supposed to be on a 20 amp circuit. Would it be a problem to use a 12 ga extension cord with a 15 amp plug to extend the 20 amp circuit? I'm making the extension box and the 2 duplex receptacles are rated 20 amp with the 15 and 20 amp configuration but if I use a 20 amp plug I won't be able to ever use this on a 15 amp circuit. Not a huge deal but I like things to be as multi purpose as possible. So would a 15 amp plug really cause any problems?

  4. #4
    An appliance or tool the requires more than 15 amps will usually come with a 20 amp plug so you don't plug it into a 15 amp circuit and pop the breaker.

    If you have 20 amp breakers and wire that will handle up to 20 amps, I would not be afraid to use a regular two or three prong 120V plug on the appliance or tool. But if you plugged it into a 15 amp circuit, the appliance or tool would pop the breaker.

    Someone who came after you would not be put on notice (because of the lack of the 20 amp plug) that the appliance or tool required a 20 amp circuit.

    Mike

    [Most outlets that are 20 amp will accept either a 20 amp plug or a 15 amp plug. It's the male plug on the appliance or tool that signifies that the tool requires 20 amps. Put 20 amp outlets on your extension box and you can plug either into it. And that way you can keep the 20 amp plug on the tool.]
    Last edited by Mike Henderson; 02-12-2018 at 8:49 PM.
    Go into the world and do well. But more importantly, go into the world and do good.

  5. #5
    The 20 amp recepticals accept the 15 amp plugs. They have the advantage of gripping plugs tighter. All the 110 recpt. in shop are 20 amp, along with the ones in our kitchen. Buy hospital grade plugs, as they are the best. Unfortunately they COST a LOT MORE.

  6. #6
    Join Date
    Sep 2010
    Location
    New England
    Posts
    2,474
    OK this all makes sense. The drum sander does not have a 20 amp plug on it but they recommend running it on a 20 amp circuit. I guess they are just being cautious in case other things are running on that circuit at the same time. I'll use a regular plug and not worry about it. All the wire is 12ga- the romex and the stranded extension.

  7. #7
    My guess, Dave, is that the sander will draw very close to (or maybe even a bit over) 15 amps when it's bogged down and that could pop a 15 amp breaker. But under normal conditions, it probably draws less than 15 amps.

    Mike
    Go into the world and do well. But more importantly, go into the world and do good.

  8. #8
    Join Date
    Sep 2010
    Location
    New England
    Posts
    2,474
    Quote Originally Posted by Mike Henderson View Post
    My guess, Dave, is that the sander will draw very close to (or maybe even a bit over) 15 amps when it's bogged down and that could pop a 15 amp breaker. But under normal conditions, it probably draws less than 15 amps.

    Mike
    Probably right on. Logical.

  9. #9
    Join Date
    Dec 2006
    Location
    Toronto Ontario
    Posts
    11,247
    Quote Originally Posted by Mike Henderson View Post
    My guess, Dave, is that the sander will draw very close to (or maybe even a bit over) 15 amps when it's bogged down and that could pop a 15 amp breaker. But under normal conditions, it probably draws less than 15 amps.

    Mike
    That could be accurate Mike, they also may have an issue with locked rotor current and needed larger overcurrent protection to start the machine.........Regards, Rod.

  10. #10
    Quote Originally Posted by Rod Sheridan View Post
    That could be accurate Mike, they also may have an issue with locked rotor current and needed larger overcurrent protection to start the machine.........Regards, Rod.
    Good point. I forgot about startup.

    Mike
    Go into the world and do well. But more importantly, go into the world and do good.

  11. #11
    Join Date
    Sep 2006
    Location
    Deep South
    Posts
    3,970
    You guys should really study up on breaker behavior. If you are familiar with using graphs, download the "trip curve" for the breaker you are using. Actually, they all behave about the same. First of all, the actual trip current of a normal breaker could be 10% or even 20% higher than the specified trip point. These are not very accurate devices. Second, most breakers will sustain twice the rated current for 20 to 40 seconds and ten times the rated current for 4 or 5 seconds. One should never oversize a breaker to compensate for startup current. That is already designed to the breaker itself. Also, momentary load peaks in excess of the trip current will seldom cause a breaker to open unless conditions are really bad - like locked rotor for an extended time.

    Here is a link to some information I found doing a quick search that looks pretty good. There are dozens of references on line.

    https://www.schneider-electric.us/en...nt/0600DB0105/

  12. #12
    Join Date
    Jun 2006
    Location
    The Hartland of Michigan
    Posts
    7,628
    All my outlets are 20 amp, so I have no problem what I plug into them.
    Never, under any circumstances, consume a laxative and sleeping pill, on the same night

  13. #13
    Quote Originally Posted by Myk Rian View Post
    All my outlets are 20 amp, so I have no problem what I plug into them.

    But you can't plug a appliance that requires a 20A plug into a 20A branch circuit, because if it draws more then 50% of the branch circuits rating then it requires it's own circuit.

  14. #14
    Join Date
    Mar 2003
    Location
    SE PA - Central Bucks County
    Posts
    65,675
    Rollie, that's true...and also probably one of the most ignored rules, particularly in kitchens. My espresso machine requires a 20 amp connection (and has the plug to prove it), but the nature of such things is that it uses the regular branch circuit because that's what's there. But it also isn't operating when something else might need to use that same circuit.
    --

    The most expensive tool is the one you buy "cheaply" and often...

  15. #15
    Join Date
    Nov 2010
    Location
    Sherman Oaks, CA
    Posts
    43
    I was a hospital manager for over 40 years in hospitals and as a department head was responsible for complying with safety rules and subject to sport inspections. Every hospital manager is responsible for assuring that hospital quality plugs are installed and that they meet OSHA and electrical standards. Hospital grade receptacles and plugs can easily be identified by a green dot embossed in the body of the plug or receptacle. In addition to have the identification, records are maintained certifying that such plugs require a minimum effective tension to be removed from their receptacle. This guarantees that a loose plug won't be accidentally withdrawn or fall out of its corresponding receptacle. If a receptacle does not meet the minimum standards for withdrawal of the plug, it must be replaced, even though it is otherwise working appropriately. The last thing that should ever happen is for a patient to be endangered by having a plug accidentally fall out of a receptacle