A question about the main breaker in a house breaker panel. I googled and found no real answer. For a big one say 100-200 amps is it actually a breaker? Or is it just a switch. I always called it the main breaker but that is just the vocabulary I learned over time. If it was a fuse block it would be called a disconnect since it is physically pulled out and totally disconnected. It does not really matter either way I would just like to know.
I have a Square D circuit breaker on my desk right now. I see nothing that says it is a overload breaker. Just the maximum amps it can disconnect about 10,000 and it meets FCC regulations about interference.
Bil lD

John Terefenko
01-10-2021, 1:07 AM
It is a breaker or as you said an overload breaker. It will trip if overloaded or surged. A disconnect can also be a nonfused circuit interrupter. No fuses in the disconnect.

Frank Pratt
01-10-2021, 10:40 AM
The 10,000A is a reference to the maximum short circuit that the supply can deliver. If the service has a short feeder length from a large transformer, then the short circuit current could be very large, even hundreds of thousands A. A 10KAIC breaker might explode or otherwise pose a safety problem if it is called upon to interrupt a short circuit higher than 10,000A. Most residential services are much less than 10,000A short circuit capacity.

Bruce King
01-10-2021, 11:28 AM
Some HVAC and water heater disconnects are just a switch for the serviceman and some have an over current feature. On Square D breakers the current rating is on the tip of the lever. Those large 100 or 200 ones are breakers, the rating is per leg.

Rod Sheridan
01-10-2021, 6:54 PM
The 10,000A is a reference to the maximum short circuit that the supply can deliver. If the service has a short feeder length from a large transformer, then the short circuit current could be very large, even hundreds of thousands A. A 10KAIC breaker might explode or otherwise pose a safety problem if it is called upon to interrupt a short circuit higher than 10,000A. Most residential services are much less than 10,000A short circuit capacity.

Yes, mine is approximately 2,300 amperes on a 100 ampere service. My panel is approximately 18 metres from the transformer...Rod

Rollie Meyers
01-15-2021, 1:46 AM
If it is not a breaker, it will be marked as a "Molded Case Switch" it provides no overcurrent protection if a MCS. The standard AIC, Ampere Interrupting Capacity is 10,000, the next is 22,000, then 42,000, 64,000, the price of the breakers escalates with each increase of AIC. A lot of newer residential panels come with a 22K, AIC rated main as standard now.

Bill Dufour
01-16-2021, 7:19 PM
I always thought it was just a switch. Good to know, thanks for the info. It does explain why they cost so much. I also thought folks who wired in a big breaker and back fed it as the main breaker were rednecks. Now I am not so sure.
Bil lD

lowell holmes
01-17-2021, 3:19 PM
Go to a store that sells electrical items and ask them.

Frank Pratt
01-17-2021, 4:33 PM
Go to a store that sells electrical items and ask them.

His question has already been answered.

Andrew Seemann
01-21-2021, 10:40 PM
I always thought it was just a switch. Good to know, thanks for the info. It does explain why they cost so much. I also thought folks who wired in a big breaker and back fed it as the main breaker were rednecks. Now I am not so sure.
Bil lD

Some panels have a back fed breaker on the branch bus as their main. It has to be mechanically fastened to the panel so it can't be pulled out like a regular breaker. They don't seem as common as panels with a dedicated main anymore though.

Frank Pratt
01-22-2021, 12:30 AM
Some panels have a back fed breaker on the branch bus as their main. It has to be mechanically fastened to the panel so it can't be pulled out like a regular breaker. They don't seem as common as panels with a dedicated main anymore though.

Almost all residential panels I've installed use a conventional breaker that is back fed through to the buss bars. It's still the most common configuration.

Perry Hilbert Jr
01-22-2021, 9:33 AM
My house has a switch of some kind where the power enters the house and that feeds to two boxes in the house. One with a main for the residential part of the house and another box with a main for the shop area..

Bruce King
01-22-2021, 10:27 AM
The code since about 2000 says something like a disconnect switch for the whole house must be near the power meter if the cable run to the main panel is more than 10ft. Once you run the cable up to the ceiling height and then down to the panel it will be over 10ft so basically the interior main panel has to be on the same wall as the power meter or you need a disconnect. I put two 200 amp panels on my previous house and had two disconnects outside. I used 200 amp breakers.

Brian Elfert
01-22-2021, 6:51 PM
The 2020 NEC now requires an exterior disconnect switch for all houses. The 2020 NEC is only in effect in eight states so far. I installed one on my house back in October even though the 2020 NEC was not yet in effect. I was replacing the meter base so I decided to add the disconnect because future plans might require it.

Bill Dufour
01-23-2021, 10:08 AM
Does just a main breaker in the panel next to the meter meet that new code? Sounds like it does to me.
Bil lD

Ronald Blue
01-23-2021, 11:35 AM
My meter base is a 400 amp service with two 200 amp disconnects because one feeds the shop and one the house. This was what was required by the power company in 2018. I think it's called a lever bypass if I recall correctly. There is a main breaker panel in the home and the shop with their own 200 amp main breakers.

Brian Elfert
01-23-2021, 11:41 AM
Does just a main breaker in the panel next to the meter meet that new code? Sounds like it does to me.

Yes, that should qualify. In northern parts of the USA we don’t have the breaker panel outside.

Andrew Seemann
01-23-2021, 12:39 PM
My meter base is a 400 amp service with two 200 amp disconnects because one feeds the shop and one the house. This was what was required by the power company in 2018. I think it's called a lever bypass if I recall correctly. There is a main breaker panel in the home and the shop with their own 200 amp main breakers.

The bypass in the meter box is so they power company can swap out your meter without disconnecting your power. The reason they told me (20 odd years ago) was so that people's burger alarms, internet, and other electronic stuff doesn't have a power loss.

Ronald Blue
01-23-2021, 1:53 PM
The bypass in the meter box is so they power company can swap out your meter without disconnecting your power. The reason they told me (20 odd years ago) was so that people's burger alarms, internet, and other electronic stuff doesn't have a power loss.

That makes sense. Thanks for clarifying the purpose of the lever bypass.

Bruce King
01-23-2021, 3:23 PM
My meter base is a 400 amp service with two 200 amp disconnects because one feeds the shop and one the house. This was what was required by the power company in 2018. I think it's called a lever bypass if I recall correctly. There is a main breaker panel in the home and the shop with their own 200 amp main breakers.

Look at the rating on the meter, they usually put in a 200 amp meter. I requested that they fix mine and they put in a 320 amp, said that was all they had.

Brian Elfert
01-23-2021, 4:14 PM
Look at the rating on the meter, they usually put in a 200 amp meter. I requested that they fix mine and they put in a 320 amp, said that was all they had.

Even though it may be called 400 amp service the norm for residential is just to have a 320 amp meter. You would have to use a LOT of electricity at once to exceed 320 amps at 240 volts.

Ronald Blue
01-23-2021, 6:11 PM
Even though it may be called 400 amp service the norm for residential is just to have a 320 amp meter. You would have to use a LOT of electricity at once to exceed 320 amps at 240 volts.

You are correct. I looked at the documents from the install and it was a 320 lever bypass meter base.