PDA

View Full Version : How cold does it have to get for pipes to freeze?



Rich Engelhardt
12-22-2011, 6:34 PM
We have a ..situation...
We're having a dispute with one of our tenants.
Our lawyer has advised us not to enter the property for the next ten days.

We're concerned that the tenant is going to shut off the heat.


Temperatures are supposed to be in the low 30's as a high during the next four days and lows in the upper 20's over that period.

The house is insulated - but - not as well as a newer house. It was built in the 1950's.

According to the long range forecast, the tempertures are suppossed to be 30's to low 40's in the day and upper 20's to low 30's at night - through next Thursday.

I'm thinking that it should be ok but - you never know.

Gary Hodgin
12-22-2011, 6:36 PM
I don't think you have much to worry about, especially if the vents are closed.

JohnT Fitzgerald
12-22-2011, 6:58 PM
I would agree. If all the windows are opened though......might be close.

If it's all from issues with a tenant, check your various insurance policies to make sure you are covered under both accidental and malicious actions by a tenant.

ray hampton
12-22-2011, 7:04 PM
what bother me is your lawyer coment to stay out of the apartment, how will you handle the maintenance of the apartment ?

Rich Engelhardt
12-22-2011, 7:59 PM
It's not ouside the realm of possibility that a window or windows could be left open.

Ray - long story, but, our lawyer says it's best if we stay out for the next week or so. Sorry I can't be more detailed, but, this being an open forum it's better to not get into certain things.

Joe Pelonio
12-22-2011, 8:32 PM
I have seen outside faucets freeze at 28F overnight, if not wrapped, then break from the ice expansion. Maybe you could at least do that without going in?

ray hampton
12-23-2011, 3:41 PM
It's not ouside the realm of possibility that a window or windows could be left open.

Ray - long story, but, our lawyer says it's best if we stay out for the next week or so. Sorry I can't be more detailed, but, this being an open forum it's better to not get into certain things.


well it is your money so keep the de-tails to yourself which I never ask for, all I say were the maintenance of the building but you must be too busy to read the whole post

Rich Engelhardt
12-23-2011, 4:05 PM
Ray,
I read the whole post.

We've started an evicition process against the tenant. Under Ohio law, we as the landlords have procedures we have to adhere to. Entering the premisis during this time period is a very touchy area.

Yes - you are correct - it is my money. I don't wish to lose any by being sued or having to defend myself against criminal charges.

Mike Cutler
12-23-2011, 4:25 PM
Given enough time, 32 degrees F at sea level for fresh water. I'd worry about those temps for an extended time, but at least it's not going to be -5 degrees or so.
Good luck with the eviction process, it's tough. I watched a co-worker get danced around by a very experienced, legal wise, tenant for about 8 months through the court system. Once the eviction process started, he also was not allowed in his dwelling, and they did do some significant damage.

Myk Rian
12-23-2011, 4:38 PM
Sneak in, adjust the T-stat, and get out. Don't tell ANYBODY.

ray hampton
12-23-2011, 6:01 PM
I hope that none of your building catch on fire above or below this apartment that you are barred from enter

David G Baker
12-23-2011, 6:18 PM
I entered my rental accompanied by a police officer during the eviction process. My tenant stole several thousands of dollars worth of items from a detached garage that was not part of the rental. My dishes were in a drain basket on the sink and several other items belonging to me were in plain site but I couldn't do anything about it because I couldn't prove that the items were mine. The tenant was out in the 21 days allowed by California law. I found out how the items were hidden, the tenant rented a storage unit and moved my items into storage. Never got any of my items back but at least I got rid of the tenant. The place was a mess when I finally was able to gain access to work on it.

Rich Engelhardt
12-24-2011, 5:11 AM
Sneak in, adjust the T-stat, and get out. Don't tell ANYBODY.
That's not really possible to do. It also would halt the eviction process and we'd have to go back and start it all over again.
As you can see from the other posts, the law is heavily on the side of the tenant - up to a certain point.


