    Hot Dawg air supply solution? Comments?

    As I wrote a few days ago I'm installing the 45,000 BTU model. Since I have worked hard to seal the cracks and insulate my shop, I'm concerned about possible negative pressure and starving the heater for air, possibly creating a CO problem.

    I hate to just cut a 7-8" opening in the wall that would allow cold air in all the time. (And we do have cold air here in the winter!) The instructions call for a 1" square opening for every 1,000 BTU's.

    So I wonder if this would work: Cut a 4" hole in the wall under the heater and install 4" metal ducting entering the shop for 1-2 feet. Then a 90 degree elbow and continue 4" duct up close to the heater. (A "L" shape) The heater is close to the wall. In the long vertical section I would install a 4" duct booster fan. I would get a switch, that I can't remember what it is called. I have one from Sears that I can plug tools and my Fein vacuum into so the Fein comes on when the tool is started and they both go off together.

    I would wire the heater with a plug and plug it into the switch and then the fan so the fan only works when the heater is running, demanding air.

    I would also put a flapper in top of the 4" duct, kind of like the flapper on top of the vertical mufflers on old farm tractors. This would prevent air from entering all the time, but would move up when the duct fan pushes air out. I would insulate the ducting.

    The switch is about $25, the duct booster is $22 at HD and some ducting. Probably a total cost of $60 or $70.

    I'm planning on maintaining the shop at 40 degrees during the winter, then when I'm working I'll fire up my wood stove to bring the temp up to 60-65 degrees. So I'm figuring the Hot Dawg won't be running a lot.

    What do you think? Or am I being paranoid??

    Thanks, Rick


  2. #2
    Rick,
    I work in the workers health and safetyt field. Carbon Monoxide is produced from incomplete combustion typically from improper air flow. If the heater requires 1sq.in. per 1000 BTU then you need 45 sq.in.
    according to my calulations you need a pipe diameter of 7.57 in. so I wouldn't use anything less then an 8" pipe.

    Area = pixRadius squared

    So working backwards

    ((45 sq.in/3.14)^.5)x2=7.571317

    Sorry, but thats what I'd use.

  3. #3
    Join Date
    Mar 2003
    Location
    SE PA - Central Bucks County
    Posts
    65,893
    Don, could he put an automatic/swinging damper on that inlet to conserve heat when the unit isn't running?
    --

    The most expensive tool is the one you buy "cheaply" and often...

  4. #4
    Quote Originally Posted by Don Baer
    Rick,
    I work in the workers health and safetyt field. Carbon Monoxide is produced from incomplete combustion typically from improper air flow. If the heater requires 1sq.in. per 1000 BTU then you need 45 sq.in.
    according to my calulations you need a pipe diameter of 7.57 in. so I wouldn't use anything less then an 8" pipe.

    Area = pixRadius squared

    So working backwards

    ((45 sq.in/3.14)^.5)x2=7.571317

    Sorry, but thats what I'd use.
    Don,
    Not meaning to hijack a thread, but what is the minimum height- floor to ceiling, that's allowed for this heater? I have 8' ceilings - am I in trouble?

    Bob
    bob m

  5. Quote Originally Posted by Rick Schubert
    As I wrote a few days ago I'm installing the 45,000 BTU model. Since I have worked hard to seal the cracks and insulate my shop, I'm concerned about possible negative pressure and starving the heater for air, possibly creating a CO problem.

    I hate to just cut a 7-8" opening in the wall that would allow cold air in all the time. (And we do have cold air here in the winter!) The instructions call for a 1" square opening for every 1,000 BTU's.

    So I wonder if this would work: Cut a 4" hole in the wall under the heater and install 4" metal ducting entering the shop for 1-2 feet. Then a 90 degree elbow and continue 4" duct up close to the heater. (A "L" shape) The heater is close to the wall. In the long vertical section I would install a 4" duct booster fan. I would get a switch, that I can't remember what it is called. I have one from Sears that I can plug tools and my Fein vacuum into so the Fein comes on when the tool is started and they both go off together.

    I would wire the heater with a plug and plug it into the switch and then the fan so the fan only works when the heater is running, demanding air.

    I would also put a flapper in top of the 4" duct, kind of like the flapper on top of the vertical mufflers on old farm tractors. This would prevent air from entering all the time, but would move up when the duct fan pushes air out. I would insulate the ducting.

    The switch is about $25, the duct booster is $22 at HD and some ducting. Probably a total cost of $60 or $70.

    I'm planning on maintaining the shop at 40 degrees during the winter, then when I'm working I'll fire up my wood stove to bring the temp up to 60-65 degrees. So I'm figuring the Hot Dawg won't be running a lot.

    What do you think? Or am I being paranoid??

    Thanks, Rick
    Interesting ... the 1" per 1,000 btu/hr of air is often the quoted amount for combustion air being supplied by a duct that communicates directly with the outside. My concern is that the damper in the duct will cause a problem ... it is restrictive ... and the heater will expose you to low levels of CO without you knowing it. Besides that, your system is fairly complicated with the duct fan, venting with ells, etc.

    There's a much better solution ... use an opening with motorized louvers interlocked with the heater.

