I think I know the answer but wanted to run this by the group for verification.
I just ordered the Grizzly G0514x2 Bandsaw and in the specs it requires a 220 volt 20 amp circuit. This is my only 220 volt tool besides my Air Compressor which I have installed about 2 years ago. It required a 30 amp circuit, I wired it with 10 gauge wire. Anyway back to my question, as far as I can tell 220 volt 20 amp requires 12 gauge wire. I already have a bunch of 12-2 with ground romex left over from wiring the 110 outlets in my shop. Will this wire be sufficent for the 220 volt 20 amp circuit? I figure 20 amps is 20 amps. Just use the Black and White for each 120 leg and the bare ground for the ground. Does this sound correct?

Thanks Mike

Rod Sheridan
04-19-2011, 1:28 PM
You are correct Mike, just tape the white wire with red tape to indicate that is no longer a neutral wire.

Enjoy your new saw.......Rod.

Chris True
04-19-2011, 1:29 PM
20 amps is 20 amps, put a piece of red tape on the white wire on each end to signify it's use as a hot leg.

Al Burton
04-19-2011, 1:29 PM
You can do that but at least buy some red tape or black to wrap all of the exposed insulation on the white wire just so there is no confusion. The better option would be to buy some 10ga wire and run it and then you have the option of just changing out the plug and breaker later if you need to upgrade to 30.

Hmm three replies at once :O

Mike Cross
04-19-2011, 2:48 PM
Thanks for the quick replies. Now all I need is a breaker, receptacle and a plug.

Appreciate the feedback
Mike

Brian Kincaid
04-20-2011, 9:40 AM
The 20A breakers are nice because they take less room in your breaker box. If you want 30A you will need a double. It's a bummer because I often wish I had just installed 30A wire+breakers on all my 220V circuits instead of 20A. Each of my 3HP Grizzly machines and my 3HP Oneida cyclone has tripped a breaker on startup at least once over the years. With 30A though my breaker box would have run out of room fast.
-Brian

Dick Thomas
04-20-2011, 12:17 PM
Maybe I missed something here, but I think someone is waaaaayy off base: The OP asked about wiring a 220V circuit with 12-2 w/ground Romex. Not only NO, but H!!! No! (In the USA) Any 220V circuit requires an xx-3 w/ground wire, xx depending on the ampacity. For 220V you have to have 2 hot leads and a neutral. (In Europe, base voltage IS 220, so an xx-2 CAN carry 220) You can't (if you want to follow codes, that is) use an un-insulated ground lead as a neutral. So your 12-2 w/g is good for 20 amps of 110V, and for 20 amps of 220V you need 12-3 w/g.

And as for the 20 vs 30 amp breaker size, HUH? The physical size of the breaker depends 1) on whether you full height or 1/2 height breakers, and 2) whether you have single pole (110V) or double pole (220v) breakers. Boxes are designed to take full height breakers. Using 1/2 height breakers allows you to place 2 circuits in place of one, as long as you don't exceed the box design limits. IF your box is designed to supply 220V circuits (and most are), then adjacent slots are desgined to feed from alternate lines (hot line 1 then hot line 2). For a 220V circuit, a double pole breaker is used, and if full height, straddles 2 adjacent; if it's a 1/2 height, it straddles (for example) slot 4B and 6A, which are adjacent, on the right side of the box.

All of this info is pretty basic, and if not aware of it, I would recommend hiring a licensed electrician.

Rod Sheridan
04-20-2011, 12:32 PM
Maybe I missed something here, but I think someone is waaaaayy off base: The OP asked about wiring a 220V circuit with 12-2 w/ground Romex. Not only NO, but H!!! No! (In the USA) Any 220V circuit requires an xx-3 w/ground wire, xx depending on the ampacity. For 220V you have to have 2 hot leads and a neutral. .

Dick, that's not correct, a device that is only 2 pole only requires 2 conductors, plus ground, no neutral required.........Regards, Rod

Mike Cross
04-20-2011, 6:59 PM
That was my assumption as well, since my Air Compresser and Welder only has has 2 pole 220 with a ground. Heck my house is only 3 wire from the utility pole. With the ground and neutral bonded in the panel. I guess my real concern was with the ground being uninsulated.

