Twice in the past couple weeks I've tripped the 100A breaker that feeds my shop from the house panel. On the first trip, I assumed it was a power outage since we've been having them rather frequently this year. I was home alone and it was light enough out to do some cleaning so I did that for an hour or so then went in the house and noticed a ceiling fan running and found the tripped breaker. After resetting I went back out and resumed work without issue. The second time I went in the house right away and found the breaker itself was almost too hot to touch, and obviously wouldn't reset. After allowing it to cool while I ordered a new breaker (see below), I reset it and resumed work without further issue. Both times, I've been running my 3HP cyclone, using AC (2.5T central AC), lights on, and I've been using a power tool. Its possible the trip occurred on AC startup but I don't know. It was pretty hot out both days it happened and the AC seems like its been on more than off.

The house panel is a Westinghouse (now Cutler Hammer) BR series. The breaker the guy before me installed is a Siemens or GE, forget which and I realized a while back it isn't rated for a CH panel. It been on my list to replace it but I haven't gotten around to it. I've ordered the proper replacement which I expect to get today. The shop panel also has a 100A main breaker. I hadn't thought to check if it was hot when I found the other.

I do plan to stick a clamp on meter on there when I've got the cover off and start up everything to get an idea. But I'm wondering--is it likely that the breaker is the problem or am I just pulling too much through it? I've never noticed a breaker that is hot before which bugs me. If I'm just pulling too much I'll have to start leaving the air off when I'm actually working.

Paul McGaha
08-04-2011, 2:52 PM
Matt,

Any idea what was running when it tripped?

100 Amps worth? If not, sounds like a problem with the breaker at the house or the feeder to the subpanel.

Just re-read your post, It sounds like you might have been pretty close load wise.

If you've got a clamp on amp meter, It would be easy enough to turn all that stuff on and amp out the feeder.

PHM

Dan Hintz
08-04-2011, 3:06 PM
A hot breaker screams fail to me... they do go bad, sometimes they're bad right out of the box.

Matt Meiser
08-04-2011, 3:11 PM
The second time I know I was running the cyclone (22A rated), AC (25A fuses), lighting, (? but I'd guess <20A), and my drill press which has maybe a 1/3HP motor. All of this was on (AC may not have been running) for a while before the breaker tripped. I can't remember for sure what I was doing the first time but know I had the cyclone, AC and lights on. And again, it was after the cyclone had been on for a while.

I definitely plan to check load with a clamp-on meter when I change out the breaker. I suppose one possibility is I have more 110 stuff on one leg than the other.

Edit: Me too Dan--hopefully that's it but I knew it should be changed anyway. The breaker came in today's mail so now I just need to find the time to shut everything down and change it out. The one in the panel is >7 years old because it was there when I moved in. Probably 15 or so from when they built the barn.

Rod Sheridan
08-04-2011, 4:30 PM
Matt, I'll buy you a beer if it's not a loose connection on the line or load side of your breaker.........Regards, Rod.

Steve Southwood
08-04-2011, 5:38 PM
What is the wire size from panel #1 to panel #2? Also distance?

Rich Noterman
08-04-2011, 5:46 PM
Matt,

I had this problem years back , it turned out to be aluminum wire, I change the feed to cooper and with the same breaker and never had a problem again. You may want to check what type of wire was used.

Rich

bruce buren
08-04-2011, 10:07 PM
I agree with loose connection, Check all connections, loose connection under load equals heating.

Ive wired many motors and terminals the last 15 yrs at the power plant I work at, and seen alot of burned up connections and terminals due to heating of a loose connection

Ole Anderson
08-04-2011, 10:27 PM
Correct me if I am wrong, but don't breakers heat up as they get close to design load, and isn't it the heat generated in a bi-metallic strip at the design load that will trip them, as well as use of a magnetic coil to detect a short circuit? Not to say that Matt may have another issue as he doesn't seem to be near the design amperage. Feel your breakers on a heavily used circuit like your DC and they should feel warm if the load has been on long enough to heat up not just the bimetallic strip, but the rest of the breaker as well.

Matt Meiser
08-04-2011, 11:04 PM
Well, I'll be retorting the connections when I change out the breaker. And since the existing breaker is the wrong type, it could very well have a bad connection on the buss in the panel, not to mention the load side. I'm not sure what the feeders are, but I'd guess aluminum on a 100a circuit run to an outbuilding.

I'd rate this as "hot" not "warm".

Mark Major
08-05-2011, 6:09 AM
I think Rod is right on with the loose connection at the breaker...have seen it many times albeit most often on the old buss fuses. But I'd tell Rod it was a faulty/worn out breaker just so I could get that beer. :D


Cheers, Mark.

Rod Sheridan
08-05-2011, 8:52 AM
I think Rod is right on with the loose connection at the breaker...have seen it many times albeit most often on the old buss fuses. But I'd tell Rod it was a faulty/worn out breaker just so I could get that beer. :D


Cheers, Mark.

Mark, I would too, however I'm betting that Matt has more integrity than me:D..................Regards, Rod.

Bruce Wrenn
08-06-2011, 1:41 PM
Wires being aluminum, don't forget the "no-ox."

Jim Neeley
08-06-2011, 2:12 PM
Alimonum wire has a much larger thermal expansion coefficient than copper. The resulting deforming of the wire during heating and shrinkage of the wire during cooling has been traced to many house fires. Quite a number of years ago in Alaska aluminum wiring was outlawed and I remember hearing the trend was speading nationwide but I have no idea how far or how fast it went.

