I've had it with this house. We live in a two story house with walkout basement. This is the second summer in the house and I'm tired of getting a $400 electric bill. It wouldn't be so bad if the upstairs was cooler than 80 degrees when I go to bed at night. There's only one forced air system for the whole house and I've got all the registers in the basement closed and still can't get decent cooling upstairs. There's plenty of blown in insulation in the attic so I'm looking for what else I can do. Below are a couple of my thoughts. Let me know what would be the most effective at reducing our energy consumption and improving the comfort on the second floor.


Reflective rolls against the underside of the roof.
Powered attic ventilation fan.


Input is much appreciated.

Thanks,
Wes

Jay Runde
07-28-2012, 5:12 PM
Instead of reflective rolls, there is also a spray that can go on the underside of the roof. I had that done in my house here in Las Vegas at the same time I had more insulation added. The attic now rarely is 10 degrees warmer than the outside temp.

You also could look at zoning your HVAC system or adding a second unit just to cool the upstairs.

Kevin Bourque
07-28-2012, 5:25 PM
Check the joints in the ductwork in the basement for leaks.

Jason Roehl
07-28-2012, 6:36 PM
Check your filters. Also, hang blinds and close them on the south and west sides of the house in the afternoon and evening.

Ed Aumiller
07-28-2012, 6:46 PM
If it is two stories plus the basement then close registers on the lower floor so all air is forced to the second story.... the cold air will fall to the first floor and keep it cool also..
An attic fan will help lots also, just be sure you have vents in attic to draw in air and it is not drawn from the living area....
Reverse it in the winter.... open downstairs vents and close upstairs vents...

Wes Billups
07-28-2012, 8:06 PM
Thanks for all the responses. The basement is finished so sealing the duckwork will be extremely difficult. I change the filter every 3 months and have all the south facing window shades pulled. No windows are on the west side of the house.

I'm thinking my major issue is radiant heat coming from the attic. Our master is on the east side of the house and with it's tray ceiling gets extremely hot. I've considered the spray foam on the underside of the roof and may look for a contractor this fall. Can't imagine too many would want to go in the attic as it's pushing 140 up there right now.

There are peak vents and soffit vents that are clear as I made sure to clear the blown insulation from the soffits when we moved in.

Thanks,
Wes

Eduard Nemirovsky
07-28-2012, 10:25 PM
Wes,
I did have same problem two years ago. Same two-story house, one system, very hot in summertime. After installing reflective rolls underside my roof - dramatic difference. Temperature just 2-3 degree higher upstairs then on first floor.
Not expensive, took 4 hours for a two guys to install. But don't do it now - very hot in the attic.
Ed.

Mike Cutler
07-28-2012, 10:34 PM
Wes

Same issues here a few years back. I fixed it by doing three things.
I installed an attic fan, gable vent style.
I put new insulation in the attic. We had blown in insulation also. Sorry, imho it's junk! It compacts over time and loses it's ability to function properly.
Cooled the downstairs. You won't cool the second story if the first story isn't cool.

Good luck.

PS.
House is 2000. sq/ft, and with the highest electric rates in the US my electric bill was $177 this month, and the AC ha s been running daily,and nightly.

Robert McGowen
07-28-2012, 10:34 PM
When we built our two-story house, I put a door at the top of the stairs specifically to help with cooling the upstairs. As hot air rises, all of the hot air from the entire house will end up in the upstairs area. It is a habit for everyone to close the door at the top of the stairs now. You can really feel the difference, as the air at the top of the stairwell might be 10 degrees or more warmer than the downstairs air.

Rich Engelhardt
07-29-2012, 8:53 AM
We have a 4 bedroom split level. Three bedrooms are on the upper floor and the 4th is a guest room off the half sunken family room.
My wife and I used to move into the guest room for the Summer.

Jerome Stanek
07-29-2012, 9:08 AM
can you put a inline booster fan to your duct to your bedroom

Phil Thien
07-29-2012, 12:02 PM
Turn the furnace/AC blower on, and leave it on. Don't run it on auto.

Running the blower 24/7 will: (1) Equalize the temperature throughout your house. (2) Keep your air cleaner.

I know some people out there are thinking it will use too much electricity (it doesn't use that much power, these are typically 1/4 to 1/3-HP motors), or cause premature failure of the motor. When I moved into my home, the existing blower motor was a pain to access and as a result I didn't add oil to the oil ports as often as I should have. So it did only last about four years under constant duty.

