    #10 Power Cord Options

    Hey all,

    I need to hook up my table saw and rather than hard wire the TS I wanted to install a power cord/receptacle for it. The TS requires a 30a breaker so I need to use 10ga wire.

    Here are a couple of options I thought of:

    1. A 6' dryer cord (about $10)

    2. Run #10's in flexible metal conduit using the correct plug (I have everything but the plug)

    3. Buy a 25' section of #10 extension cord and use less than 10ft of it and add the correct plug ($45)

    4. Another option that I can't think of

    The saw will be positioned in a way where the cord will be out of the way but I don't really want to take a chance on nicking the cord.

    What are your thoughts?

    TIA,
    Doug

  2. #2
    Join Date
    Dec 2003
    Location
    West of Ft. Worth, TX
    Posts
    5,815
    Option 4: Buy 10 gauge by the foot, add appropriate end and strain relief. That's what I did for mine. But be careful, where the cord into the switch probably won't accept 10 gauge wire without modification. I think the cord from the factory on mine is 14 gauge. Same thing on my BS. I haven't changed it out since the factory cord reaches the receptacle. Jim.
    Coolmeadow Setters...Exclusively Irish! When Irish Eyes are smiling....They're usually up to something!!
    Home of Irish Setter Rescue of North Texas.
    No, I'm not an electrician. Any information I share is purely what I would do myself. If in doubt, hire an electrician!
    Member of the G0691 fan club!
    At a minimum, I'm Pentatoxic...Most likely I'm a Pentaholic. There seems to be no known cure. Pentatonix, winners of The Sing Off, s3.

  3. #3
    Join Date
    Mar 2003
    Location
    Southport, NC
    Posts
    3,147
    As Jim says, buy #10 stranded wire by the foot. Any big box will have it. Buy the appropriate 30 amp plug and receptactle.
    Howie.........

  4. #4
    Join Date
    Dec 2009
    Location
    Vadnais Heights, MN
    Posts
    1,607
    Thanks for the responses.

    When I stopped at Menard's last week, they only sold 10/3 stranded in 25ft or 50ft rolls. The 25ft roll was $35 and I was only going to use 8-10ft of it.

    I stopped at Home Depot and they were selling 10/3 for $1.65/ft so I bought some.

    Maybe I can get my saw running tonight!
    Doug

  5. #5
    Join Date
    Dec 2009
    Location
    Vadnais Heights, MN
    Posts
    1,607
    Okay a few more questions:

    I was planning on using a NEMA 10-30P plug and receptacle (similar to a 3 wire dryer receptacle).

    Since I am running 10/3 wire (2 hots and a ground) can I use the third prong for the ground? On the both the receptacle and plug, it say's WHITE on the third prong.

    Is there a reason not to use it for grounding? It would have continuity all the way to the panel.

    Or should I find a different receptacle/plug combination?

    Thanks!
    Doug

  6. #6
    Quote Originally Posted by Doug W Swanson View Post
    I was planning on using a NEMA 10-30P plug and receptacle (similar to a 3 wire dryer receptacle).

    Or should I find a different receptacle/plug combination?
    Technically you should use 6-30 or L6-30. Assuming this is on a wall I'd go with 6-30 with a right-angle plug so the heavy cord falls straight down.

    10-30 is for two hots and a neutral with no ground where you need both 120V and 240V . It would work, but it would be unexpected and thus not ideal.

  7. #7
    Join Date
    Dec 2006
    Location
    Toronto Ontario
    Posts
    11,277
    Hi, a 10-30P is not the correct device.

    Presuming that you have a 240 volt application, 6-30P is the correct device, if 120 volt then you need a 5-30P.

    Regards, Rod.

    P.S. Sorry for the repeat info from Chris, we must have posted at aproximately the same time.
    Last edited by Rod Sheridan; 05-04-2010 at 3:03 PM. Reason: Added Post Script

  8. #8
    It's because of the cord you chose. The old Nema-10 series cords were designed to ground through the neutral.....this is back when that was still legal. My suggestion would be to return it and use the newer L6, twistlock connector (hot-hot-ground). It would be L14 if you wanted 4 conductor (hot-hot-neutral-ground).

    The 10 series will work but can be extremely confusing, especially if you're going to a sub-panel. Anyone else working in your shop might assume that the 3rd conductor is a proper neutral, and may someday wire something up as such, potentially causing code violations and other problems. Twistlocks look cooler anyway.

  9. #9
    Quote Originally Posted by Rod Sheridan View Post
    P.S. Sorry for the repeat info from Chris, we must have posted at aproximately the same time.
    Ditto for me

  10. #10
    Join Date
    Dec 2009
    Location
    Vadnais Heights, MN
    Posts
    1,607
    Thanks for the quick replies.

    This is all going in my basement shop and I am doing the wiring myself (with a permit). I've done a fair amount of wiring but not much when it comes to 240v stuff.

    I will swap out my recept/plug for the correct ones...

    Thanks!
    Doug
    Last edited by Doug W Swanson; 05-04-2010 at 3:17 PM.

  11. #11
    Join Date
    Dec 2009
    Location
    Vadnais Heights, MN
    Posts
    1,607
    Quote Originally Posted by John Coloccia View Post
    It's because of the cord you chose. The old Nema-10 series cords were designed to ground through the neutral.....this is back when that was still legal. My suggestion would be to return it and use the newer L6, twistlock connector (hot-hot-ground). It would be L14 if you wanted 4 conductor (hot-hot-neutral-ground).

    The 10 series will work but can be extremely confusing, especially if you're going to a sub-panel. Anyone else working in your shop might assume that the 3rd conductor is a proper neutral, and may someday wire something up as such, potentially causing code violations and other problems. Twistlocks look cooler anyway.
    Thanks for the info. I am installing a 240 receptacle for my table saw. Since the previous owner of the TS had the saw hard wired, I want to add a cord to it.

    Thanks for the help!
    Doug

  12. #12
    Join Date
    Mar 2008
    Location
    Beantown
    Posts
    2,831
    Just curious...what's the amperage stated on the saws motor plate? A 30 amp circuit and 10 gauge wire is pretty beefy for tablesaw.
    JeffD

  13. #13
    Join Date
    Dec 2009
    Location
    Vadnais Heights, MN
    Posts
    1,607
    The saw is a 5hp Grizzly and needs a 30A breaker.

    The bummer is that I had already ran wire for a 240v, 20A breaker assuming I would buy a 3hp TS when I upgraded. I got a good deal on this 5hp one so I have to redo all of the wiring....

    Doug

  14. #14
    I am sure the electricians will correct me if I am wrong here, but if you are wired to a sub panel, the ground and neutral must remain seperate. I had an electrical inspector tell us that if you connect a neutral and ground together in a sub or beyond you create the potential for an alternate route for current to pass......

    YMMV

    Bryan

  15. #15
    Join Date
    Dec 2009
    Location
    Vadnais Heights, MN
    Posts
    1,607
    Quote Originally Posted by Bryan Rocker View Post
    I am sure the electricians will correct me if I am wrong here, but if you are wired to a sub panel, the ground and neutral must remain seperate.
    I'm going back to the main service panel in my house so this shouldn't be a problem....

    Doug