PDA

View Full Version : Shop power estimate



mark mcfarlane
03-24-2017, 10:55 PM
Anyone care to review my 'max simultaneous power' requirements? Am I missing anything? Do these numbers look reasonable?

I am wondering if I can run both the shop and my 2800 sq ft house (in Houston, AC land) on the current 200AMP feed, or if I need to pay the significant fee to bring in a new feed, and maybe a new transformer....



Shop - Max simultaneous power usage
Qty
HP
Note


Amps (running)




Circuit






CU300


1


4.8 HP (230V)
30 amp curcuit, probably only uses 20 amps


30




230V


http://www.scmgroupna.com/en/products/classical-machines.c884/universal-combined-machines.887/cu-300-classic.721


DC40 Stock Feeder


1


0.5 HP




3




230V


http://www.cantekamerica.com/machinery/feeders/dc30-3-roll-variable-speed-power-feeder-2883.html


Dust Gorila Pro


1


5.0 HP (maybe 3HP)
30 amp curcuit, probably only uses 20 amps


20




230V


https://www.oneida-air.com/inventoryD.asp?item_no=XGK050105H&CatId={7F6C8978-92E8-4902-9A37-D8A254EDF4FC}


Shop Lights


30


32 watts
960 watts


8








Radio, mini-fridge








3








AC (mini-split) Shop


9000 BTU / 30.5 SEER




12




230V


http://www.mitsubishielectric.ca/en/hvac/PDF/m-series/Cooling-Heating_SingleIndoorUnit_Spec05.pdf


Studio Lights








3








AC (mini-split Studio)








12




230V






Total Simultaneous Amps








91

John Sayen
03-25-2017, 8:19 AM
I think you should convert all line items to watts and then compare your total watts with your total panel watts capacity.

Will help avoid void any confusion with 110 vs 220 with regard to amp capacity.

jack duren
03-25-2017, 8:23 AM
Why are you asking a woodworking hobby forum to instruct you on electrical issues?

John Sayen
03-25-2017, 8:58 AM
Why are you asking a woodworking hobby forum to instruct you on electrical issues?

I'm not the OP but I imagine because this forum's description is as follows?

Building Electrical, Construction, Shop Layout and Dust Collection: Everything you want to know about housing all those tools!

jack duren
03-25-2017, 9:07 AM
Even a certified electrician on the forum won't guarantee your house from catching on fire.

He should be asking the correct people in his area...

Leo Graywacz
03-25-2017, 9:13 AM
What are you worried about? The worst that can happen is you trip a breaker (as long as everything is compliant). Adding things up looks like a peak of 168 amps total. Most of your machines when not under load draw substantially less. Lights, resistance heat and compressors draw continuous high currents.

jack duren
03-25-2017, 9:24 AM
Should he add to his 200amp or pay to run a separate power to another building. He needs to check with local authorities on this...

mark mcfarlane
03-25-2017, 11:01 AM
Why are you asking a woodworking hobby forum to instruct you on electrical issues?

Jack, I am consulting with my job electrician on this also. He used to teach the NEC code for 10 about years. Seems knowledgable to me.

From this forum I was more concerned about making certain I have identified what the max simultaneous load will be for the shop part of the build, so the chart above is what I call the worst case scenario: jointer running with DC and stock feeder on, all lights on,...

I guess I could add a 2HP compressor recycling in the 'worst case'.

Thanks for chiming in.

Cheers,

John Lanciani
03-25-2017, 11:15 AM
Should he add to his 200amp or pay to run a separate power to another building. He needs to check with local authorities on this...

Why are you so worried about it? Lots of talent and knowledge here...

jack duren
03-25-2017, 11:47 AM
I'm not worried about it. But have seen it too many times run into 40 replies with conflicting answers especially from NON qualified people who read a lot and think their qualified

So lets see if a certified electrician can answer this without a bunch of static for once.

jack duren
03-25-2017, 12:03 PM
Jack, I am consulting with my job electrician on this also. He used to teach the NEC code for 10 about years. Seems knowledgable to me.

From this forum I was more concerned about making certain I have identified what the max simultaneous load will be for the shop part of the build, so the chart above is what I call the worst case scenario: jointer running with DC and stock feeder on, all lights on,...

I guess I could add a 2HP compressor recycling in the 'worst case'.

Thanks for chiming in.

Cheers,

I understand your trying to get info on your needs Mark. I just hope an answer can come without confusing the original question.

On a one man shop it's hard to overcome a 100 amp service. I have 95 amp service off my main into the garage. I can't pull enough by myself to pop the breaker..

The fact that it's a separate building concerned me on insurance with fire....

Ole Anderson
03-25-2017, 1:54 PM
I am not a licensed electrician, but I did stay at a Holiday Inn Express about a month ago, so here goes: To answer your question, I believe you have it covered as you admit you might be 10 amps high on the CU300 (whatever that is) and that would be on one leg, the other leg will be less as some loads are 115 volts. However to be safe I would add in the compressor as you never know when it will decide to kick in.

I have the 2 hp Dust Gorilla and it draws 10 amps with the largest gate open, so you might be a bit low on assuming 20 amps for the 5 hp version.

As far as running it off your existing 200 amp panel, I wouldn't, not on a 2800 sf house in hot Texas. I would ask the electrician to run a second feed off the meter to your shop panel (if allowed by local code and your utility). I have seen that done frequently on 50 amp 240 volt spas. Check with the utility to make sure their secondary feed is adequate. You imply from your post that it is not. I wouldn't assume that when picking your options.

What are you looking at as far as your shop panel? If you go off before your house panel, it wouldn't be a sub-panel.

Jim Andrew
03-25-2017, 2:08 PM
I have a 2 ton ac, a 3hp dc, multiple 4 bulb fluorescent fixtures, and a whole shop of woodworking machines I run on a 100 amp service with no problems.

Art Mann
03-25-2017, 2:27 PM
Double post.

Art Mann
03-25-2017, 2:43 PM
Panels are not rated in watts. They are rated in amps at 240 VAC and there is a good reason. Even if the total theoretical watt capacity of the panel isn't exceeded, the current capacity of one leg could still be exceeded. You have to pay attention to balance as well as wattage capacity. It is the current on the most heavily loaded leg that defines the required panel current capacity. For example, if one leg requires 5 A and the other leg requires 60A then the wiring and panel must be sized for 60A @ 240 VAC. That is just the way it works.


I think you should convert all line items to watts and then compare your total watts with your total panel watts capacity.

Will help avoid void any confusion with 110 vs 220 with regard to amp capacity.

John K Jordan
03-25-2017, 5:08 PM
Jack, I am consulting with my job electrician on this also. He used to teach the NEC code for 10 about years. Seems knowledgable to me.
From this forum I was more concerned about making certain I have identified what the max simultaneous load will be for the shop part of the build, so the chart above is what I call the worst case scenario: jointer running with DC and stock feeder on, all lights on,...
I guess I could add a 2HP compressor recycling in the 'worst case'.


When designing my shop electrical I figured on these possible simultaneous loads:
5 hp ClearVue dust collector (measured 14+ amps after starting, BTW)
5 hp air compressor
all lighting, inside and out, security system, etc.
HVAC with aux resistance heat
20 amps to feed some farm water heaters.

Even though it is usually just me, I do have occasional students and figured several 1 to 3 hp machines (lathes, bandsaw, drill press, grinders) could be used at once. When I'm using the big welders I'm not using the wood.

Even with a 25% overage allowance my worst case load was well under a maximum of 100 amps so I installed a 100 amp panel. One thing that is very important to me - voltage drop. There are recommended voltage drop allowances to avoid excessive light dimming and power glitches when pulling big loads. I wanted zero noticeable light dimming so I oversized the wiring to the shop. My case was complicated by putting the shop 250 ft from my transformer and meter. They laughed at me when I installed #1 copper for the power but hey, it is so much effort to dig the trench and lay conduit that even double the cost for the permissible or even the "normally acceptable" conductors was negligible compared to the total cost of the shop from dirt to roof. BTW, don't forget long internal runs too - my two 5hp motor loads were about 50' from the panel so I fed a sub panel there with oversized cable. I'd rather have too much capacity than too little. Materials are cheaper than the time.

Another thing I'm glad I added to the trench - I ran two extra underground conduits - one with two ethernet cables to feed the shop WiFi, personal cell tower, and security system (one cable is a backup), and one 2" conduit empty except for a rope - for some then un-imagined use.

Also, install a panel with more breaker slots than you can imagine you will ever need. I paneled with ply and screws instead of sheet rock so I can take things apart gracefully to modify things if ever needed. (I already removed one wall panel three times!)

JKJ

Jim Becker
03-25-2017, 5:17 PM
I was concerned with this when I built out my shop, too, Mark. I had 200 amp "service" put in to the shop at the same time we were upgrading the house panel considering "more capacity can be better"; both come from the same meter, but are essentially separate, otherwise, and the house side of the service is built and rated for 400 amps. However, the power company refused to upsize the actual service from the street (arial) so that's still a 200 amp supply. Fortunately, there's not been a problem and it's been that way since 2005. Both the licensed electrician and inspector were ok with it, too. Go figure... :)

mark mcfarlane
03-25-2017, 6:04 PM
Thanks everyone. The question wasn't about panels and wire sizes, but about max draw for the shop.

The current plan is to have a separate 200 AMP panel in the shop. The main feed gets splits to two cutoffs, then on to two 200 AMP panels.

Van Huskey
03-25-2017, 6:09 PM
The problem is nobody (even an electrician or EE) can even guess in significant part because there is little information about the house current draw. If for example the house is all electric and you have a house full of people and run the 4 top and oven while kids are taking hot showers and running the washer and dryer along with 8 tons of AC starting while you are running heavy cuts on the shaper with both your mini-splits starting you are definitely going to have a problem.

The reality is most all electric homes in hot climates have well over the potential draw to pop the main breaker if you fire up everything at once but it is a very rare occurrence with the current average 200 amp supply.

From a practical POV I have run shops with very similar and slightly higher max current demands on 100A sub panel and never had an issue. The key is machines rarely pull FLA and then usually only for short periods of time (not counting the uber-quick inrush).

The big problem is without enough supply to cover every electrical item you own running at the same time sizing a supply is a guessing game, balanced by experience on the electricians part.

Van Huskey
03-25-2017, 6:12 PM
The question wasn't about panels and wire sizes, but about max draw for the shop.


Que? I thought you were asking about how much total supply you need for the house and the shop. The shop based on your machines is more than fine with a 100 amp supply.

mark mcfarlane
03-25-2017, 6:17 PM
Thanks Van. Our AC is electric but heat and water are gas. The electrician told me the 'expected max load' (by some named authority, I assumed either power company or county, state,...) for houses in our area of our size was 100 AMPs, but he always put in 200 AMP services.

The current house is 2800 sq ft. The addition is 2000 sq ft.

.. but I fear I am helping the thread get off track.

John K Jordan
03-25-2017, 7:31 PM
I was concerned with this when I built out my shop, too, Mark. I had 200 amp "service" put in to the shop at the same time we were upgrading the house panel considering "more capacity can be better"; both come from the same meter, but are essentially separate, otherwise, and the house side of the service is built and rated for 400 amps. However, the power company refused to upsize the actual service from the street (arial) so that's still a 200 amp supply. Fortunately, there's not been a problem and it's been that way since 2005. Both the licensed electrician and inspector were ok with it, too. Go figure... :)

If the split is hard wired before either panel then the service from the pole/transformer will typically provide far more than you could ever use. A utility guy told me once what a typical aerial line on a pole could handle and I don't remember the numbers but it was surprising.

In my case we ran the feed a few feet from the transformer (on the ground on the property) to a meter mounted in an outside breaker box. In that box I put three breakers: a 220v breaker to feed the house panel, a 220v breaker to feed the shop, and a 110v breaker to feed an outside receptacle below the meter box. A friend from the utility company did the hookup so I assume they are happy with it.

JKJ

Rick Fisher
03-25-2017, 8:58 PM
I would consider the compressor as well but you will be fine .

I ran 400 amps to the shop and split the shop and house .. each is only 200 amps. We have an empty conduit 2" from the house to shop which would allow me to poach more power than I have from the house but its not needed.. I have some bigger stuff running, still no issue at all. 200 amps is a lot of power in a one man shop.

mark mcfarlane
03-26-2017, 1:29 AM
Here's an update with a compressor added:



Shop - Max simultaneous power usage
Qty
HP
Note


Amps (running)




Circuit






CU300


1


4.8 HP (230V)
30 amp curcuit, probably only uses 20 amps


30




230V


http://www.scmgroupna.com/en/products/classical-machines.c884/universal-combined-machines.887/cu-300-classic.721


DC40 Stock Feeder


1


0.5 HP




3




230V


http://www.cantekamerica.com/machinery/feeders/dc30-3-roll-variable-speed-power-feeder-2883.html


Dust Gorila Pro


1


5.0 HP (maybe 3HP)
30 amo curcuit, probably only uses 20 amps


20




230V


https://www.oneida-air.com/inventoryD.asp?item_no=XGK050105H&CatId={7F6C8978-92E8-4902-9A37-D8A254EDF4FC}


Shop Lights


30


32 watts
960 watts


8








Radio, mini-fridge








3








AC (mini-split) Shop


1


9000 BTU / 30.5 SEER




12




230V


http://www.mitsubishielectric.ca/en/hvac/PDF/m-series/Cooling-Heating_SingleIndoorUnit_Spec05.pdf


Compressor


1




1HP


4








Studio Lights








3








AC (mini-split Studio)


1








12




230V






Total Amps








95

Ole Anderson
03-26-2017, 8:39 PM
Minor, but 4 amps on a 1 hp compressor can't be correct.

Roger Feeley
03-27-2017, 4:28 PM
I ran my shop on 50A for 20 years. I never measured the draw but I only ran one machine at a time.
20 2-tube T12s at 80watts = 1600w. Be generous at 15A
3hp Table saw was the big suck call it 20A cause that was how big the breaker was
1.5hp dust collector. Another 12A

That would be 47A which is kind of close.
In my new shop, I replaced all lights with LED so I cut those amps down to 6.
That brings me to 41A and I put in a 100A sub-panel on a 70A breaker.

I figure I can run those lights and a small TIG welder and be fine.

Studio Lights?

mark mcfarlane
03-27-2017, 7:31 PM
Studio Lights?

The build includes a recording studio. I could forget and leave the lights on in there....

Phillip Gregory
04-02-2017, 10:25 PM
I was concerned with this when I built out my shop, too, Mark. I had 200 amp "service" put in to the shop at the same time we were upgrading the house panel considering "more capacity can be better"; both come from the same meter, but are essentially separate, otherwise, and the house side of the service is built and rated for 400 amps. However, the power company refused to upsize the actual service from the street (arial) so that's still a 200 amp supply. Fortunately, there's not been a problem and it's been that way since 2005. Both the licensed electrician and inspector were ok with it, too. Go figure... :)

Utilities are very loath to provide anything more than a 25 KVa (108 amps at 240 volts) transformer for single phase residential service. I have lived in three houses with at least 400 amps of nominal panel capacity running from the meter and all of them had a standard 25 KVa pad transformer. They do that even if you heat with a heat pump with resistive secondaries (and the entire rest of the house is electric as well), and can draw 40+ KW once the temp drops below freezing, or are running 8-10 tons of air conditioners off of that one 25 KVa transformer. The last one is the worst, because the biggest air conditioner is about a 5-6 ton unit that draws about twice the start current as the transformer is rated for and often causes appliances and computers to shut off due to voltage drop when it fires up.

lee cox
04-02-2017, 11:11 PM
I have gas in my house. You did not say whether you are all electric or not. I converted my dryer and water heater to gas which reduced my electric load and bills. My only house load now is my refrig, freezer and 5 ton AC as I live in Texas. I run a small detached shop off the same main breaker panel as the house. It seems to work fine. It is just me in the shop so I am not running a lot of tools simultaneously.

John K Jordan
04-02-2017, 11:15 PM
Utilities are very loath to provide anything more than a 25 KVa (108 amps at 240 volts) transformer for single phase residential service.

How could I find out what my transformer capacity is? All I know is it has 7200 volts on a single underground cable about 600 ft from the pole, sits on a concrete pad about 50 ft from the house.

Twice in 20 years the end of the cable exploded right at the transformer when some termites crawled in there to keep warm in the winter.

JKJ

mark mcfarlane
04-03-2017, 12:47 AM
I have gas in my house. You did not say whether you are all electric or not....

We have gas heat and gas water heater. Clothes dryer is plumbed/wired for both, and we are currently running an electric dryer since it was <1 year old when we moved into the house.

Phillip Gregory
04-03-2017, 6:04 AM
How could I find out what my transformer capacity is? All I know is it has 7200 volts on a single underground cable about 600 ft from the pole, sits on a concrete pad about 50 ft from the house.

Twice in 20 years the end of the cable exploded right at the transformer when some termites crawled in there to keep warm in the winter.

JKJ

Pretty well all of the residential transformers in my area have the kVA rating painted on them or on a large sticker that is clearly visible. Mine have all had a "25" on them. I looked at the specification label on the last few to see the model number, then looked that up online on the manufacturer's website to confirm the rating.

Squirrels and delivery trucks are the biggest reasons that transformers in my area bite the dust. A 25 kVA pad transformer is no match for a speeding FedEx truck that fails to negotiate a curve, and squirrels have a big predilection to mess with electrical equipment. I saw one get roasted a few years ago. It ran up the pylon for a line junction, and then there was a huge bang and an orange-green flash.

John K Jordan
04-03-2017, 10:17 AM
Pretty well all of the residential transformers in my area have the kVA rating painted on them or on a large sticker that is clearly visible. Mine have all had a "25" on them. I looked at the specification label on the last few to see the model number, then looked that up online on the manufacturer's website to confirm the rating.

Squirrels and delivery trucks are the biggest reasons that transformers in my area bite the dust. A 25 kVA pad transformer is no match for a speeding FedEx truck that fails to negotiate a curve, and squirrels have a big predilection to mess with electrical equipment. I saw one get roasted a few years ago. It ran up the pylon for a line junction, and then there was a huge bang and an orange-green flash.

Ah, I went out with a flashlight last night and did find a 25 kva stencil near the bottom.

Fortunately my transformer is between my dog lot and a holly tree in the middle of my 27 acres. Three times in 14 years I've had squirrels disrupt my power when I am negligent in keeping the vines cut back around the pole a 1/4 mile down the hill. I'll hear an explosion loud enough to wake the dead when the fuse blows and always find a nicely roasted squirrel on the ground. Fortunately the neighbors work for the utility company and have always had a pole and spare fuses on hand.

JKJ

mark mcfarlane
04-03-2017, 10:59 AM
357535

The transformer feeding my house is appears to be shared by 5-6 homes. The 'sticker' that probably had some specs on it on it is bleached white by the sun.

Phillip Gregory
04-03-2017, 11:38 AM
Looks like probably 75 kVA- look at the bottom near the grass. That would fit with it being used to supply several houses.

Kelly Craig
04-07-2017, 10:37 PM
I can see asking a woodworkers forum for input. Over on another site, a fellow hired and electrician, to make sure it was all done right. The electrician installed fourteen gauge lines and outlets.

As to a hundred amp panel working for a one man shop, maybe. I'm upgrading mine from a hundred to a two hundred. The reason is simple:

1) twenty four foot LED'S @ 40 watts each, for a total of 1000 watts, or 9 amps
2) a Unisaw with a run amperage of 7 amps
3) a three horse collector with a run amperage of 15 amps
4) an HVAC system that demands a 40 and a 60 amp breaker
5) a 5 amp radio system
6) computer @ about 5 amps

At this point, that pushes too near the hundred amp limit, since it comes to about 101 amps and we never want to push the capacity to near max.

Now come my friends who:

6) fire up the band saw, jointer, edge sander or ..... at about 7 amps.
7) fire up the other collector at about 7 amps.

Now I am, definitely pushing the limit.

Many of us do have friends who like to drop by and fire up the pin router, or whatever.

Better safe than sorry. Having too much capacity only hurts once, when you pay for it.