[I hope that none of your building catch on fire above or below this apartment that you are barred from enter
In this case, we're ok there since it's a single family house, not an apartment building.
There's still houses on either side of it though.

Curt Harms
12-24-2011, 8:25 AM
Wisconsin has a law where you can't evict a tenant in the winter, apparently. I know of a situation where the tenant just quit paying rent in Nov. or Dec. and lived rent-free for a few months. They moved out when "winter" ended. Didn't do any damage though, thank goodness.

JohnT Fitzgerald
12-24-2011, 8:35 AM
There are definitely "professional renters" out there who know how to game the system. The trick is to have the right legal team experienced in dealing with the tenant's shenanigans, and the patience to let the process take its course (and not do something silly, like "Break into" the unit to check on it).

I would like to think that for each such "professional", there are many many legitimate renters.

Good luck with your situation.

David Larsen
12-24-2011, 8:52 AM
From my experience, the interior of an insulated / unheated structure is usually about 10 degrees warmer than the outside temperature. The pipes would have to get below 32 degrees F. to freeze.

Brian Elfert
12-24-2011, 8:55 AM
Why are laws so slated towards tenants that a landlord can't protect their $100,000+ investment?

It seems to me if you have rentals in areas with freezing weather that a low temp alarm could be installed. The only problem is most require a land line and a lot of people no longer have those. (Might not be allowed to connect to a tenant's line anyhow.) They probably have models that use cellular connections I suppose. Would a judge really not allow a landlord to check on a unit that is sending low temp alarms?

Myk Rian
12-24-2011, 8:56 AM
That's not really possible to do. It also would halt the eviction process and we'd have to go back and start it all over again.
As you can see from the other posts, the law is heavily on the side of the tenant - up to a certain point.
OK then. Pay a thief to do it.
Hell, give me $100 and I'll do it.

EDIT: Not that I'm a thief, mind you.

Mac Cambra
12-24-2011, 9:05 AM
In you can't go in I would recommend that you crack open one of the outside faucets, minimal flow, this will help prevent freezing and also allow for expansion should freezing happen.

ray hampton
12-24-2011, 10:52 AM
If the water are in your name simply call the water works and had it turn off, MERRY CHRISTMAS

Lloyd Kerry
12-24-2011, 11:10 AM
Now I remember why I got out of the apartment rental business in 1999! Best of luck, Rich.

Matt Meiser
12-24-2011, 11:11 AM
We've got a laundry sink in our unheated but insulated garage. The pipes to it don't freeze until it gets bitter cold unless Someone leaves the garage door open. I usually shut off the valves in the basement, well, about now, just to be safe but they've never frozen hard enough to do damage.

If you have good reason to believe they are intentionally vandalizing the place, can't you get the police get involved?

Rich Engelhardt
12-24-2011, 11:35 AM
I know this & my guarded replies can be frustrating. I'm just as frustrated....

First - thanks for the tips on the freezing pipes. I know my attached and unheated garage never get's cold enough to freeze anything until it gets well below zero.
I *think* we're going to be ok - at least I hope so.

Re: the situation.
We'll have to wait to see how the court decides. I really can't say any more than that. I can't do something based on what someone might do or might not do.

Kevin W Johnson
12-24-2011, 1:21 PM
If the water are in your name simply call the water works and had it turn off, MERRY CHRISTMAS


Even if he could legally do this, and he can't, it still wouldn't prevent the pipes from freezing unless they were drained.

Myk Rian
12-24-2011, 8:50 PM
Even if he could legally do this, and he can't, it still wouldn't prevent the pipes from freezing unless they were drained.
I think the idea is that there wouldn't be a flood.

Kevin W Johnson
12-24-2011, 9:36 PM
I think the idea is that there wouldn't be a flood.


