08-16-2007, 11:47 AM
I just got my G1023SLX!!!!:) The question I have is that the manual says to wire to a 20A, 220V breaker but both electricians that I talked to want to put a 30A breaker in because the motor draws 18A, what would you do or what have you done?

Either way, I assume 10/2 wire will be sufficient, any thoughts?

Thanks!

Steve Clardy
08-16-2007, 11:49 AM
My older 1023 is on a 30amp
10 gauge wiring

Greg Cole
08-16-2007, 11:51 AM
Inrush current on starting that motor will be much higher than the listed 18A. I''d go along with the electrician on the 30A breaker.

Cheers.
Greg

Von Bickley
08-16-2007, 11:58 AM
Depends on the size of your wiring....

#10 copper - good for 30 amps.

#12 copper - good for 20 amps.;)

Montgomery Scott
08-16-2007, 12:19 PM
That seems rather odd that the motor draws 18A as I assume it's a 3hp motor. My unisaw states it draws 12A. I have it on a 30A circuit as I also use the circuit to power my 4.8hp MM16 that has a stated current requirement of 22A.

Curt Harms
08-16-2007, 12:22 PM
Disclaimer-I'm not an electrician or electrical engineer. Having said that;) I suspect a 20 A. circuit wired with 12-2 copper would be fine, 30 amp. circuit wired with 10-2 is fine as well. As far as inrush current, yup, it'd be more than 20 amps. I suspect it'd be a bunch more than 30 amps too but for less than a second. I'm pretty sure circuit breakers and wire will safely carry considerably more than rated amperage for short periods of time. The Grizz cabinet saws have magnetic starters that should include overcurrent protection for the motor.

Worth what You paid for it

Curt

Jason Brown
08-16-2007, 12:25 PM
I think that 18 amp value listed in the manual must already consider the peak inrush current. By my calculation 3hp = 2237 watts. For a 220V circuit, this translates to about 10 amps. I guess I'd call Grizzly direct to confirm.

N.B.: I'm not an electrician, nor do I own a G1023.

SCOTT ANDREWS
08-16-2007, 12:42 PM
I have my 1023 on a 20 A breaker with 10/3 wire and have never tripped it.

Greg Funk
08-16-2007, 12:44 PM
If you're starting from scratch and wiring in a new circuit you may as well go 30A as the incremental materials cost will be small and you will have capacity for future growth in case you want to upgrade to 5HP.

Greg

Chris Friesen
08-16-2007, 1:08 PM
I think that 18 amp value listed in the manual must already consider the peak inrush current. By my calculation 3hp = 2237 watts. For a 220V circuit, this translates to about 10 amps.

You forgot about efficiency and power factor. Rule of thumb is 5A/HP at 240V, so the Grizz motor is probably less efficient than some.

Normally the motor nameplate does not include inrush current, but is rather the "full load amperage" of the running motor. Peak inrush can be 4-6 times as much.

Chris Friesen
08-16-2007, 1:20 PM
I just got my G1023SLX!!!!:) The question I have is that the manual says to wire to a 20A, 220V breaker but both electricians that I talked to want to put a 30A breaker in because the motor draws 18A, what would you do or what have you done?

The simplest route is to use a 30A breaker with #10 wire and a 30A receptacle. This would require changing the saw plug to a 30A plug as well.

The code is interesting for motors. Based on 430.22A, for "continuous" motor loads you're supposed to wire for 125% of the motor full load current rating. You don't actually have a continuous load, so based on table 430.22E a continuous-rated motor on an intermittent "tool head" load should have conductors rated for 140% of the nameplate. (Beats me why a continuous load needs less ampacity than an intermittent one...)

David DeCristoforo
08-16-2007, 1:51 PM
Technically speaking, if the recommendation is for a 20A circuit, that's what you should use. The "logic" that, if you use a 30A circuit, you will have more "headroom" is flawed because the "protection value" of the rated circuit will be defeated. In a "perfect world" all of your 220 machines would be on dedicated circuits. The only reason to use a higher rated breaker would be if you plan to run more than one machine at a time on the circuit. But, as pointed out already, you also have to be sure that your wire size is correct for the breaker value.

Gary McKown
08-16-2007, 1:51 PM
No expert here, but my experience:

My 5-YO 1023 was put on an existing 20-A circuit, #12 wire with a short 15-ft. run to the box (plus another 10 ft. with the cord). I have never had any indication that it does not work well.

