Rod Sheridan
Where I live flexible cord is only allowed for portable devices or where motion is required, it cannot be used as a substitute for permanent wiring.........Regards, Rod.
If you're talking about "cord" as in extension-type cord, no, that use is typically not allowed for permanent electrical connections. I have never seen it allowed anywhere.
Greenfield or Sealtite can be used when connecting to motors or other loads to reduce vibration. In the areas I worked, when hooking up a motor, flexible conduit was required. But there are limitations on length and there may be additional grounding required. For instance if you're using Sealtite to connect a motor and the motor is rated over 20A, a ground wire is required. Usually, the limit on length for any flexible conduit is 6 feet. (All this based on my personal experience working as an electrician in the Chicago area.)