So I replaced it with a high-quality, American-made permanently sealed BB motor (about $100) and it has been running ever since (12 years). I also redid the layout in the basement so if I need to get into the blower, I could do it very easily now.

Gary Max
07-29-2012, 12:17 PM
They make a product called Double Bubble Double foil------ will pay for itself the first year. If you have the space whole house fans really kick butt.

Myk Rian
07-29-2012, 1:11 PM
I retired from Ford, and our department pretty much perfected the process of balancing the paint ovens. The company had us traveling all over the country getting the ovens working properly.

Balancing air flow involves closing off the air closest to the source (furnace), and opening it up farther down the line. Works the same for supply and return air.

We have a Tri-level and it stayed warm upstairs. For a test, I covered the upstairs return air registers except for a couple inches left open. That forced more of the return air down-stairs, and gave a better mix.
Then I turned the fan on all the time. That kept the air moving, and also added to the air mixing.
It worked very well, especially during the 100 deg days we had recently.

ray hampton
07-29-2012, 4:16 PM
one fact is being ignored, the color of your roof, a dark roof will increase the temperature inside, if you install a white foil in the attic to reflect the heat back thru. the roof, will this lower the whole house temperature ?

Lee Schierer
07-29-2012, 8:25 PM
You need to check the air flow out of each register upstairs with a flow meter and compare that air flow to the down stairs registers. They should be the same. Also check the air temperature at all registers. Most likely you have significant air leaks in the duct work leading to the upstairs. You may also not have sufficient air returns on the second floor. A good HVAC company can help with this and yes you might need to open some walls to get to the duct work. If your duct work is running up outside walls or through the attic space most likely they are not well insulated and you are losing cooling in the uninsulated ducts. At $400 per month, it won't take long to recoup the investment to have a professional look at your system even if you have to open up some walls. On the Holmes Inspection series on TV they often encounter this type of problem and 9 times out of 10 it is poor duct work design and air leaks that are robbing the system of efficiency. Return air paths are not usually well done by contractors, they assume that drywall on studs and open cavities in walls will allow proper air flow back to the unit in the basement. Look inside your ducts to see what size the real opening back to the unit is. Your return air ducts on the second floor must be equal or slightly larger than the total square inches of the delivery ducts. The pro can also check to see if your compressor is working at optimum efficiency as well. You should have R40-50 in your attic. A hot 2nd floor ceiling indicates that the insulation isn't working.

When we upgraded our system a few years ago to add A/C we got a DC powered fan motor so it is variable speed. On the advice of the installer we run the fan on low 24/7 and it balances out the house temp due to sun loading. When the unit is actually cooling it jumps up one speed and then goes back to low once the temp is reached. The year we started the system we turned it on July 5 and ran it 24/7 until early October. We used exactly the same KW that summer as we had the previous year running fans and a dehumidifier. Our house is 2200 sq ft on one story and we pay about $110 per month for electricity (no gas, wood or oil bills either).

Angie Orfanedes
07-30-2012, 6:55 AM
All good advice. After you have done the upgraded insulation and checked your ductwork, you should consider adding a zone control damper and zone control board run from a second thermostat upstairs. That way you can have your upstairs calling for all the air (or heating) when it is bedtime. Since I presume you are a diy kind of guy, you should be able to do this for about $275 in parts.

Angie

Brian Ashton
07-30-2012, 7:22 AM
I've had it with this house. We live in a two story house with walkout basement. This is the second summer in the house and I'm tired of getting a $400 electric bill. It wouldn't be so bad if the upstairs was cooler than 80 degrees when I go to bed at night. There's only one forced air system for the whole house and I've got all the registers in the basement closed and still can't get decent cooling upstairs. There's plenty of blown in insulation in the attic so I'm looking for what else I can do. Below are a couple of my thoughts. Let me know what would be the most effective at reducing our energy consumption and improving the comfort on the second floor.


Reflective rolls against the underside of the roof.
Powered attic ventilation fan.


Input is much appreciated.