Mike

Alan Schaffter
04-20-2011, 9:19 PM
Two hots and a gnd. 12-2 w/gnd ROMEX.

Al Burton
04-20-2011, 9:56 PM
Dick if you have an above ground service entrance take a look at it, there are two hots and a ground coming from the utility, if you run a neutral and a ground up to the weatherhead the power company will tie them together. In 110 the neutral is also a current carrying conductor but one that will not normally carry current all the time. Now 12/3 or 10/3 etc is used on quite a few things like driers etc that also need a neutral, normally 230(220) motors do not need a neutral so wiring with two current carrying conductors will work. The easiest way to think of it is that the appliances that need a neutral usually have electronics that require 115. If you wire a machine to use a 6-20 plug your only option is to cap the neutral or bond it to the ground, depending on your service panel.

Just to clarify further on your main service panel the NEC does not require ground and neutral to be seperated though most seperate, there is even a bonding bar included to connect the two bars. Now if you have a disconnect it is treated like a subpanel where they must be seperated. I brought this up to make you think about the role of the neutral wire and that it is used as a way to regulate the current on 115/110 circuits.

As for the breaker size, you are exactly right. Single pole and double pole breakers are the same size no matter the amp rating.

Dick Thomas
04-21-2011, 12:06 PM
Rod/Al: Mea Culpa! Engage brain before opening mouth! I guess I got scrambled & was thinking of driers, ranges, etc - of course they all use both 220 & 110 (controls, lights) and need the neutral. I don't have anything in the (in-progress) shop wired for 220, and pre-retirement, all 220 & higher equipment was 3-phase, Y!

Thanx for correcting me!

Kevin Flynn
03-24-2017, 10:04 AM
What do you do with the neutral in the outlet box? there are only three hookups on a receptacle?

Vince Rosypal
03-24-2017, 12:05 PM
What do you do with the neutral in the outlet box? there are only three hookups on a receptacle?

Depending on the device connected.... if it is a 220V three wire device then the neutral is not needed and can be capped in the box.... it should also be capped in the main panel
Some devices need 4 wire (including ground) thus a neutral if they are using 120 volt from one of the phases for control power

Mike Cross
03-24-2017, 4:22 PM
You guys realize this thread is 6 years old. Although the info is good, previous responders my not see recent activity.

Mike

Vince Rosypal
03-24-2017, 4:28 PM
You guys realize this thread is 6 years old. Although the info is good, previous responders my not see recent activity.

Mike

Ya I seen that but was responding to Kevin's question this morning

Lee Schierer
03-24-2017, 4:35 PM
The 20A breakers are nice because they take less room in your breaker box. If you want 30A you will need a double. It's a bummer because I often wish I had just installed 30A wire+breakers on all my 220V circuits instead of 20A. Each of my 3HP Grizzly machines and my 3HP Oneida cyclone has tripped a breaker on startup at least once over the years. With 30A though my breaker box would have run out of room fast.
-Brian

Note that the OP wants a 240 volt 20 amp circuit so he will have to use a 20 amp double breaker to achieve that.

Chris True
03-24-2017, 4:48 PM
Yes, well - the OP asked the question 6 years ago <g>.

Rollie Meyers
03-28-2017, 4:01 AM
In the US the voltage is either 208 or 240 volts, 220 is a pre-war voltage, where 220 still exists it is 50 Hertz & the color code is brown for the hot/live, blue for the neutral, and yellow with a green stripe for the grounding/ earth conductor, it is derived from 220/380V 3 phase wye or "star" as it is referred over there, line to neutral is 220V, line to line is 380V, the European Union "harmonized" the voltages to 400/230V because some countries like the UK, & France, were 415/240V & others were 380/220V so they went in the middle, nothing changed though other then 1 standard across the EU.

If you look at electrically heated appliances like ranges, dryers, water heaters they have 240 volt ratings, if the voltage were still 220, there would be reduced performance when they are operated at a reduced voltage, the elements will operate at a reduced wattage, a note though: ranges & dryers are 120/240V & do require a neutral as they have components that require 120V.