Originally Posted by
Michael W. Clark
The motor is working harder, reference your TCF example. The BHP went up. More air is being pulled at a higher pressure, and the fan is more efficient, but it is requireing more BHP/CFM. The increase in DP is more than the increase from flow, there is at least an addition 1" of SP required and one can only assume this is from the vanes. Even though the fan curve has shifted up due to a higher efficiency, they are at an operating point that is higher on the fan curve. The higher up the curve you move, the closer you get to an unstable operating point.
I did not say "always," I said "can." In the case of retired2 (at my site), he found adding straighteners reduced motor draw while also increasing airflow:
"What I've since discovered is that it isn't an aberation at all, but rather it is part of a consistent pattern that shows the addition of an air straightener allows the fan to move more air with fewer amperes. If you go back to my test data and compare the numbers for a given test without the air straightener to the same test with the air straightener, you will see that in every case the fan is moving more air with fewer amps when the air straightener is installed. So, if your DC is marginally powered for your system, as mine is, milking every last ounce of performance out of the fan is important." Reference: My forum, which I cannot link here. PM me if you need links.