  1. #1

    what gauge wire

    I just purchased a used dust collector I'm not sure what gauge wire I need to run from he panel to the plug.
    it's a 3hp motor it draws 18 amps wired for 220 volts.

  2. #2
    Join Date
    Nov 2007
    Location
    Milwaukee, WI
    Posts
    900
    10g on a 30 amp circuit

  3. #3
    Thank you that's kind of what I thought but I wasn't sure.

  4. #4
    Join Date
    Feb 2003
    Location
    Doylestown, PA
    Posts
    7,576
    You can use 10 ga., you don't have to. I'm pretty sure 12 ga. is good to 25 amps on a motor. A 20 amp circuit should be adequate unless the DC's manual specifies otherwise. What may matter is the circuit breaker. Some seem to be motor rated and will tolerate brief loads in excess of their rated amperage, others are not and will produce nuisance trips. A 3 h.p. dust collector will probably have a starting amp. spike of around 40 amps, maybe more. Do you need a 40 amp circuit? No.

  5. #5
    Join Date
    Feb 2003
    Location
    South Windsor, CT
    Posts
    3,304
    Quote Originally Posted by Curt Harms View Post
    ... I'm pretty sure 12 ga. is good to 25 amps on a motor ...
    The only time #12 is good for 25 amps is if it's individual conductors like THHN/THWN run in raceway (conduit). #12 NM cable ("Romex" is a brand of NM cable) is only rated for 20 amps.

  6. #6
    Join Date
    Feb 2003
    Location
    Doylestown, PA
    Posts
    7,576
    Quote Originally Posted by Rob Russell View Post
    The only time #12 is good for 25 amps is if it's individual conductors like THHN/THWN run in raceway (conduit). #12 NM cable ("Romex" is a brand of NM cable) is only rated for 20 amps.
    Thanks. I wonder about use as an extension cord where the cable is not enclosed in a wall. Either way, 12 ga. is adequate for an 18 amp load, isn't it?

  7. #7
    Quote Originally Posted by Curt Harms View Post
    Thanks. I wonder about use as an extension cord where the cable is not enclosed in a wall. Either way, 12 ga. is adequate for an 18 amp load, isn't it?
    Curt, I wouldn't think so from a protection standpoint. You're so close to the max nominal rating of 20 amps for a 12 gauge circuit, even if it was indiv. wires like Rob pointed out in a conduit and you're bumped up to a 25 amp rating. Why take a chance, just run 10 gauge and the correct cicuit breaker and be done with it. This way you have some tolerance room for aging or other issues built into the circuit and you're not maxed out like using 12 gauge wiring would leave you.

  8. #8
    Join Date
    Nov 2007
    Location
    Milwaukee, WI
    Posts
    900
    The cost to run a 10 gauge 30A 240V circuit versus 12/20 is a few bucks more unless it's a long wiring run, which needs to be the 10/30 anyway. I really don't get some of these responses...

  9. #9
    The other variable that has not been given much mention is the length of the run.

  10. #10
    Join Date
    Feb 2003
    Location
    Doylestown, PA
    Posts
    7,576
    Quote Originally Posted by Steven Wayne View Post
    The other variable that has not been given much mention is the length of the run.
    Yeah, for some reason I was thinking this was from an outlet to the saw.

  11. #11
    Join Date
    Nov 2007
    Location
    Milwaukee, WI
    Posts
    900
    Quote Originally Posted by Curt Harms View Post
    Yeah, for some reason I was thinking this was from an outlet to the saw.
    It's not from an out let to the saw, it's a circuit for a new dust collector.

  12. #12
    And the answer is:

    10 ga wire with a 20 amp breaker. 10 ga because it is big enough, with a little extra in view of the ability of most dust collectors to go over current when no hose is installed. And 20 amps to protect the wiring of the dust collector, which is probably less than 10 ga. As George mentioned, wiring is not the place to cheap out.

  13. #13
    Join Date
    May 2005
    Location
    Highland MI
    Posts
    4,524
    Blog Entries
    11
    And my answer is:

    10 ga wire with a 25 amp 2 pole breaker. A 20 amp breaker is only good for a 16 amp load (80% of the rated circuit load). If you can't find 25 amp breakers, 30's will do. Your mag starter provides motor overload protection. Your breaker provides wire overload protection. You do have a mag starter right?

  14. #14
    220v dictates a double pole breaker my guess is you will be hard pressed to find a 25 amp breaker and a 20 amp isn't big enough as was pointed out above so you are likely going to end up with a 30 amp breaker

    this is not a place for cutting it close use the 10ga wire and the 30 amp breaker and save the fire extinguishers for something you can't control

    to add to what George already said the cost to use the correct wire and breaker is not alot more than to use the wrong stuff initially and potentially is alot less when you factor in the fire hazard you would create by using wire and breakers too small for the intended use

    rememeber , to paraphrase Smokey Bear, only you can prevent shop fires !!! be safe everyone the people who love you will be happier
    Last edited by Don Alexander; 09-05-2011 at 1:02 AM.

  15. #15
    The length of the run is approx. 50ft. I went with the original suggestion of 10 gauge wire and a 30 amp breaker. I felt the extra expense was worth having the extra margin of safety.