The startup on mine is eye-blinking quick - much less than a second to full speed. At first, it actually kinda made me jumpy that there is almost zero wind-up, compared to the 2-4 seconds on the old Craftsman or my 2-hp DC. Makes sense, I guess, with 3-hp cranking only an arbor and saw blade. Sometimes I wish that it came with some sort of soft-start mechanism.

I do not have a peak-hold or surge ammeter, but I did measure the no-load running current at about 9 amps. Haven't measured it under load, but it has never labored even when cutting 10/4 oak material with a Forrest WWII, at modest feed rates.

Rick Christopherson
08-16-2007, 2:00 PM
You don't need a 30 amp circuit, but it won't hurt either, so it all comes down to cost and convenience. If you are doing the wiring, working with #10 wire can be a pain, but if you are having the electrician install the circuit and outlet, then it makes no difference to you. If they are going to charge about the same for either size, then go with the #10, but if the difference is significant, then stick to the 20 amp circuit.

It is not necessary to derate the circuit (125% of load) because this is a cord and plug application, so it is perfectly within NEC code to use the 20 amp circuit for an 18 amp (max) load.

Furthermore, you will not likely ever load a 3 hp saw to the point of reaching its full load amperage rating unless the saw is in a binding situation, in which case, you would be happy to have the breaker trip. When idling, a motor will draw about 1/2 of it full load amperage, so this saw will be drawing 9 amps when not cutting, and about 15 amps when doing moderate cutting.

I also agree that the 18 amps FLA sounds incorrect for even a poor motor. Power = I x V x pf x eff, so with a low efficiency of 0.8 and a powerfactor of 0.8, the 3 hp motor would be drawing 14 amps FLA.

Ryan Marcoux
08-16-2007, 2:44 PM
Thanks guys! I am going with 30A and 10/2 wire.

Don Bullock
08-16-2007, 2:45 PM
I had the same type of question about a 6" jointer I was considering buying from Grizzly. While I realize that I was asking for information on a different tool, it seems to be Grizzly's policy is to provide the maximum draw of a machine on their specs. Here is the email response I received from them.



...Thank you for contacting us with your questions. A 15 amp dedicated circuit is recommended for the G0604 Jointer. Also, a 15-amp dedicated circuit is recommended for the G0452 Jointer.

The 15-amp breaker in each circuit will provide the most protection for each machine. Each breaker should trip when the machine on its circuit is drawing approximately 15 amps for a period of time.

Since the motor on the G0604 should not pull more than 13 amps, a 15-amp dedicated breaker would provide adequate protection for this machine. Also, since the motor on the G0452 should not pull more than 14 amps, a 15-amp dedicated breaker would provide adequate protection for this machine. The proper 15-amp dedicated breakers would allow each machine to start and run properly.


Grizzly's responce is rather puzzeling. They perceive the breaker as being a protection to the machine, not your shop's wiring and possible fire hazzard. This is similar to some information that I found in my SawStop manual. I would say that based on the response I got from them a 20 amp circuit would be fine for you. If you're not sure, give Grizzly a call or send them an email like I did. That will give you a definitive answer from the source, not speculation from me.

Since I just had a new 220 circuit installed in my shop, I can understand that there is a big difference in cost due to the current high price of copper. Because of some savings I was able to provide to my electrician by rerouting the wire and providing some of the material he needed, he installed a 30 amp circuit for the same amount he quoted me for a 20 amp, but he's done a lot of work for me and we get along wery well. Your experience may differ.

Ryan Marcoux
08-16-2007, 2:54 PM
I know that the 110v outlets in my garage must be GFI protected, does this also apply to the 220 service? Is this even possible? The outlet will be extremely close to the garage door (possible wet environment).

Perry Schmidt
08-16-2007, 3:00 PM
I have my 1023 on a 20 A breaker with 10/3 wire and have never tripped it.

Same with me...I've had my 1023 on a 20A breaker for...6 years now? Never tripped it yet.

30A is OK, but I think it's overkill.

Chris Friesen
08-16-2007, 3:49 PM
It is not necessary to derate the circuit (125% of load) because this is a cord and plug application, so it is perfectly within NEC code to use the 20 amp circuit for an 18 amp (max) load.

I'm a bit confused then. 210.1 explicitly says that circuits that supply only motor loads are covered by section 430. Does the fact that it's a cord and plug application override that, even though currently the circuit would be currently dedicated to a motor load?