    110v, 115v, 120v - Electricians and/or EE's Does it matter?

    I'm hoping someone can shed some light on "voltage" ratings for outlets, switches and appliances. I've read that for all practical considerations, that an outlet or switch rated at 110v 20 amp, versus 115v 20 amp, versus 120v 20 amp are equivalent. Such that if you install outlets that are rated 110v 20 amp, you are safe to use them to power motors spec'd at 120v 20 amp.

  2. #2
    Join Date
    Jan 2010
    Location
    Bellingham, Washington
    Posts
    1,149
    It's my understanding that all outlets are 120 volt or 240 volt and that 110 is just a laypersons number. You are definitely safe using a 120v 20 amp.

  3. #3
    Join Date
    Nov 2007
    Location
    Glenelg, MD
    Posts
    12,256
    Blog Entries
    1
    Technically, what is supposed to be at every outlet in your house is 120V. Once you take into account resistive losses, long line lengths, etc. it can vary a bit once it makes it to your house (particularly if you're far away from the main grid). You'll see mention of 110V, 115V, and so on, and many people may actually measure something similar at their wall, but it's designed to be 120V (and 240V when used across both phases, not the 210V, 220V, etc. you often see).

    So, with that in mind, most things will work just fine on 110V, even if it was designed to run off of 120V. Electronics are downconverted to 12V, 5V, etc., so a little less at the high end is irrelevant. Motors, on the other hand, prefer to run at the voltage they were designed for. Running at a lower voltage increases the heat from the windings, so you want to watch the line from getting too low. Old refrigerators, well pumps, etc. can be victims of this. Newer equipment can often be controlled indirectly by microprocessors that handle variances in the line voltage, so they're somewhat safe to use on the lower voltages.
    Hi-Tec Designs, LLC -- Owner (and self-proclaimed LED guru )

    Trotec 80W Speedy 300 laser w/everything
    CAMaster Stinger CNC (25" x 36" x 5")
    USCutter 24" LaserPoint Vinyl Cutter
    Jet JWBS-18QT-3 18", 3HP bandsaw
    Robust Beauty 25"x52" wood lathe w/everything
    Jet BD-920W 9"x20" metal lathe
    Delta 18-900L 18" drill press

    Flame Polisher (ooooh, FIRE!)
    Freeware: InkScape, Paint.NET, DoubleCAD XT
    Paidware: Wacom Intuos4 (Large), CorelDRAW X5

  4. #4
    Join Date
    Jul 2010
    Location
    Northern Kentucky
    Posts
    3,279
    105 ,110 ,115,120,125 volts do make a different when apply to a lamp bulb a high voltage will cause the bulb to be extra bright, the older transformer were rated for a lower voltage if I not mistaken

  5. #5
    Join Date
    Oct 2009
    Location
    Pacific Northwest
    Posts
    281
    What Dan said...also depending on where you live voltage varies. If you live out in the sticks it is likely at the higher end.
    I am not an electrician, but I play one from time to time...

  6. #6
    Join Date
    Dec 2006
    Location
    Seattle/Tacoma
    Posts
    12
    In a less than perfecxt world, ten per cent up or down should be okay on voltage. What I've been finding a lot of lately are cheap capaciters that just don't last. A capacitor not living up to it's rating can reak havoc, hot motor, burnout, etc.

  7. #7
    Join Date
    Jan 2010
    Location
    LA & SC neither one is Cali
    Posts
    9,447
    110V is a legacy term left over from ages gone by
    115V comes from the design side, equipment is normally designed to run on 115V +/- 10%
    120V comes from the supply side, under standard conditions electrical utilities deleiver electricity at 120V +/- 5%

    In the end for us the numbers mean the same thing, just as 220/230/240 mean the same thing BUT 208V does NOT.
    Of all the laws Brandolini's may be the most universally true.

    Deep thought for the day:

    Your bandsaw weighs more when you leave the spring compressed instead of relieving the tension.

  8. #8
    Join Date
    Feb 2003
    Location
    Doylestown, PA
    Posts
    7,551
    Quote Originally Posted by Nick Lazz View Post
    What Dan said...also depending on where you live voltage varies. If you live out in the sticks it is likely at the higher end.
    I am not an electrician, but I play one from time to time...
    Higher voltage is not just in remote areas. Where I live I can see the steam from exhausted neutrons at the Limerick nuke plant. The times I've checked line voltage - generally during hot spells with high air conditioning loads we run 124/248 volts. Just speculating here - no a sparky pro of any description - but I'm guessing they run as high as they can get by with to keep line & transformer temps down or capacity up? Higher volts require less amps to transport the same number of watts? We haven't had any electrical problems in the 16 years we've lived here so I'm not complaining.

  9. #9
    Join Date
    Jan 2010
    Location
    Lafayette, Indiana
    Posts
    1,378
    My question was motivated by a discussion in another thread regarding remote control units for DC's. The OP asked about remote control units rated for 120v 20 amp. I suggested the iVac Pro which is rated at 115v 20 amp https://www.mbrightonline.com/ecomme...?ecategoryid=9.