Maybe so, but as long as there are tenants who occupy the rental structure, many states (if not all) prevent you from turning off utilities even if they aren't paying the rent.

ray hampton
12-25-2011, 12:36 PM
A certain city in OHIO are having a problem with the utilities because of the unpay bills, the tenants will pay their rent but the building owners refuse to pay the utilities bill and the tenant are the ones that suffer because of their utilities getting turn off, this were not just one time thing but it happen many time during the past decade, the U S A need a law that will work for the whole nation as a whole which will deal with providing heat to all renters and home owners, this law could be grandfather to protect the owner in case of the tenant being evict from the property

David G Baker
12-25-2011, 1:17 PM
Some seniors have died in their homes in Michigan due to utility companies turning off their power during the cold months due to their inability to pay. I think that Michigan has passed some legislation to stop the companies from cutting power and hold them accountable in the event of deaths.

ray hampton
12-25-2011, 1:40 PM
the utility s LIST includes cable, phone, water, electric and gas, the last two are for heat during the winter and for cooking, A C during the summer and cooking, turning them off will results in the murder of someone

Brian Elfert
12-25-2011, 1:46 PM
Minnesota has a law that does not allow utilities to turn off gas/electric during the cold months. I think plenty of people take advantage of the law and simply don't pay their bill until absolutely forced to. Service can be disconnected in the spring unless a payment plan is established.

One of the problems is lower income people tend to live in drafty homes that cost a ton to heat. I've heard of people here in Minneapolis paying up to $500 for natural gas in a really cold month. I live in a 10 year old house and my combined gas/electric bill has never been beyond $210 that I can recall. I have a budget plan with a $137 month a payment right now. I run the A/C at 75 degrees all summer long so that adds to my bill.

Daniel Berlin
12-25-2011, 3:09 PM
We have a ..situation...
We're having a dispute with one of our tenants.
Our lawyer has advised us not to enter the property for the next ten days.

We're concerned that the tenant is going to shut off the heat.


Temperatures are supposed to be in the low 30's as a high during the next four days and lows in the upper 20's over that period.

The house is insulated - but - not as well as a newer house. It was built in the 1950's.

According to the long range forecast, the tempertures are suppossed to be 30's to low 40's in the day and upper 20's to low 30's at night - through next Thursday.

I'm thinking that it should be ok but - you never know.

I'm a bit bored.
Assume they turn off the heat. Let's use math to waste some time :)

Heat loss in BTUs/hr is
HL = U-value * Area of wall (sq ft) * temperature difference
U-value = 1/ <sum of r values of layers>

(U-value is actually standardized to certain conditions, but it's all we've got :P)

A 2x4 stud wall with 3.5 inches of fiberglass is about R-15 (and a U value of 1/15)

IE the wall is 8x20, you would lose (1600*temp difference/15) BTUs an hour through that wall.

How many BTU it takes to raise or lower the air in your house one degree depends on the volume, but it's roughly 0.02 BTU to raise 1 cubic foot of air 1 degree.

Basically, as it gets closer to the outside temperature, the rate of cooling will slow down.
Worst case, assuming you have a 1600 sq ft home (which was average in 1950), and it was only walls (this is the worst case), and it was 35 feet tall (a lot of zoning codes in the country allow 35 feet from top to bottom), and it was square (40 * 40 ft), you have 40 * 35 feet of wall space on each of the 4 walls, or 5600 sq ft of wall space. Assuming it started out at 68, it will initially lose 14187 btu/h through the walls when the outside temp is 30 degrees (and the btu/h will decrease quickly as you lose temperature in the house).

