    Chiller not working

    My chiller is behaving oddly. It's only 60 degrees farenheit in the room but it's having trouble chilling the water down to 19 degrees Celsius even with the laser not running for many minutes at a time. It's a CW 6000 model so it's typically a beast, and has no problem chilling the water down to 19 degrees C even in 110 degree weather normally. I've cleaned the filters, checked the water level. What am I missing?
    Last edited by Keith Winter; 12-06-2016 at 9:40 AM.
    Trotec Speedy 400 120w, Trotec Speedy 300 80w
    Thunderlaser Mars-130 with EFR 130w tube
    Signature Rotary Engravers (2)
    Epson F6070 Large Format Printer, Geo Knight Air Heat Presses (2)

  2. #2
    Your ambient temp is ~16c and I think 20c is the lowest these units are allowed to go. Not sure what type of controller you have so I am just swaging it. My first thought is the system is confused by the low ambient temp, and may not have any issue. Can you bring the ambient room temp up close to 20c? Since everything looks good mechanically, I would look into the controller side. Good luck

  3. #3
    Join Date
    Oct 2013
    Location
    United States
    Posts
    1,038
    My other chiller the same room is working fine, was working fine for 6 months until today. The CW series chillers are adjustable from 15c-30c. It's about 65 degrees in the room right now (18.3 C), and it won't cool down. As soon as I turn on the laser it spikes and cannot keep the water cool.
    Trotec Speedy 400 120w, Trotec Speedy 300 80w
    Thunderlaser Mars-130 with EFR 130w tube
    Signature Rotary Engravers (2)
    Epson F6070 Large Format Printer, Geo Knight Air Heat Presses (2)

  4. #4
    Join Date
    Mar 2014
    Location
    Iowa USA
    Posts
    4,485
    Is there warm air blowing out the condenser coil? If not is your compressor running? If nether one I would suspect a control problem. If the compressor is running and no warm air out the condenser, suspect a bad compressor (valves) or a loss of refrigerant.
    Retired Guy- Central Iowa.HVAC/R , Cloudray Galvo Fiber , -Windows 10

  5. #5
    my guess is your refer unit is toast, and the heat generated by simply running is heating the water. That and the laser of course--

    If you can disconnect all the refer workings so only the pump will run, you'll do better. The pump-in-a-bucket may be your best short term option, at least you can add ice cubes--
    ========================================
    ELEVEN - rotary cutter tool machines
    FOUR - CO2 lasers
    THREE- make that FOUR now - fiber lasers
    ONE - vinyl cutter
    CASmate, Corel, Gravostyle


  6. #6
    Join Date
    Oct 2013
    Location
    United States
    Posts
    1,038
    Ok so I don't know a lot about compressors and such but here goes

    On the left side the black thing I'm pointing to that appears to be the compressor yes? It is vibrating so it is running, it is extremely hot, finger burning hot.

    The top silver box is moving a small amount of air below it. The fan on the top is running and moving air outside the machine.

    Does this tell you guys anything?


    chiller-malfunction.jpg
    Trotec Speedy 400 120w, Trotec Speedy 300 80w
    Thunderlaser Mars-130 with EFR 130w tube
    Signature Rotary Engravers (2)
    Epson F6070 Large Format Printer, Geo Knight Air Heat Presses (2)

  7. #7
    Join Date
    Mar 2015
    Location
    Arkansas
    Posts
    137
    Kieth I would take to a local ac shop. Could be low Freon or bad compressor. These don't usually have taps on them to fill and check Freon. The appliance guys have tools that puncture the copper lines and add fittings. They also know about start and run capacitors. They may save you some money in the end.
    Thunder Laser MARS 90 (130 watt)
    RD Works V8
    1 Phillips Screwdriver
    1 Straight Edge
    1 Hammer
    1 Dull Chisel
    1 Pencil Sharpener (manually operated)

  8. #8
    Join Date
    Apr 2015
    Location
    Austin, TX
    Posts
    590
    Quote Originally Posted by Ron Gosnell View Post
    Kieth I would take to a local ac shop. Could be low Freon or bad compressor. These don't usually have taps on them to fill and check Freon. The appliance guys have tools that puncture the copper lines and add fittings. They also know about start and run capacitors. They may save you some money in the end.
    This is good advice. I tend to agree it is probably low Freon or bad compressor. If it's running full time, and all the fans are on, then it's not a controller or sensor issue. Compressors either run and cool or they don't (they never intentionally run and don't cool based on a setting).**

    Edit: **I'll add that this is based on my knowledge of commercial food and beer coolers. There may very well be something different with your smaller unit.
    Last edited by Keith Downing; 12-06-2016 at 6:10 PM.
    60W, Boss Laser 1630
    75W, Epilog Legend 24EX
    Jet Left Tilting table saw and Jet 18" Band saw
    Adobe Creative suite and Laserworks 8

  9. #9
    Join Date
    Mar 2014
    Location
    Iowa USA
    Posts
    4,485
    Looks like a small rotary compressor. Is the underneath side of the air cooled condenser coil above clean of dirt and fan running full on? Also the discharge line coming out the the compressor should be hot and it looks like there is a electric solenoid valve Tee'd into it, is that correct? Sometimes on smaller units the compressor will run all the time and when its not calling for cooling they open that valve electrically and bypass hot gas into either the suction line or evaporator. There are better ways for temperature control, but we are looking at a price point.