    The OP is concerned that since this module is not rated 120v 20 amp, it would not be up to snuff. My thought was that for this application the 115v 20 amp rating is essentially the same as a 120v 20 amp rating.

    In many respects it is kind of a mute point as it relates to the OP, since the manufacturer now is stating that anyone running 1.5 HP or more should use a contactor in conjunction with the switch (use the switch to turn on the contactor). But still I thought it would be good to hear from those who understand this topic a little bit better about the appreciable difference between the ratings. I note that Leviton's 20 amp outlets are now rated at 125v.

  10. #10
    Join Date
    Jul 2010
    Location
    Northern Kentucky
    Posts
    3,279
    I forgot what my actual voltage are suppose to be but the multimeter read my voltage at 127 if I recall right, the electric company assume me that my voltage are okay

  11. #11
    The voltage on commercial electrical power lines fluctuates, depending on the load. There are some loads--big motors, for example--that draw substantially more current when starting up than when running. Back in the early days of my career as a broadcast engineer, I worked at a high-power UHF TV station. When we fired up the big power supplies (the beam supplies for big klystron tubes), the fluorescent lights all over the building would go out for a fraction of a second.

    The nominal voltage of electrical service--120/240 in the US--is the average voltage over time. Depending on whose set of standards you look at, the voltage could vary as much as +5% -13%. Properly designed electrical equipment is designed to deal with those variances. The NEMA (National Electrical Manufacturer's association) standard calls for electrical appliances and equipment to be designed to operate between -10% and +10% of nominal nameplate voltage. A motor with a nameplate rating of 115 volts is therefore designed to operate between 103.5 and 126.5 volts.

    Bottom line: don't worry about it.

    D.
    I finally figured out how to deal with sawdust in my hair.

    I shaved my head.

  12. #12
    Join Date
    Nov 2007
    Location
    Glenelg, MD
    Posts
    12,256
    Blog Entries
    1
    Dan,

    Those huge supplies are scary pieces of equipment. When I worked for a telecommunications consulting firm, the owner's son was out on a field call from a client with an AM tower. He didn't know the gate around the tower was there for a reason, so he put his hand out to lean on the tower. Needless to say, the spark that shot out of the tower did a bit of damage to his finger and made sure he never did that again.
    Hi-Tec Designs, LLC -- Owner (and self-proclaimed LED guru )

    Trotec 80W Speedy 300 laser w/everything
    CAMaster Stinger CNC (25" x 36" x 5")
    USCutter 24" LaserPoint Vinyl Cutter
    Jet JWBS-18QT-3 18", 3HP bandsaw
    Robust Beauty 25"x52" wood lathe w/everything
    Jet BD-920W 9"x20" metal lathe
    Delta 18-900L 18" drill press

    Flame Polisher (ooooh, FIRE!)
    Freeware: InkScape, Paint.NET, DoubleCAD XT
    Paidware: Wacom Intuos4 (Large), CorelDRAW X5

  13. #13
    Quote Originally Posted by Dan Hintz View Post
    Dan,

    Those huge supplies are scary pieces of equipment. When I worked for a telecommunications consulting firm, the owner's son was out on a field call from a client with an AM tower. He didn't know the gate around the tower was there for a reason, so he put his hand out to lean on the tower. Needless to say, the spark that shot out of the tower did a bit of damage to his finger and made sure he never did that again.
    He was a lucky guy. RF energy burns from the inside out and the burns can be particularly painful. I've been bitten by a few AM's over the years. At lower power levels, it's seriously unpleasant. At higher power levels, it can be seriously life-shortening.

    D.
    I finally figured out how to deal with sawdust in my hair.

    I shaved my head.

  14. #14
    Join Date
    Feb 2008
    Location
    Northern, New Jersey
    Posts
    76
    Blog Entries
    3
    Joe, I think you have shown me the way! It appears the surge of my dust collector starting, as well as high amp output while running, causes the plug connection between my dust collector and the remote control unit to be welded together! (I am still awaiting receiving a amp meter to confirm my dust collector motor's output.)

    It looks like the answer is to install a relay switch (contactor) between the dust collector and remote control. Yes, I know it is more expensive. It should solve my welding problem and having to replace remotes every so often.

    Nice to see IVac has added a remote controller. I may want to go their components the whole way.

    What does OP mean?


    Quote Originally Posted by Joe A Faulkner View Post
    My question was motivated by a discussion in another thread regarding remote control units for DC's. The OP asked about remote control units rated for 120v 20 amp. I suggested the iVac Pro which is rated at 115v 20 amp https://www.mbrightonline.com/ecomme...?ecategoryid=9.

    The OP is concerned that since this module is not rated 120v 20 amp, it would not be up to snuff. My thought was that for this application the 115v 20 amp rating is essentially the same as a 120v 20 amp rating.

    In many respects it is kind of a mute point as it relates to the OP, since the manufacturer now is stating that anyone running 1.5 HP or more should use a contactor in conjunction with the switch (use the switch to turn on the contactor). But still I thought it would be good to hear from those who understand this topic a little bit better about the appreciable difference between the ratings. I note that Leviton's 20 amp outlets are now rated at 125v.
    Last edited by Bob Landel; 01-23-2012 at 11:34 PM.