You would have roughly 56000 cubic ft of air in this house (40*40*35), and it will take 56000*0.02 = 1120 btu to effect a 1 degree change in air temperature.
So over the first hour, it will lose 12.6 degrees.
The second hour, we start out at 68-12.6=55.4 and if it was still 30 degrees outside, it would lose 9482 btu that hour, or 9 degrees, roughly.
So the third hour, we are down to 46. If it was still 30 degrees outside, we'd lose 5973 btu that hour, or 5 degrees, roughly.
So the fourth hour, we are down to 41. If it was still 30 degrees outside, we'd lose 4100 btu that hour, or 4 degrees, roughly
So the fifth hour, we are down to 36. If it was still 30 dgrees outside, we'd lose 2240 btu that hour, or 2 degrees
So the sixth hour, we are down to 34. If it was still 30 degrees outside, we'd lose 1490 btu that hour, or 1.something degrees

etc
Again, remember these calculations are very much overestimating the temperature loss because it changes every instant as the temp difference goes down. I don't have mathematica to do this properly and am too lazy to do it by hand.

But basically, after the first day, inside your house is going to pretty closely follow the outside temperature, lagging behind by a few hours.

For the pipe containing your water, copper pipe heat loss for fluid inside 3/4 pipe with a 40 degree temp difference is 29 BTU/hr per foot. So it will take slower to follow the temperature, but there is less of it.
Water takes about 143 btu per lb to convert to ice (this is pure water).

Multiplying it all out, this theoretical house may actually have water freezing after the first day, at night, but its going to be close.
There are other things at play. If it's city water, it will tend to have a lower freezing point due to impurities. Additionally, once you hit back to the line you are sharing with your neighbors, , the heat from that water (at 40 degrees) is going to diffuse through the rest of the pipe/water over time. Same with all the other water that may get over 30 degrees.


All this said, i'd say
1. Its going to be close as to whether anything freezes. If it gets into the low 20's for more than a few hours, i'd be worried. If it stayed 30 degrees the whole time, i wouldn't be worried.
2. I have successfully used math to waste time.

David Larsen
12-25-2011, 5:09 PM
I'm a bit bored.
Assume they turn off the heat. Let's use math to waste some time :)

Heat loss in BTUs/hr is
HL = U-value * Area of wall (sq ft) * temperature difference
U-value = 1/ <sum of r values of layers>

(U-value is actually standardized to certain conditions, but it's all we've got :P)

A 2x4 stud wall with 3.5 inches of fiberglass is about R-15 (and a U value of 1/15)

IE the wall is 8x20, you would lose (1600*temp difference/15) BTUs an hour through that wall.

How many BTU it takes to raise or lower the air in your house one degree depends on the volume, but it's roughly 0.02 BTU to raise 1 cubic foot of air 1 degree.

Basically, as it gets closer to the outside temperature, the rate of cooling will slow down.
Worst case, assuming you have a 1600 sq ft home (which was average in 1950), and it was only walls (this is the worst case), and it was 35 feet tall (a lot of zoning codes in the country allow 35 feet from top to bottom), and it was square (40 * 40 ft), you have 40 * 35 feet of wall space on each of the 4 walls, or 5600 sq ft of wall space. Assuming it started out at 68, it will initially lose 14187 btu/h through the walls when the outside temp is 30 degrees (and the btu/h will decrease quickly as you lose temperature in the house).

You would have roughly 56000 cubic ft of air in this house (40*40*35), and it will take 56000*0.02 = 1120 btu to effect a 1 degree change in air temperature.
So over the first hour, it will lose 12.6 degrees.
The second hour, we start out at 68-12.6=55.4 and if it was still 30 degrees outside, it would lose 9482 btu that hour, or 9 degrees, roughly.
So the third hour, we are down to 46. If it was still 30 degrees outside, we'd lose 5973 btu that hour, or 5 degrees, roughly.
So the fourth hour, we are down to 41. If it was still 30 degrees outside, we'd lose 4100 btu that hour, or 4 degrees, roughly
So the fifth hour, we are down to 36. If it was still 30 dgrees outside, we'd lose 2240 btu that hour, or 2 degrees
So the sixth hour, we are down to 34. If it was still 30 degrees outside, we'd lose 1490 btu that hour, or 1.something degrees

etc
Again, remember these calculations are very much overestimating the temperature loss because it changes every instant as the temp difference goes down. I don't have mathematica to do this properly and am too lazy to do it by hand.

