Originally Posted by
Malcolm McLeod
I believe amp draw for 10Hp at 240V/1phase is typically 40 amps. That's #8 AWG wire.
15Hp at 240V/1phase is typically 60 amps. That's #6 AWG wire.
...And both assume you're not running it to the back-40 (I think sizes are for 50ft or less??). If you need it, I hope you own a copper mine!
Whether the motor is running at single phase or 3 phase, it will require the same power to produce the same HP. So assuming the same input voltage, the total current will be the same for either single phase or 3 phase. But with the 3 phase, the current will be divided over three wires, instead of two as in single phase. So you could use smaller wire for the 3 phase, but you have to run an additional wire.
I would guess that the total amount of copper is about the same for either.
Mike