06-09-2013, 12:06 PM
I know that the electrical code for sub panels calls for 4 wires to be run from the main panel to the 220 volt sub panel (2 hots, neutral & ground), isolating the neutrals & grounds in the sub panel and no ground rod at the sub panel.

What is the reason for using the ground at the main panel & no ground rod at the sub panel?

Art Mann
06-09-2013, 1:17 PM
I do not believe it is a violation of the NEC to use a local ground rod at the sub panel. I certainly did because it is safer than counting on a ground reference that is 150 feet away (in my case). The important thing is to keep this ground separate from the neutral, because it is current carrying and the ground is not.

Richard Shaefer
06-10-2013, 6:44 AM
Agreed.
no restriction against using a local ground rod. Depedning on the mood of your local inspector, he may either demand that you install a local ground rod or remove one that you already have installed. Only reliable adviec that I can offer you is that however you ground it, the inspector will likely want it the other way. ;)

Thomas Bank
06-10-2013, 9:39 AM
You don't state it, but my experience is for a local ground rod if the sub-panel is in a separate structure and using the existing grounding if it is in the same structure as the main panel.

Julie Moriarty
06-10-2013, 4:05 PM
From 2011 NEC:

250.24 Grounding Service-Supplied Alternating-Current Systems.
(A) System Grounding Connections. A premises wiring system supplied by a grounded ac service shall have a grounding electrode conductor connected to the grounded service conductor, at each service, in accordance with 250.24(A)(1) through (A)(5).

(1) General. The grounding electrode conductor connection shall be made at any accessible point from the load end of the service drop or service lateral to and including the terminal or bus to which the grounded service conductor is connected at the service disconnecting means.

Informational Note: See definitions of Service Drop and Service Lateral in Article 100.

(2) Outdoor Transformer. Where the transformer supplying the service is located outside the building, at least one additional grounding connection shall be made from the grounded service conductor to a grounding electrode, either at the transformer or elsewhere outside the building.

Exception: The additional grounding electrode conductor connection shall not be made on high-impedance grounded neutral systems. The system shall meet the requirements of 250.36.

(3) Dual-Fed Services. For services that are dual fed (double ended) in a common enclosure or grouped together in separate enclosures and employing a secondary tie, a single grounding electrode conductor connection to the tie point of the grounded conductor(s) from each power source shall be permitted.

(4) Main Bonding Jumper as Wire or Busbar. Where the main bonding jumper specified in 250.28 is a wire or busbar and is installed from the grounded conductor terminal bar or bus to the equipment grounding terminal bar or bus in the service equipment, the grounding electrode conductor shall be permitted to be connected to the equipment grounding terminal, bar, or bus to which the main bonding jumper is connected.

(5) Load-Side Grounding Connections. A grounded conductor shall not be connected to normally non–current carrying metal parts of equipment, to equipment grounding conductor(s), or be reconnected to ground on the load side of the service disconnecting means except as otherwise permitted in this article.

Take from that what you want, but every sub-panel I have ever installed (and I've installed a lot) is grounded back to the main panel. That may be through metallic conduit or through a grounding conductor. Some inspectors have required a grounding rod in addition to the grounding conductor. There's some controversy regarding potential differences created by two separate grounding systems on the same feeder but I've never seen that issue resolved. Grounding is the grey area of electrical systems.

The easiest way to know what you need to do in your area is to call the inspector.

Michael Dunn
06-10-2013, 7:05 PM
This most certainly will not apply to your situation, but multiple paths to ground is an absolute nuisance when dealing with professional audio. The potential difference between the paths to ground creates a ground loop and shows itself as a terrible 60Hz hum with a buzz several harmonics above the fundamental.

For that, I would personally prefer to have one path to ground. But I'm also an audio engineer in addition to being a woodworker.

David L Morse
06-10-2013, 10:25 PM
What is the reason for using the ground at the main panel & no ground rod at the sub panel?

Short answer: It makes it less likely that lightning ground currents will take a shortcut through your house and fry all of your line powered electronics.

Google "lightning ground potential rise" for some really scary numbers.

Chris Rosenberger
06-11-2013, 10:06 PM
Thank you for the replies. I will check with the inspector.