But basically, after the first day, inside your house is going to pretty closely follow the outside temperature, lagging behind by a few hours.

For the pipe containing your water, copper pipe heat loss for fluid inside 3/4 pipe with a 40 degree temp difference is 29 BTU/hr per foot. So it will take slower to follow the temperature, but there is less of it.
Water takes about 143 btu per lb to convert to ice (this is pure water).

Multiplying it all out, this theoretical house may actually have water freezing after the first day, at night, but its going to be close.
There are other things at play. If it's city water, it will tend to have a lower freezing point due to impurities. Additionally, once you hit back to the line you are sharing with your neighbors, , the heat from that water (at 40 degrees) is going to diffuse through the rest of the pipe/water over time. Same with all the other water that may get over 30 degrees.


All this said, i'd say
1. Its going to be close as to whether anything freezes. If it gets into the low 20's for more than a few hours, i'd be worried. If it stayed 30 degrees the whole time, i wouldn't be worried.
2. I have successfully used math to waste time.

Take into consideration the thermal transfer of windows. Yes, they do lose heat, but they also gain heat during the daylight hours and create a "greenhouse" effect on the interior temperature. Also, the inside of an insulated/ unheated structure doesn't normally fall to the same temperature as the outside air.

David Larsen
12-25-2011, 5:16 PM
Minnesota has a law that does not allow utilities to turn off gas/electric during the cold months. I think plenty of people take advantage of the law and simply don't pay their bill until absolutely forced to. Service can be disconnected in the spring unless a payment plan is established.

From my understanding if a person were behind on their utility bills, they have to set up and stick to a reasonable payment plan. If they fail to do this then they can be disconnected even if it is winter.

Kevin W Johnson
12-26-2011, 2:39 AM
Minnesota has a law that does not allow utilities to turn off gas/electric during the cold months. I think plenty of people take advantage of the law and simply don't pay their bill until absolutely forced to. Service can be disconnected in the spring unless a payment plan is established.



I can assure you that people DO take advantage of this. Many of those cases that I'm aware of, they HAVE the money to pay their bill. However they want to spend that money on something else, and will claim they can't pay it right up to the moment before disconnection, then pay it to keep their lights on. I really wish I could elaborate more on this, you'd be amazed.

It's sad really, cause it makes it nearly impossible to help out those who truly need it/deserve it, without the rest taking advantage and working the system to the fullest.

Curt Harms
12-26-2011, 8:18 AM
Kevin I know of some people like you speak of. They and their friends have figured out how to game the system. They know the right things to say to achieve their desired result. Pride and self respect? What a quaint old fashioned notion.

Chuck Wintle
12-26-2011, 11:08 AM
could you enter the premises with a police escort? there must be a way to have access to prevent possible major damage to this dwelling.

Joe Mioux
12-26-2011, 11:09 AM
Assuming you have Natural Gas, is there an outside meter that you can read and check to see if fuel is being used?

Rich Engelhardt
12-26-2011, 12:42 PM
http://www.sawmillcreek.org/images/misc/quote_icon.png Originally Posted by Daniel Berlinhttp://www.sawmillcreek.org/images/buttons/viewpost-right.png (http://www.sawmillcreek.org/showthread.php?p=1836212#post1836212)I'm a bit bored.


LOL! Yeah - Christmas Day afternoon can get like that! ;) I had some "down time" around noon yesterday right before we headed out for the Christmas dinner w/the wife's side.
Thanks for the calculations! BTW the house is listed on the county auditors website as being just under 900 sq feet.

Re: utilites.
We open ourselves to criminal charges if we shut off any of the utilites.

