  1. #1

    Breaker trpping w/o turning on saw

    Just got my saw back from my neighbor. I wired the motoy back up for 220, plugged it in, and it tripped the breaker. I unplugged the saw flipped the breaker on and there was no issue with the breaker. I unplugged my motor so that there was only electric going to the switch and there was no problem. The breaker only trips when the motor gets plugged in, and the motor isn't even on. I hit the red reset button several times no dice. I checked the wiring twice and it looks right to mr.
    IMG_3416.jpg IMG_3417.jpg
    Help!

  2. #2
    Join Date
    Sep 2010
    Location
    Livonia, Michigan
    Posts
    780
    I usually try to stay out of the electrical problems, the norm is just enough info to make things confusing.

    In your picture it APPEARS that you have the white wire and the green wire on the same terminal. If the white is one of the phases and the green is ground the breaker will trip.

    From the picture it looks like terminals 1 and 5 are at the top of the picture but the diagram have them at the bottom. So I'm not clear on which way is up.

    -Tom

  3. #3
    As Mr. Stenzel has pointed out........it appears upside down. Hard to tell. Sometimes you find numbers stamped on or near the tabs.....the picture is too blurry to see but I think I see numbers. As if you connect the wires corresponding to the numbers provided on diagram.

  4. #4
    Join Date
    Sep 2009
    Location
    Medina Ohio
    Posts
    4,534
    For 220 the white is a hot and the green is a ground there is no neutral so the green and white are causing a short

  5. #5
    Colin, I agree with Jerome on this one. You have a direct short. The brown lead is buried underneath the white lead. Remove the brown lead and plug it onto the terminal at the top left of the block. Then the white lead takes the place of the previously removed brown lead. Hopefully, problem solved. Cross your fingers and mail me the $100 service fee. Good luck, buddy. Electrical issues can be a bugger.

  6. The green & white do seem to be connected together, dead short.

  7. #7
    Join Date
    Mar 2006
    Location
    SoCal
    Posts
    22,513
    Blog Entries
    1
    Now's when you wish you took a picture before you rewired it for the neighbor ;-) Other things aside, the green is frame ground and should not be connected to your hot lead.
    "A hen is only an egg's way of making another egg".


    – Samuel Butler

  8. #8
    Join Date
    Feb 2016
    Location
    NE Iowa
    Posts
    1,246
    Colin,

    The problem is with your wiring coming from the power plug. The green lead is the frame ground coming directly from the cord. It should be connected directly to the motor frame, usually by putting it under one of the screws attaching the wiring cover plate - like the one at the very top of your picture. When plugged into a 110 V outlet, the frame ground and the white line lead are both at ground, so the arrangement you have would work fine. With a 220 V outlet, both the white and black line lead are "hot", and having them on connected as you do creates a direct short. The white and black line leads from the cord are both correctly connected.

    Note that you also have to replace the plug on the cord with an appropriate 220 V plug properly wired. It will either have one of the two flat blades turned 90 degrees from the orientation found on 110V plugs, or have both of them turned 45 degrees. Google "220V US plug image" to see what I mean.

    If by chance you didn't change the plug when the machine went to your neighbor's shop, and your shop doesn't have the kind of plug I describe above, then your shop is probably not actually wired 220.

    I believe you have the actual motor wires (red, brown, blue) right for 220V operation.

  9. #9
    Quote Originally Posted by Steve Demuth View Post
    When plugged into a 110 V outlet, the frame ground and the white line lead are both at ground, so the arrangement you have would work fine.
    It would work, but it would be wrong and unsafe. Ground and neutral must be separated, and only bonded at the main panel.

  10. #10
    Join Date
    Feb 2016
    Location
    NE Iowa
    Posts
    1,246
    Dan,

    Totally agree. Should not have used the words "work fine" and no one should wire a motor that way. The evidence suggests though that that is how the borrower had it wired. Colin clearly didn't decide to put the green wire on that terminal, as he's just trying to follow the motor wiring instructions, which obviously don't say anything about where you put the frame ground.

  11. #11
    Thank you everyone for responding, and Happy Thanksgiving.
    There is a power plug for 220v on the pwrr cord.
    The diagram and the actual terminal plate are askew from one another.
    I understand that tje ground and lines should be separate, but looking at the numbering I thought I have it correctly.
    IMG_3418.jpg

  12. #12
    IMG_3426.JPGIMG_3424.jpgIMG_3417.jpg
    As you can see, the line wire is on terminal 4 and brown is on terminal 6 as dictated by the wiring diagram. I guess I'm confused?
    Last edited by Colin Tanner; 11-24-2016 at 4:02 PM.

  13. #13
    Just talked to my brother in-kaw, who installs appliances, and he said that sometimes neutral and ground are connected. He suggested pulling the line conneced to the ground and try it. It was just an idea, but it worked. What gives?

  14. #14
    Your brother-in-law is wrong. Ground and neutral are NEVER connected at the load.

    The reason it worked is because you've got the ground wire (green) connected to the wrong place in the motor. You've short-circuited it. In your middle picture, see that screw at the very top that goes into the painted black portion? The one that nothing is connected to? That's where your green wire goes.

    EDIT: Also, reconnect that "floating" white wire to terminal #4 (where the ground wire is, now)

  15. #15
    Join Date
    Feb 2016
    Location
    NE Iowa
    Posts
    1,246
    Colin,

    As I said before, you have to remove the green power cord wire from terminal 4 and attach it to the motor frame by putting it under the bronze screw at the top of your photo. The white power cord wire then goes on terminal 4.

    So, you end up with the following:

    Terminal 1 (lowermost on your original photo): Black wire from power cord.
    Terminal 2 (upper right corner): Red and Blue wires from motor.
    Terminal 4 (center of picture): White wire from power cord.
    Terminal 5: (upper most in your picture): empty.
    Terminal 6: (single tab at far right of your picture): Brown wire from motor.

    And, again, the green wire from cord goes on the motor housing.

    You have the right 220V plug. Check that the green wire is connected to the ground pin (rounded pin), and the white and black wires are connected to the two blade-like power pins.

    Then you're good to go. If you have any doubts, just wire it up and send a picture of the results on both ends before you power it up.

    As I said in my earlier post, the configuration your friend had this wired with worked because with a 110V source, the frame ground (green wire) and neutral (white wire) CAN be wired together. They shouldn't be, because it makes the setup less safe than the proper configuration, but it will work. When you switch to 220V, it will no longer work, because in a 220V wiring, both the white and black wires are powered relative to the true ground (the frame ground). So, with the white wire and green wire on the same terminal, you've got a direct short to ground. So, your break blows to keep the wires from melting.
    Last edited by Steve Demuth; 11-24-2016 at 4:48 PM.