Rollie Meyers
06-14-2013, 8:23 AM
The ground rods are not needed for clearing faults, as electricity is not "trying to get to the ground" as as most folks think, it is trying to return to it's source & will take all avail. paths including the earth. If a panel is in a separate structure then a rod or other allowed grounding electrode is required, & if a rod is used if the installer cannot prove 25 Ohms of resistance or less a 2nd one has to be driven at least 6 feet from the other per NEC art. 250.56 & it's cheaper to just drive another rod because the testing equipment is expensive & the user needs to be qualified to use it. There is no need to use a rod for a subpanel in the same structure it is fed from & it will not be any safer if one is used, if done improperly it can less safe.

David C. Roseman
06-17-2013, 9:56 AM
The ground rods are not needed for clearing faults, as electricity is not "trying to get to the ground" as as most folks think, it is trying to return to it's source & will take all avail. paths including the earth. If a panel is in a separate structure then a rod or other allowed grounding electrode is required, & if a rod is used if the installer cannot prove 25 Ohms of resistance or less a 2nd one has to be driven at least 6 feet from the other per NEC art. 250.56 & it's cheaper to just drive another rod because the testing equipment is expensive & the user needs to be qualified to use it. There is no need to use a rod for a subpanel in the same structure it is fed from & it will not be any safer if one is used, if done improperly it can less safe.

Chris, I think Rollie has stated this correctly. Would be interested to hear what you learn from talking to the inspector.

David

Jim Neeley
06-17-2013, 1:57 PM
The ground rods are not needed for clearing faults, as electricity is not "trying to get to the ground" as as most folks think, it is trying to return to it's source & will take all avail. paths including the earth. If a panel is in a separate structure then a rod or other allowed grounding electrode is required, & if a rod is used if the installer cannot prove 25 Ohms of resistance or less a 2nd one has to be driven at least 6 feet from the other per NEC art. 250.56 & it's cheaper to just drive another rod because the testing equipment is expensive & the user needs to be qualified to use it. There is no need to use a rod for a subpanel in the same structure it is fed from & it will not be any safer if one is used, if done improperly it can less safe.

Rollie,


Your answer is correct however I want to expound slightly less someone miss-read and thereby misunderstand the full intent. Please understand that this is intended in no way to reflect in any way negatively on you; I have no doubt that you fully understand the intent of the code. This is from the 2011 code, where 250.56 is deleted, being covered by 250.53 (3)B:

(B) Electrode Spacing. Where more than one of the electrodes
of the type specified in 250.52(A)(5) or (A)(7) are
used, each electrode of one grounding system (including
that used for air terminals) shall not be less than 1.83 m
(6 ft) from any other electrode of another grounding system.
Two or more grounding electrodes that are bonded
together shall be considered a single grounding electrode
system.

Section 250.58 goes on to say:

250.58 Common Grounding Electrode. Where an ac system
is connected to a grounding electrode in or at a building
or structure, the same electrode shall be used to ground
conductor enclosures and equipment in or on that building
or structure. Where separate services, feeders, or branch
circuits supply a building and are required to be connected
to a grounding electrode(s), the same grounding electrode(
s) shall be used.
Two or more grounding electrodes that are bonded together
shall be considered as a single grounding electrode
system in this sense.

Just my $0.02… YMMV.

Jim in Alaska

Julie Moriarty
06-18-2013, 1:03 PM
When the cell phone carriers were first coming into Chicago to set up their systems I was involved in the electrical end of the installations. We had to install a ground grid around both the equipment cabinets and the tower. We'd drive 10' x 5/8" copper ground rods spaced 6' apart. They would all be bonded by cad-welding a #2 tinned bare copper wire from one ground rod to the next so as to create a loop around the equipment and the tower. We'd then run tails off the ground loop to various points on the equipment, platform and tower. If there was a fence around it, we'd bond the fence too. It was the most extensive grounding I have seen in my 34 years as an electrician.

So you can certainly have two or more ground rods in the same system but if they are connected electrically through panels or bus bars, there might be an issue. Grounding-wise, you can't isolate the ground in the main panel from the ground in the sub panel unless you isolate the neutral bus from ground. I've never seen that done in a residential application. So if the main panel and sub panel are not bonded either through the case or through a grounding conductor, the neutral will act as a ground path between the two panels. And that's not good.

Chris Hachet
06-24-2013, 8:31 PM
Bingo...I am a state listened master electrician and this is indeed the correct answer.

Joseph Tarantino
06-24-2013, 9:14 PM
in which state?

Art Mann
06-25-2013, 11:04 AM
The information that has been offered in the most recent posts, which Chris Hachet endorsed, is based on the National Electrical Code. State codes are additions to the NEC.

