Thread: How many watts and amps do laser cutters take?

  1. #1

    How many watts and amps do laser cutters take?

    I know the tube wattage. But the overall wattage and amps is what I'm interested in. I know different machines will take different kinds of power. But I have a 220volt 50watt machine. I don't want to blow my breaker. I know 50 / 220 gives me .22ma. But that is just the tube? Anyone?

    Thanks

  2. #2
    Join Date
    Mar 2011
    Location
    Olalla, WA
    Posts
    1,532
    50W/220V = 227mA (but the input values are wrong)

    There are huge losses. It takes four or five times as much watts going in as to what you get out. Your laser is probably running around 20,000V and 25mA, that would give you 50W. The total draw may be a couple hundred watts for just the laser.

    The motors of course use a bit of current, so does the air assist, and the exhaust fan is probably the biggest single consumer of electricity in the system. However, with just a 15A breaker on your 220 circuit you will be good for 3,000 watts, you will probably use less than half that.
    Shenhui 1440x850, 130 Watt Reci Z6
    Gerber Sabre 408

  3. #3
    Join Date
    Jul 2005
    Location
    Sammamish, WA
    Posts
    7,630
    When I added the (45 watt)laser in 2006 the difference in my electric bill, running 8 hours a day with exhaust, maybe 1/3 of that with air assist pump was only $20. Rates have gone up a bit since then but we are still at only about 7 cents/kWh. I would agree that 1,500 watts total is probably about right.



    Sammamish, WA

    Epilog Legend 24TT 45W, had a sign business for 17 years, now just doing laser work on the side.

    "One only needs two tools in life: WD-40 to make things go, and duct tape to make them stop." G. Weilacher

    "The handyman's secret weapon - Duct Tape" R. Green

  4. #4
    Join Date
    Jul 2007
    Location
    Michelmersh, ROMSEY, Hampshire UK
    Posts
    1,020
    My 60W Epilog draws about 1.5kW power from the mains when engraving at full power and highest speed.

    Measured with a meter and enough to make my 2000VA (1.4kW) UPS complain after about five minutes.

    Rich's guestimate seems about spot-on!
    Last edited by Michael Hunter; 03-27-2014 at 9:05 PM.
    Epilog Legend 32EX 60W

    Precision Prototypes, Romsey, UK

  5. #5
    Rich is pretty much bang on, at best Glass tubes are about 10% - 12% plug efficiency just for the resonator. RF's are a bit better but not a huge amount.

    cheers

    Dave
    You did what !

  6. #6
    After moving in the landlord let me know a previous tenant ran space heaters and kept on blowing the breaker making me nervous.

    Also when I plugged the unit in there was no power. My power supply was not working. I've ordered a new one, but now I'm nervous about the electrical quality. I did have to manually ground the plug to a pipe.

  7. #7
    If you are worried about the wiring not being good enough to run your laser you can always run new new wire and a new circuit breaker and have a dedicated circuit just for your laser that you you know it can carry the current needed.
    Universal M-300 (35 Watt CO2)
    Universal X-660 (50 Watt CO2)

    Hans (35 watt YAG)
    Electrox Cobra (40 watt YAG)


    Glass With Class, Cameron, Wisconsin

  8. #8
    Join Date
    Mar 2011
    Location
    Olalla, WA
    Posts
    1,532
    Quote Originally Posted by Clark Pace View Post
    After moving in the landlord let me know a previous tenant ran space heaters and kept on blowing the breaker making me nervous.
    One space heater on a 120V circuit will draw around 12A. That and something else on that circuit could easily blow a 15A breaker. Two space heaters is a near guarantee that you will blow a breaker.

    Are you using you laser with a 220V outlet or are you using a 110 to 220V converter? If the latter, then you might want to try to put something on a separate circuit since you may be getting close to 15A.

    Also, these seems to be a good time for a reminder: the purpose of a breaker is to protect the wiring between the breaker box and the outlet, not to protect the appliance. This is why you do not swap to a larger breaker, the breaker is sized to the wiring not the device.
    Last edited by Rich Harman; 03-28-2014 at 1:20 PM.