Thanks,
Wes

I've been living in Queensland for about 7 years now and one things for sure… it's the land of no insulation and steel or clay tile roofs… You want to talk about heat in the summer, attics can easily reach 45 degrees C, on a cloudy day. The cheapest alternative is to get as much air flow as possible into the attic. The more roof and soffit vents you have the more air flow you'll get. This has had good results on my house. The downside in your neck of the woods is cold winters where you don't want that air flow in the attic. Here winter mean you put on sox which is no big deal. Whereas you guys get real cold temps and air flow will cause your heating bill to go through the roof, so to speak. The more expensive is to insulate the roof and the ceiling. The roof insulation will inhibit the solar heat radiating into and heating the space in the attic and all the surrounding materials. And the ceiling insulation will stop most of any latent heat from radiating through the ceiling. The best is a combination of the two where by you can have controllable vents.

Brian Elfert
07-30-2012, 9:02 AM
As far as zoning after the fact do most two story houses have a single trunk line to second floor? I thought a lot of two story houses don't necessarily have just one trunk line for second floor? I had zoning installed in my two story house when it was built in 2001 for about $700 additional. I have a separate trunk line for the second floor for the zoning. My house is built with floor trusses instead of joists so running the duct work was easy for the HVAC guys. I like my zoning as it is common even in Minnesota for the second story to be hot in the summer and too warm in the winter.

I've heard that in Pheonix hardly anyone has two story houses due to the heat. The second floor just gets too warm.

A crazy idea might be to just move the thermostat upstairs so the upstairs controls the house temp, but it get too cold on the first floor.

Greg Portland
07-30-2012, 1:59 PM
How open is the upper floor to the lower level? If it is not sealed off then the cold air is going to flow right down the stairs (and the hot air is going to flow right up). In other words, closing off the downstairs vents are not going to help you and in fact will make the problem worse.

Assuming the duct work is properly designed and installed, running the air handler fan on 'low' will ensure that the air gets mixed effectively between the floors. Modern air handlers are extremely efficient so running it on low is pennies a day. My 2 floors are open to each other and running the fan keeps the temperature difference @ about 2-3 degrees (plus it keeps the air cleaner).

Now, how certain are you that your duct work is designed and sealed properly? How old is the home and what is the sq.ft.? I'd have a HVAC pro come out and inspect the home (at a minimum get someone who is NATE certified). They should be able to pinpoint your problem (insulation, air leaks, duct/system design, equipment, etc., etc.).

Finally, an old or poorly sized cooling system (low SEER, old air handler) is going to burn a lot of power compared with the modern efficient systems. Of course, the upgrade cost will be high. If the duct work has major problems a (large) mini-split system with multiple indoor units might be a more economical solution.

Myk Rian
07-30-2012, 5:51 PM
The downside in your neck of the woods is cold winters where you don't want that air flow in the attic..
Quite the opposite.
If the roof isn't insulated, then you still want all the air flow possible. That keeps the attic cold, and prevents ice dams on the roof edges, which can creep under the shingles and wreak havoc.
The more insulation on the attic floor, the better.

Carroll Courtney
07-30-2012, 6:21 PM
One of the problems w/houses that only have one system is not enought tonnage(400-500sq ft per ton) or lack of airflow due to a dirty coil,dirty filter,to small of a return air or an open return air(sucking hot air into the return)or maybe a dirty condenser coil.These are common problems here in Tx and I'm sure other places.If your in a subdivision and the floor plan is the same,check with your neighbor who has the same floor plan or same sq.ft for a comparision----Carroll

greg lindsey
07-30-2012, 8:04 PM
I had HD put in through one of their contractors 20" in insulation, spray radiant barrier and add 9 soffets (sp) for 1700.00 last summer, I have a pretty big attic. My electric bill has dropped by 75.00 a month, believe me. I know what its like having electric bills upwards of 600.00 a month. Besides new windows and sliding doors , that was one of the best investments in saving energy I have had. Example: Before they started I checked my attic temp , it was 123 within two hours of completing it was 103. Glad I wasn't up there doing it myself.

Brian Elfert
07-30-2012, 8:06 PM
Rules of thumb should not be used when sizing air conditioners. If you bring in a good HVAC contractor they will do a Manual J calculation that sizes the proper unit for your home based on insulation, number of floors, and other factors.

Pat Barry
07-30-2012, 8:58 PM
My opinion is that you are better off putting a window AC unit in upstairs. This is point of use and will be highly effective. Takes the load off the main unit and will net reduce your electric bill. Much easier than some of the other options.