John Coloccia
06-25-2013, 11:37 AM
FWIW, imagine what would happen if you ever lost the neutral in the sub-panel and it happened to be bonded to ground in the sub-panel. Your ground wire would suddenly become a current carrying conductor with a subsequent voltage drop all the way back to the service panel, and you would have stray currents energizing every ground connection on that panel, and you would never know it until it caused problems.

Even worse, if that cable were ever damaged, say by accidentally drilling through it...or a fire....or an earthquake....or anything like that, and you happened to loose the neutral AND the ground, you would then have a situation where the return path because the metal chassis of equipment. Every piece of metal in the shop suddenly becomes deadly, including the sub-panel itself. Keeping the ground and neutral separate insures this can never happen.

David C. Roseman
06-26-2013, 11:45 AM
Some of the discussion in this thread does not reference a distinction between a sub-panel in the same structure as the service panel, and one in a separate outbuilding, such as a detached garage, shop or barn. Just want to be sure my understanding is correct: That is, in both cases, the sub-panel should be bonded back to ground at the service panel through the ground conductor in the feeder cable, and, if in a separate structure, it must also be bonded to its own ground rod (or other approved electrode) at that structure. Also, at least if residential, in both cases the neutral should be bonded to ground at both the sub-panel and service panel (through bonding of the neutral and ground busses).

Is that right? Not an electrician, but I take this stuff very seriously. :eek:

David

Matt Marsh
06-26-2013, 12:16 PM
Some of the discussion in this thread does not reference a distinction between a sub-panel in the same structure as the service panel, and one in a separate outbuilding, such as a detached garage, shop or barn. Just want to be sure my understanding is correct: That is, in both cases, the sub-panel should be bonded back to ground at the service panel through the ground conductor in the feeder cable, and, if in a separate structure, it must also be bonded to its own ground rod (or other approved electrode) at that structure. Also, at least if residential, in both cases the neutral should be bonded to ground at both the sub-panel and service panel (through bonding of the neutral and ground busses).

Is that right? Not an electrician, but I take this stuff very seriously. :eek:David


David,


The only time you bond the neutrals and grounds together is where the panel in question is fed with a 3-wire feeder. The neutral bus in a sub-panel fed with a 4-wire feeder must be isolated from the grounding system, whether it is in the same structure, or a seperate structure. A panel in a seperate structure, whether it is fed with a 3-wire or 4-wire feeder, must have it's own seperate grounding electrode system. The only exeption to this rule, is when the seperate structure is fed by a single branch circuit. A multi-wire branch circuit is still considered a single branch circuit.

David C. Roseman
06-28-2013, 11:13 PM
David,


The only time you bond the neutrals and grounds together is where the panel in question is fed with a 3-wire feeder. The neutral bus in a sub-panel fed with a 4-wire feeder must be isolated from the grounding system, whether it is in the same structure, or a seperate structure. A panel in a seperate structure, whether it is fed with a 3-wire or 4-wire feeder, must have it's own seperate grounding electrode system. The only exeption to this rule, is when the seperate structure is fed by a single branch circuit. A multi-wire branch circuit is still considered a single branch circuit.

Thanks, Matt! That explanation is very clear, and makes complete sense.

David

Scott T Smith
06-30-2013, 8:55 PM
When the cell phone carriers were first coming into Chicago to set up their systems I was involved in the electrical end of the installations. We had to install a ground grid around both the equipment cabinets and the tower. We'd drive 10' x 5/8" copper ground rods spaced 6' apart. They would all be bonded by cad-welding a #2 tinned bare copper wire from one ground rod to the next so as to create a loop around the equipment and the tower. We'd then run tails off the ground loop to various points on the equipment, platform and tower. If there was a fence around it, we'd bond the fence too. It was the most extensive grounding I have seen in my 34 years as an electrician.

So you can certainly have two or more ground rods in the same system but if they are connected electrically through panels or bus bars, there might be an issue. Grounding-wise, you can't isolate the ground in the main panel from the ground in the sub panel unless you isolate the neutral bus from ground. I've never seen that done in a residential application. So if the main panel and sub panel are not bonded either through the case or through a grounding conductor, the neutral will act as a ground path between the two panels. And that's not good.

Julie, you brought back some memories! I spent several years with Nextel in Chicago, the first year and a half was on the site development side. I'll be you know what "Motorla R56" is....