As for me, I'd look hard at replacing the aluminum with copper, but YMMV.

Jim Neeley, EE

Matt Meiser
08-06-2011, 2:52 PM
Replacing is not an option for the sake of replacing. Its underground to the shop. I'd look at separate service before doing that because it could run from the pole to the shop without tearing up sidewalk, etc.

Rollie Meyers
08-07-2011, 3:00 AM
Alimonum wire has a much larger thermal expansion coefficient than copper. The resulting deforming of the wire during heating and shrinkage of the wire during cooling has been traced to many house fires. Quite a number of years ago in Alaska aluminum wiring was outlawed and I remember hearing the trend was speading nationwide but I have no idea how far or how fast it went.

As for me, I'd look hard at replacing the aluminum with copper, but YMMV.

Jim Neeley, EE


Aluminum alloy conductors are allowed by the NEC & if installed correctly is safe & reliable

Matt Meiser
08-07-2011, 9:37 AM
Ok, I changed out the breaker and did some load tests this morning.

First the old breaker was a Siemens. The screws on the load side weren't what I'd call tight but weren't noticeably loose. The contacts on the line side are spread further apart than the new CH breaker, and I'd guess they weren't making the best contact.

Base load for the shop, including the lighting, computer, mini fridge, etc showed 20a on one leg, 0.5 on the other. I think I'll rearrange some things in the shop panel to move one of the lighting circuits to the other phase and balance that better. I then turned on the AC, cyclone, and jointer/planer and saw about 45a/35a so I'm really nowhere close, except that I didn't have any blast gates open and wasn't putting a load on the j/p. Still, seems like I would be well away from 100a.

Paul McGaha
08-07-2011, 9:47 AM
Matt,

Yeah it does seem you're good load wise, Looks to be less than 50 amps on a 100 amp feeder and that should be great.

Hopefull you've got it fixed with changing out the breaker.

PHM

Dan Hintz
08-08-2011, 6:39 AM
As for me, I'd look hard at replacing the aluminum with copper, but YMMV.
The vast majority of houses out there use aluminum feeders coming into the main panel... aluminum works just fine, you simply need to make sure the connections are rated appropriately. Copper everywhere else.

Jim Neeley
08-08-2011, 2:11 PM
I did not say, nor did I intend to convey, that aluminum conductors are forbidden by the NEC.

Just in case anyone here is unaware, the NEC per se is not forced on any region in America nor does a new version being issued make it take effect in any area. These are concious choices by local jurisdictions. They can choose to accept a revision, accept it with revisions (usually stricter, sometimes with exemptions), or not accept it.

What I said is:

"Quite a number of years ago in Alaska aluminum wiring was outlawed and I remember hearing the trend was speading nationwide but I have no idea how far or how fast it went."

Alaska outlawed it due to a string of electrical fires and near misses whose root cause was tied to aluminum coming loose in the terminals due to the differing thermal expansion coefficient.

Alaska outlawing it, by definition, indicates it was done at the local (statewide) level. No state controls the NEC; it is an instrument of the National Fire Protection Association (NFPA). Technically, the NEC is known as NFPA70.

Rob Russell
08-08-2011, 2:58 PM
Matt,

I think you said you were going to properly torque the connections when you replaced the breaker. That's important - something most folks don't do.

Rob

Mark Ottenheimer
08-16-2011, 5:47 PM
If the breaker terminal is copper and connecting an aluminum conducted you must use no-ox or it will loosen up. I have seen heated main breakers because of bad connect from the aluminum service cable. A good practice is to check the main breaker lug every time you are in the panel if you have an aluminum service cable.

Steven Wayne
08-16-2011, 8:37 PM
I work as a NETA certified electrical testing technician. In english that means I test electrical systems for a living. While it is true that molded case circuit breakers used in these types of panels do fail, the majority of the time this type of problem is caused by a poor connection. There are two acceptable methods to test this type of connection - a low-resistance ohmmeter (DLRO or ductor) or torque check. The DLRO injects current (usually 10, 100 or 200 amps) and then measures the millivolt drop across the connection. I have seen hundreds, if not thousands of connections that "look" good that would fail this test with current passing through them. Since you most likely don't have a DLRO, torque check the connections.

Mike Henderson
08-16-2011, 11:43 PM
I had that exact problem with the main breaker coming into my house. The breaker would get hot and trip. I tracked it down to corrosion between the aluminum wires running from the meter to the breaker and the copper connections on the breaker. I pulled the meter (to turn off the power) and replaced the wires with copper. That fixed the problem permanently.

Mike

Ken Fitzgerald
08-16-2011, 11:53 PM
While aluminum may meet specs, I won't have it in my home or shop.

While waiting for base housing to come available while stationed at NAS Meridian, MS I lived in a rented trailer house. The landlord was an excellent landlord. He was an E-6 in the US Navy too. Nice guy. In the evenings after the kids went to bed and the lights were turned low, you could watch the sparks from the aluminum wires attached to the outlets in the house. It was a constant chore for the owner and I to tighten connections.

6 months after we moved into base housing, the trailer burned to the ground due to an electrical fire. I don't do aluminum. My shop I built a few years ago....200 amp service....The utility company's aluminum feed ties to my copper pig tail just outside the mast to the meter box. Copper through out. Yup it's expensive. So is replacing everything due to a fire....insurance doesn't tyically cover everything.

Just my personal preference.