    You have to oversize the louvers in this case to get the "net free area" of 45", but a 10 x 10 motorized louver would be enough (they usually deduct 50% for the louvers). When the heater is going to come on, the signal first goes to the louver motor, it opens the louvers and when they are fully open, the heater comes on. At the end of the heating cycle, the louvers close. If the louvers don't open, the heater doesn't come on (unlike your duct fan, which might not come on, and you might not notice it until you're looking down from Heaven watching your wife find your body.)

    There are also combustion air fans that provide the air only when needed .... see the "fan in a can" at http://www.fieldcontrols.com/cas3-4.html This turns on the fan, and supplies the air only when the heater is operating. But these are more expensive than the motorized louvers.

    The motorized louvers are probably the best bet. The greenhouse supply places all carry them, and the wiring between the heater and the louvers is simple enough.

  6. #6
    Join Date
    Jan 2005
    Location
    Minnesota
    Posts
    173
    Quote Originally Posted by BOB MARINO
    Don,
    Not meaning to hijack a thread, but what is the minimum height- floor to ceiling, that's allowed for this heater? I have 8' ceilings - am I in trouble?

    Bob
    Bob,

    I'm pretty sure the instructions said 10 feet maximum.

    Rick


  7. #7
    Quote Originally Posted by Rick Schubert
    Bob,

    I'm pretty sure the instructions said 10 feet maximum.

    Rick
    Is that minimum?

    Bob
    bob m

  8. #8
    Join Date
    Jan 2005
    Location
    Minnesota
    Posts
    173
    Sorry, I misread your message. I looked again in the instructions and didn't see any reference to minimum height. Only the clearances to combustables which are 1 inch top and bottom.

    Although I obviously could have misread or missed it entirely.

    Rick


  9. #9
    Join Date
    Jan 2005
    Location
    Minnesota
    Posts
    173
    Quote Originally Posted by Don Baer
    Rick,
    I work in the workers health and safetyt field. Carbon Monoxide is produced from incomplete combustion typically from improper air flow. If the heater requires 1sq.in. per 1000 BTU then you need 45 sq.in.
    according to my calulations you need a pipe diameter of 7.57 in. so I wouldn't use anything less then an 8" pipe.

    Area = pixRadius squared

    So working backwards

    ((45 sq.in/3.14)^.5)x2=7.571317

    Sorry, but thats what I'd use.
    Don,

    I assumed the 1 inch square was for an opening in the wall. With the booster duct fan I figured it would be pulling more air in than a hole in the wall. So I thought I could go with a smaller opening.

    From what I read between the lines in previous posts on these heaters, I assume most applications are not using any air replacement. I think most are relying on leaks and air seepage. So I thought this might be a lot better than nothing. Probably incorrect thinking.

    Rick


  10. #10
    Join Date
    Sep 2003
    Location
    WNC mountains
    Posts
    143

    You still need 450 cubic feet/hour air flow

    What is the flow of the booster fan with 4" duct and the back pressure of the elbow and flap damper? To be safe you need a combustion air pressure switch to prove that the fan is truly on.

    Bill in WNC mountains

  11. #11
    So what provides the fresh air intake that the woodstove needs? I'd be much more worried about that than the Hot Dawg. The Hot Dawg has a powered vent to make sure the combustion gasses leave the shop. The stove only has convection.

  12. #12
    Bob, as for minimum height, I have a similar restriction, and it's posed no problem to my installation. As long as you observe min clearances, you'll be fine.

    I suspect the minimum height formulas are for maximum distribution of the heat, and not safety. You can leave your hand on the case of the unit while running. The distribution fan in the unit makes sure the hot air moves around the shop.

  13. #13
    Join Date
    Oct 2005
    Location
    Northern VA
    Posts
    8
    Rick,

    I have a 4' x 4' window on one wall in my shop and was planning on leaving it cracked an inch or so while in the shop and using the heater. Or I could leave my main shop door cracked an inch or so since it is a 6' door.

    Was your original thought with your design to have more of an automatic way of having air available when the heater was running?

    Randy

  14. #14
    Join Date
    Oct 2005
    Location
    Northern VA
    Posts
    8
    Bob,

    I read that the unit should not be installed below 7' from the bottom of the unit for commercial applications and 5' from the bottom of the unit for residential applications. So you should be okay with the 8' ceilings.

    Randy

  15. #15
    Rick, Randy and Randy,

    Thanks - off to the Town office for a plumbing permit!

    Bob
    bob m

Similar Threads

  1. Alcohol Drying??
    By Chuck Harris in forum Turner's Forum
    Replies: 28
    Last Post: 01-03-2010, 3:24 PM
  2. Hot Dawg Heater Venting - Fresh Air
    By Rick Schubert in forum General Woodworking and Power Tools
    Replies: 8
    Last Post: 11-05-2005, 12:25 PM
  3. Replies: 15
    Last Post: 03-12-2005, 9:57 PM
  4. General Industrial Supply Website
    By Ken Salisbury in forum General Woodworking and Power Tools
    Replies: 19
    Last Post: 10-28-2004, 7:58 PM
  5. Soliciting comments re Festool Systainers
    By Frank Pellow in forum General Woodworking and Power Tools
    Replies: 41
    Last Post: 06-27-2004, 6:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •