PDA

View Full Version : Wrong plug end on this TS cord?



Alex Gauthier
08-22-2016, 11:52 AM
With the new Griz 1023 in my garage, it's time to plug it in and tune it up however I've run into a little bit of a conundrum.

Not being super savvy on electrical stuff but having googled it a bit, I've managed to make myself more confused while trying to figure this out.

My saw came with the plug in the photo below. This appears to be an under spec plug for the amperage of the saw (5HP model, 30amp). Am I correct in this statement?

Also, it doesn't match the 240 receptacle in my space which looks more like the dryer plug style receptacle. I'm planning on installing a new receptacle in the wall beside my saw (because it's directly adjacent the fuse box, I'm assuming this will be superior in all ways to running cord from the other corner of the garage (20 ft) to my saw.

The question is: what plug end should I be using? Also, the breaker is 30amps which might be a touch on the low side for when the saw first fires up. Should I beef that breaker up as well?

342776

Malcolm McLeod
08-22-2016, 12:12 PM
I believe the pic is a 20A. plug, but 5Hp should draw ~23-24A.(max). Griz recommends L6-30 for plug - - so I'd replace it.
Also recommend 30A for breaker, so what you have should work on start up (all breakers will ride through the brief start-up, inrush current 'overload').

Patrick McCarthy
08-22-2016, 12:54 PM
I think Malcolm is correct; it looks like a 20amp plug for a 110 (?) circuit. But I am not an electrician.

I would suggest you look at the motor plate to make sure you have a 5hp motor . . . . .

Google photos shows it as a 6-15 plug, which is not the one spec'd for your saw IF you got the right saw and motor combo. Grizzly does spec a 6-15 on one of their other cabinet saws, but I think it is a 3hp, 13 amp.


IF it is the right saw/motor combo, switching the plug is easy enough but make sure the wire gauge is heavy enough for a 30amp circuit.

lee cox
08-22-2016, 1:04 PM
I am no expert but it looks like a 20amp 110 volt plug. I don't think you can run a 5hp motor off of 110 volt. You need to check the motor plate and the way it is wired inside. Don't just change the plug and hope.

Ryan Mooney
08-22-2016, 1:06 PM
I am no expert but it looks like a 20amp 110 volt plug. I don't think you can run a 5hp motor off of 110 volt. You need to check the motor plate and the way it is wired inside. Don't just change the plug and hope.

Its 20a 240v, the one prong being crosswise is the difference..

Malcom has it right.

John Aperahama
08-22-2016, 1:09 PM
I am guessing you did not buy from grizzly they do not supply machines with plugs.
For what it is worth all of my machines use 220v plugs as shown some are 5hp no problems.
If you are concerned just change it.

lee cox
08-22-2016, 1:10 PM
My 220 volt 20amp has 2 prongs crosswise. I don't use much 20amp 220 volt as I standardized on 30amp twist lock plug.

lee cox
08-22-2016, 1:22 PM
You might want to standardize on your 220 volt plugs so if you mover things around it all still will work.

Alex Gauthier
08-22-2016, 1:33 PM
It's definitely a 5HP saw. The motor plate states 5HP and 30amps. It's an older saw that I recently purchased. I suspect the previous owner didn't really pay much mind to the plug amperage rating and just wired it with what he had on hand. Since I have to make changes either way, I'm thinking I'll follow the advise stated and standardized on the locking type.

Thanks!


I think Malcolm is correct; it looks like a 20amp plug for a 110 (?) circuit. But I am not an electrician.

I would suggest you look at the motor plate to make sure you have a 5hp motor . . . . .

Google photos shows it as a 6-15 plug, which is not the one spec'd for your saw IF you got the right saw and motor combo. Grizzly does spec a 6-15 on one of their other cabinet saws, but I think it is a 3hp, 13 amp.


IF it is the right saw/motor combo, switching the plug is easy enough but make sure the wire gauge is heavy enough for a 30amp circuit.

lee cox
08-22-2016, 1:38 PM
I guess you know if you extend your 220v 30amp plug you will give up your current plug. You need 1 breaker per plug. You can't string a bunch of 220v 30amp plugs together like stringing lights on one 110v 20amp breaker.

David Boardman
08-22-2016, 2:05 PM
I guess you know if you extend your 220v 30amp plug you will give up your current plug. You need 1 breaker per plug. You can't string a bunch of 220v 30amp plugs together like stringing lights on one 110v 20amp breaker.

Well, you can daisy chain 220 but it's not to code from my understanding and you can't run the machines at the same time.

I suggest standardizing all your plugs. I went with the twist lock plugs. The are expensive but nice and beefy. I hate that grizzly sends out their machines with crappy plugs on them. It really irks me to get a brand new tool and even before I turn it on I have to cut it up.

Malcolm McLeod
08-22-2016, 2:06 PM
I guess you know if you extend your 220v 30amp plug you will give up your current plug. You need 1 breaker per plug. You can't string a bunch of 220v 30amp plugs together like stringing lights on one 110v 20amp breaker.

Apparently you can - at least in my neck of the world. I had licensed electrician wire my shop with a single 50A circuit with 3 receptacles (2 ea. L6-30R, 1 ea. 6-20R). It was inspected by municipality while I explained what it was for - single tool use. It passed with no issues or raised eyebrows.

Edit: L6-30 are for 5Hp/240v, 6-20 is for 3Hp/240V (and wish I'd used the L6-20). Everything else is 110V/20A.

And FYI for those interested -
http://webstorehouse.com/happywoodworking/images/NEMAplugs.gif

John Lankers
08-22-2016, 2:25 PM
Apparently you can - at least in my neck of the world. I had licensed electrician wire my shop with a single 50A circuit with 3 receptacles (2 ea. L6-30R, 1 ea. 6-20R). It was inspected by municipality while I explained what it was for - single tool use. It passed with no issues or raised eyebrows.

Edit: L6-30 are for 5Hp/240v, 6-20 is for 3Hp/240V (and wish I'd used the L6-20). Everything else is 110V/20A.

And FYI for those interested -
http://webstorehouse.com/happywoodworking/images/NEMAplugs.gif

Correct.
He needs a plug and receptacle rated for 30 Amp 250 Volt and needs to make sure the panel, breaker and wiring is sized to match.

lee cox
08-22-2016, 2:41 PM
Apparently you can - at least in my neck of the world. I had licensed electrician wire my shop with a single 50A circuit with 3 receptacles (2 ea. L6-30R, 1 ea. 6-20R). It was inspected by municipality while I explained what it was for - single tool use. It passed with no issues or raised eyebrows.

Edit: L6-30 are for 5Hp/240v, 6-20 is for 3Hp/240V (and wish I'd used the L6-20). Everything else is 110V/20A.

And FYI for those interested -
http://webstorehouse.com/happywoodworking/images/NEMAplugs.gif

I would like to string plugs together because I am out of breaker space. What size wire did you use? Was the wire sized to the tool or the circuit?

Malcolm McLeod
08-22-2016, 3:53 PM
It was several years ago and done by someone else, but #6 copper (Romex) is rattling around in my head...???

There may be provision to use #8 THHN copper? But now you need conduit (if not in code, I'd certainly encourage it). I also recall something about wire smaller than #6 copper if it is for a motor AND it has overload protection AT the motor...?

Caveat: I'm not an electrician! Nor do I have NEC rules as a tattoo. Please consult an expert. And legal in one jurisdiction, is not always legal in next.

lee cox
08-22-2016, 4:10 PM
6 ga wire is pretty big and expensive. It would probably be cheaper for me to replace my breaker box and use smaller wire.

I do have a 50 amp welding circuit which I could use.

Art Mann
08-22-2016, 5:24 PM
I no longer offer information on house/shop wiring because it is difficult for people to tell who knows what they are talking about and who doesn't. All I will say is that you need to seek out an authoritative local source for advice because much of what has already been offered is just plain wrong.

David L Morse
08-22-2016, 5:39 PM
I had licensed electrician wire my shop with a single 50A circuit with 3 receptacles (2 ea. L6-30R, 1 ea. 6-20R). It was inspected by municipality while I explained what it was for - single tool use. It passed with no issues or raised eyebrows.


I would like to string plugs together because I am out of breaker space. What size wire did you use? Was the wire sized to the tool or the circuit?

The applicable NEC section is 210.21(B)(3):
342790
You can attach multiple receptacles to one branch circuit. They must all have the same current rating as the branch circuit except as shown in the table for 20A and 40A circuits.

Randy Viellenave
08-22-2016, 7:18 PM
The 5HP motor requires 3.73KW, or 15.54A at 240VAC, so the plug is correct. The circuit should be just like most water heaters, AWG12 wire on a 2P 20A breaker. a 5HP 120V motor would be a rare thing, but I would check anyway and make sure you are wired for 240V 1P (single phase).

lee cox
08-22-2016, 7:46 PM
The 5HP motor requires 3.73KW, or 15.54A at 240VAC, so the plug is correct. The circuit should be just like most water heaters, AWG12 wire on a 2P 20A breaker. a 5HP 120V motor would be a rare thing, but I would check anyway and make sure you are wired for 240V 1P (single phase).

I have a 3 HP Rockwell motor on my Unisaw and it draws 22 amps as stated on the metal plate on the motor for 220 volts.

I am wrong. I went out and looked at the motor plate. I tried to post the plate but I cannot insert an image. It is 16 amps for 220v and 32 amps for 110v.

Randy Viellenave
08-22-2016, 7:56 PM
If that plate were correct, it would be about 6.5HP, so it is not correct. Each HP is equal to 746W (0.746KW) @100% efficiency. If you have 3HP, regardless of the voltage, you have 0.746KW X 3 = 2.238KW. If you are running at 240VAC, you would pull 9.325A, or double that to 18.65 @ 120VAC. You can draw a bit more due to an old motor or simply out of spec, but not that much more. I can see getting a 22A draw on startup, but that should be there and gone very fast.

Wade Lippman
08-22-2016, 8:40 PM
If that plate were correct, it would be about 6.5HP, so it is not correct. Each HP is equal to 746W (0.746KW) @100% efficiency. If you have 3HP, regardless of the voltage, you have 0.746KW X 3 = 2.238KW. If you are running at 240VAC, you would pull 9.325A, or double that to 18.65 @ 120VAC. You can draw a bit more due to an old motor or simply out of spec, but not that much more. I can see getting a 22A draw on startup, but that should be there and gone very fast.

Total nonsense. Ignore the HP claim and wire to either the manufacture's recommendation or the amperage on the plate.

My 3hp Grizzly cyclone is 22a and my 3hp Sawstop is 13a; but I don't think any manufacturer is whimsical enough to claim their 9a motor is 3hp.

But in the end, I have to agree with Art; if you are asking questions like these, you shouldn't be doing wiring.

Brice Rogers
08-22-2016, 10:33 PM
For the Grizzly 1023 with the 5 HP motor, Griz recommends using a 30 amp power source, a Nema L6-30 plug and says that the full load current rating is 22 A. You can look this up easy enough. Here's a link: http://cdn1.grizzly.com/manuals/g1023rl_m.pdf

There are lots of charts on the internet addressing "ampacity" and wire size. One from Cerrowire suggests using 10 gauge (solid) wire. http://www.cerrowire.com/ampacity-charts

So this is what you should use for wire from the breaker box to saw receptacle.

Ole Anderson
08-23-2016, 10:01 AM
It was several years ago and done by someone else, but #6 copper (Romex) is rattling around in my head...???

There may be provision to use #8 THHN copper? But now you need conduit (if not in code, I'd certainly encourage it). I also recall something about wire smaller than #6 copper if it is for a motor AND it has overload protection AT the motor...?

Caveat: I'm not an electrician! Nor do I have NEC rules as a tattoo. Please consult an expert. And legal in one jurisdiction, is not always legal in next.

10 gauge copper is good for 30 amps unless you have a very long run. 10-2 wg NM cable (romex) is generally jacketed in orange.

Ken Combs
08-23-2016, 12:00 PM
If you really want to get confused, Google L6-30 Horsepower (or HP) rating. According the NEC ratings, none of my plug in stuff above 2HP is legal.

amperage rating and HP ratings are not what most of us think. At least in the legal NEC world.

Wade Lippman
08-23-2016, 12:15 PM
If you really want to get confused, Google L6-30 Horsepower (or HP) rating. According the NEC ratings, none of my plug in stuff above 2HP is legal.

amperage rating and HP ratings are not what most of us think. At least in the legal NEC world.

I noticed that a few years ago and asked Grizzly about it; their recommended plugs were inadequate to the HP ratings. They told me to ignore the HP rating and go by amperage. I guess that ties into the capricious nature of claimed HP ratings.

Ken Combs
08-23-2016, 10:01 PM
I noticed that a few years ago and asked Grizzly about it; their recommended plugs were inadequate to the HP ratings. They told me to ignore the HP rating and go by amperage. I guess that ties into the capricious nature of claimed HP ratings.

I don't think it's the hp rating, as the 'phantom ratings' are limited to brush type motors and air compressors. Even in those, the motor makers don't do the lying, it's the air compressors makers that attach the fake numbers...Most, if not all the mis=rated units say one thing on the tank, but the motor will say 'spl' (for special) or some other non-numerical phrase.

It's my guess that the NEC rule makers considered the possibility of a plug being removed while a motor was starting under load. the resultant arc flash of say a 5hp would be really hot!

High HP sockets and plugs are available as are 3ph plugs/sockets but are really expensive.

i think any equipment maker that encourages users to ignore the NEC is technically right when the usage is considered, but there is a liability risk if something should go wrong.

Robby Tacheny
08-25-2016, 8:20 AM
Lower amps = smaller wire (when wired correctly)
Higher amps = bigger wire (when wired correctly)
20amps at 110v = 10amps @ 220V (when wired correctly)
110v = One "hot" leg from breaker box (when wired correctly)
220 = Two "hot" legs from breaker box (when wired correctly)
3 Phase = I get confused :)

These are the ultra basics. Get some testing tools (probes that tell you if a circuit is hot and tell you voltage; maybe an clip on amp meter if want to check a running tool in that outlet) if you are going to do work your self. Check outlet before working on it with testing tool and check again even after flipping breaker before you work on it.

Check your local laws and building codes and follow them. Get help if you don't feel comfortable with all of this.

-Robby

lowell holmes
08-25-2016, 9:09 AM
I'm not an electrician, but if I remember correctly from my house building days, #12 romex is rated for 20 amps, 30 amps would require #10 conductors.

An electrician needs to confirm this.

John Lankers
08-25-2016, 10:21 AM
With the new Griz 1023 in my garage, it's time to plug it in and tune it up however I've run into a little bit of a conundrum.

Not being super savvy on electrical stuff but having googled it a bit, I've managed to make myself more confused while trying to figure this out.

My saw came with the plug in the photo below. This appears to be an under spec plug for the amperage of the saw (5HP model, 30amp). Am I correct in this statement?

Also, it doesn't match the 240 receptacle in my space which looks more like the dryer plug style receptacle. I'm planning on installing a new receptacle in the wall beside my saw (because it's directly adjacent the fuse box, I'm assuming this will be superior in all ways to running cord from the other corner of the garage (20 ft) to my saw.

The question is: what plug end should I be using? Also, the breaker is 30amps which might be a touch on the low side for when the saw first fires up. Should I beef that breaker up as well?

342776



To get back to the original question, this plug is a fire waiting to happen.
The ratings are engraved on the plug (usually on the face), what you want is a 30 Amp, 250 Volt rated plug, there are choices like a 30 Amp welder plug or a 30 Amp twist lock plug.
Next point, your 30 Amp breaker was installed to protect the wiring leading to the receptacle NOT the tool you plug into it that is your responsibility. If the breaker trips when you turn the saw on or work it hard talk to a qualified electrician.

Alex Gauthier
08-25-2016, 4:53 PM
Wow... didn't expect so much input on this but I guess it makes sense considering the nature of the question.

An Update: I've already stripped the inadequate plug from the saw and replaced it with an L6-30 locking plug. This new plug and the matching receptacle are both marked 30Amp/250v capacity. My plan is to use the existing 30A circuit in the breaker box. Because it so happens I want the outlet to be on the same wall as the breaker box, I plan to simply sever the run that leads from that 30A circuit to the far side of the shop where the previous owner plugged in who knows what. I'll use the now shortened run to install the receptacle 24" below the breaker in the adjacent stud chamber. The wall is OSB so I don't even need to worry about drywall. Also, I won't need to touch the breaker box itself at all (other than to kill the power). While I'm at it, I'll make sure the wire is 10g or better.

Based on research elsewhere and this thread, that seems like the safest way to go. I think I'll also pay an electrician to just give it a glance for me. I'd rather do the work myself as a learning experience and then pay them to bless it.




To get back to the original question, this plug is a fire waiting to happen.
The ratings are engraved on the plug (usually on the face), what you want is a 30 Amp, 250 Volt rated plug, there are choices like a 30 Amp welder plug or a 30 Amp twist lock plug.
Next point, your 30 Amp breaker was installed to protect the wiring leading to the receptacle NOT the tool you plug into it that is your responsibility. If the breaker trips when you turn the saw on or work it hard talk to a qualified electrician.