    PS I still have my gauges and vacuum pump etc, how far are you from Iowa?
    Last edited by Bill George; 12-06-2016 at 6:54 PM.
    Retired Guy- Central Iowa.HVAC/R , Cloudray Galvo Fiber , -Windows 10

  10. #10
    Your thoughts make sense Bill. After some basic online research, I could not tell how these systems control water temp if they get too cold. I have seen a more sophisticated type of digital hot gas bypass controller on SMC and Shinwa units, but there is usually a heater function also built into the systems. I agree with the others, that you can never discount low coolant or a bad compressor, but you would hate to spend that kind of money to find out you had a stuck valve or relay. Something to be said about taping components with a screw driver. Looking forward to hearing what the root cause is Keith.

  11. #11
    Join Date
    Dec 2010
    Location
    NW Arkansas
    Posts
    1,957
    Blog Entries
    1
    I would imagine low freon. Especially if compressor is hot. It is trying to work...
    I assume you are pumping water.
    And I've got a 5000 and it is set at 19.7C. Room is about 18. Compressor comes on about every 30 minutes for maybe 30 seconds when I'm not running, laser pushes temp up to 20c and compressor will come on till back near 19c.
    Woodworking, Old Tools and Shooting
    Ray Fine RF-1390 Laser Ray Fine 20watt Fiber Laser
    SFX 50 Watt Fiber Laser
    PM2000, Delta BS, Delta sander, Powermatic 50 jointer,
    Powermatic 100-12 planer, Rockwell 15-126 radial drill press
    Rockwell 46-450 lathe, and 2 Walker Turner RA1100 radial saws
    Jet JWS18, bandsaw Carbide Create CNC, RIA 22TCM 1911s and others

  12. #12
    Join Date
    Mar 2014
    Location
    Iowa USA
    Posts
    4,485
    I used to work on these systems using hot gas bypass, and if the bypass valve is leaking internally or the coil burnt out they will go into dumping hot gas back into the system. The largest one I ever worked on with that system was over to the Firestone plant here, and it had a 75 Hp refrigeration compressor running a air dryer. Cycling the compressor on and off is a poor way of exact temperature control.
    Retired Guy- Central Iowa.HVAC/R , Cloudray Galvo Fiber , -Windows 10

  13. #13
    Join Date
    Oct 2013
    Location
    United States
    Posts
    1,038
    Thanks, great suggestions all around. I think I will see if there is an ac shop I can take it to per Rons suggestion.
    Trotec Speedy 400 120w, Trotec Speedy 300 80w
    Thunderlaser Mars-130 with EFR 130w tube
    Signature Rotary Engravers (2)
    Epson F6070 Large Format Printer, Geo Knight Air Heat Presses (2)

  14. #14
    Join Date
    Oct 2013
    Location
    United States
    Posts
    1,038
    Quote Originally Posted by Bill George View Post
    Looks like a small rotary compressor. Is the underneath side of the air cooled condenser coil above clean of dirt and fan running full on? Also the discharge line coming out the the compressor should be hot and it looks like there is a electric solenoid valve Tee'd into it, is that correct? Sometimes on smaller units the compressor will run all the time and when its not calling for cooling they open that valve electrically and bypass hot gas into either the suction line or evaporator. There are better ways for temperature control, but we are looking at a price point.

    PS I still have my gauges and vacuum pump etc, how far are you from Iowa?
    Thanks Bill long ways away unfortunately in Oklahoma
    Trotec Speedy 400 120w, Trotec Speedy 300 80w
    Thunderlaser Mars-130 with EFR 130w tube
    Signature Rotary Engravers (2)
    Epson F6070 Large Format Printer, Geo Knight Air Heat Presses (2)

  15. #15
    Join Date
    Oct 2013
    Location
    United States
    Posts
    1,038
    Quote Originally Posted by Ron Gosnell View Post
    Kieth I would take to a local ac shop. Could be low Freon or bad compressor. These don't usually have taps on them to fill and check Freon. The appliance guys have tools that puncture the copper lines and add fittings. They also know about start and run capacitors. They may save you some money in the end.
    Ron what would an ac store be called? Did some googling didn't find much except ac repair technicians like you'd call to your house.