Re: access.
We're currently looking into gaining access to the property. Since it's a civil matter andinvolves real porperty, I believe the county sherriff has jurisdiction, not the police.
We have a call into our lawyer to see how we should proceed.
Due to the circumstances, even setting foot on the property is trickey.
Thank God we're having a warm spell. That's been the only thing keeping my wife and I sane the last few days.

ray hampton
12-26-2011, 1:39 PM
you will need to call the sheriff dept and ask if they are the person in charge if the paperwork do not say whom office issued it, I were evict once and also give up a house because of a tenant that refuse to pay his rent

Daniel Berlin
12-26-2011, 2:33 PM
Take into consideration the thermal transfer of windows. Yes, they do lose heat, but they also gain heat during the daylight hours and create a "greenhouse" effect on the interior temperature. Also, the inside of an insulated/ unheated structure doesn't normally fall to the same temperature as the outside air.

It would in fact fall to the same temperature, given enough time. Unless the laws of physics are broken, the temperatures will eventually equalize.

However at some point, depending on the level of insulation, the amount of BTU you lose per hour is so small as to be eaten by local temperature differences outside, and by then the temperature outside starts increasing again.
Additionally, there are other weird impacts you have to take into account that don't normally matter. For example, your water/chairs/tables/etc have some heat capacity, and when the ambient air around them gets to a high enough temperature difference, the BTU they transfer into the air will matter (particularly because water holds 62 btu per lb (or something like that) and air only 0.02, so 1 pound of water can heat a lot of air :P. Wood is similar )

Rich Engelhardt
01-03-2012, 7:20 AM
First off - thanks to everyone!

We finally gained access to the property yesterday. Just in time as the temperatures dropped under 20* last night and look to be staying there all week long.
The tenant had contacted the utility companies last week and had them shut off the services.
Nice huh? Lock us out & then have the gas and electric shut off - in the dead of Winter. :|

I can't say any more on that subject though since it's possible criminal charges may be forthcoming.

Ole Anderson
01-03-2012, 9:14 AM
Pipes on an outside wall are more likely to freeze than ones on an inside wall. I bet you will be ok if all of the pipes are on inside walls.

Curt Harms
01-03-2012, 9:23 AM
Rich I hope there was no major plumbing or water damage. I wonder if if would be possible to set something up with utility companies where if they receive a disconnect request on a rental property, they notify the owner of record? That doesn't seem like it'd infringe on anyone's rights or privacy and might possibly save an expensive mess. Of course someone with ill will could simply turn the heat off (and open the windows).

Rich Engelhardt
01-03-2012, 9:45 AM
Curt,
The utilities are supposed to verify ownership prior to shutting off service.
People lie though and sometimes the utilities take their word for it, apparently without checking first to see who the owner is.

Thankfully, we got to it when the temperatures were high enough.

Dan Hintz
01-03-2012, 11:15 AM
Yeah, but you don't always want to be the "owner"... if you are, it means you are ultimately responsible for any charges the tenant racks up. This varies from locale to locale, but one notable story was on Holmes on Homes a couple of years back. The house was in CA (Canada, not the home of San Francisco), and the tenants had burrowed through the basement wall to get to the electrical contacts before the meter... to steal the electricity for all of their grow lights, turning the entire house into a marijuana nursery. The electric company wanted $40k+, but luckily the house owner made the tenant get the electricity bill in their name, and therefore the tenant is (properly) stuck for it... if they can ever find/arrest them.

Rich Engelhardt
01-03-2012, 11:44 AM
Dan,
We always have our tenants put the utilites in their name. Water service requires a seperate meter for each side if it's a duplex. All of our units are single houses so we're ok there.

"Skip outs" can be and are a problem for the utilites.
One city, Cuyahoga Falls, has been trying to pass a law that the landlord has have the utilites in their name, then try to collect each month from the tenants or include the utilities in the rent.
Naturally, they won't help us out if we can't collect from a tenant, and they won't pay us a monthly fee for collecting payments for them....