OK...I am FINALLY ready to bring 220 into my basement. Its a new house and I have allot of space on my box which is in the basement (and in the shop area).

I have 3 tools to bring 220 to and would like to be prepared for any future use if you think thats possible.I have a 2HP Bridgewood DC, 2HP PM60 jointer and my 1.5 HP Delta CS which I want to convert to 220v. I will use the DC with each tool, but never all 3 together. So can I share one CB with the 2 tools and a separate CB for the DC? Would it make sense to drop in a sub panel here? Finally if I do all the wiring fro from outlets back to the box...what is the rule regarding metal conduit? I have exposed rafters and concrete walls. I have 2 20-amp double gang CB's and all the 12/2 wire and outlets I will need...I just want to know what the next step is. I will get an electrician in to do the hook-up...but I want to move this forward this weekend so I can finally get going.CS is 8.6amps DC is 12amps and the jointer is 10amps.

Thanks for taking the time to read this (and for all the other help you guys give).

Rob Russell
01-19-2005, 10:22 PM
20 amp circuits for the machines are fine. You can run the 12/2 through all your joists with no problems. Sleeve the NM in conduit where you run it down a concrete wall. There is no problem sharing a circuit for more than 1 240v machine. Use twistlock plugs and receptacles - they are more expensive but give a better connection.

Jim Dunn
01-19-2005, 10:32 PM
Tim,

Now I want to preface this by stating that I am not an electrician but I do play one on weekends;) That said , yes you can share a single circuit breaker for the jointer and delta. You would just wire two separate outlets, or if the units are movable just unplug one and plug the other in the same receptical. If you think about it it's the same thing.

I can't possibly answer your question about conduit. That's a county/city/state thing regarding use of metal conduit, pvc conduit or exposed romex. Where I am, I can run romex in the floor joists so long as it's not running down a wall, where it could be damaged. A common sence approach would be to emulate the type of wiring already in your home i.e. if you have conduit all over your home then I would match that type of installation. Personally I ran pvc conduit through my shop. No local codes demand metal conduit.

Jim

Gary Sostrin
01-20-2005, 12:40 AM
You might want to use 10 gauge wire instead of 12 gauge, good to 30 amps. You must remember that there is an initial surge current (which I forgot-personal experience) which can be 30% higher than steady state and could trip a breaker. Also putting a sub panel in the basement is a good idea. You can add whenever you need. If you go this route use 6-8 gauge wire.

You should have at least 2 separate 120 V circuits and one 220v circuit.

For romex, it can be used in my area as long it is not exposed, like behind drywall. If exposed you might be able to get by with armoured cable (BX) check your local building codes

Jim Becker
01-20-2005, 12:51 AM
Tim, the DC should defnitely be on its own circuit. How you handle the other two tools is up to you, but realistically speaking, the cost to have one circuit for them and to have separate, dedicated circuits is not all that much different...the cost of a breaker pretty much and maybe a little more wire. I do have some circuits with "shared" outlets in my shop for 240v, largely left over from when I was moving things around a lot, etc. Presently, the actual sharing has dropped to none, although there are open outlets on two of the circuits available for convenience.

Ted Shrader
01-20-2005, 11:51 AM
Tim -

How many openings are left in the box? If 6 (or fewer), recommend put in a sub panel now. On advantage to having a sub panel is you can open the feeder breaker on the main box and power down all your tools. (Leave the light circuit on the main panel.)

Your plan for a dedicated DC circuit is good. The jointer and TS can be on a single circuit. But if you put them on dedicated circuits now, you can share the circuits with new tools that you will but in the future. :) :D :)

I have metal conduit running in my garage/shop. Not hard to run afte a couple of practice bends.

Ted

Lewis Mills
01-20-2005, 12:34 PM
Tim,
I went thru some of your issues a year ago, and decided on a subpanel. Even though it seemed like there was plenty of space in my main panel, 2 or 3 220 breakers and a handful of singles eat it up fast. I put the subpanel right in the middle of one of the long walls in the shop. It's only 25 feet from the main panel, but it is a lot easier running circuits to the sub than running each circuit that extra 25 feet. How you set it up will depend on your layout. If your main is already right in the middle of the shop, that's good. If you really have lots of empty spaces (like 20 or more) in the main panel, and you don't foresee any major home additions or remodels, that's good. Otherwise, I'd suggest a subpanel. Note that you might need a permit for a subpanel. I did.

About conduit.... Well, you said it's a new house, so this is a good time to get acquainted with your local code enforcement folks. If yours are anything like mine, they will be happy to tell you what you need to do. I think NM thru joists in an unfinished basement space is fine -- usually. Whether it's in the code or not, my code enforcement guy wanted conduit when I told him it was going to be a woodworking shop space.

The other responses are good ideas. But with all due respect, I've always understood that the general rule is that NM shouldn't be run thru conduit. I doubt that a short run from the ceiling down to a wall-mounted box would cause any problem, but might be something to sound out the inspector about.
Lewis

Wm Bauserman
01-20-2005, 12:58 PM
About conduit.... Well, you said it's a new house, so this is a good time to get acquainted with your local code enforcement folks. If yours are anything like mine, they will be happy to tell you what you need to do. I think NM thru joists in an unfinished basement space is fine -- usually. Whether it's in the code or not, my code enforcement guy wanted conduit when I told him it was going to be a woodworking shop space.

The other responses are good ideas. But with all due respect, I've always understood that the general rule is that NM shouldn't be run thru conduit. I doubt that a short run from the ceiling down to a wall-mounted box would cause any problem, but might be something to sound out the inspector about.
Lewis
Lewis is correct, the code is very unclear about when NM can and can't be placed in conduit. It say that NM can placed in conduit for protection over "short" runs (no definition of short though), other than that it is really up to the inspector's leanings. I'd call and ask the inspector first.

Steven Wilson
01-20-2005, 5:16 PM
Put in a subpanel; 50 or 60A should do. I run conduit to my 220V tools and find it fairly easy to reconfigure when I need to; THHN is fairly easy to handle when you get use to it.

Tim Morton
01-20-2005, 5:32 PM
[QUOTE]Put in a subpanel; 50 or 60A should do. I run conduit to my 220V tools and find it fairly easy to reconfigure when I need to; THHN is fairly easy to handle when you get use to it.


Ff I put in a sub panel, which is kind of where i am leaning...then I can do all the wiring to the sub panel, and then the electrician just comes into check everything and run one wire to connect the two? Sounds like the easiest way to tackle this project.

Rob Russell
01-20-2005, 5:51 PM
Tim,

Is there some reason you wouldn't install the subpanel yourself? It's basically the same as running circuit, just that there are 4 wires not 3.

If you're going to run a sub, run a 60 amp sub. Use NM 6/3, up in the floor joists to feed the panel. You need a "main lug" (sub)panel with isolated ground (neutral) and grounding bars.

You could rough in the wiring to the sub, connect at the sub, do all the branch circuit wiring to the subpanel and then connect the sub to the main if you felt more comfortable doing that. Pull a permit and have it inspected.

FYI, the NEC code section on conduit and NM says that NM must be run in condut when needed for protection. There is no statement that says "short lengths". That's one of the reasons that there are debates about running NM in conduit for longer runs.

Rob

Tim Morton
01-20-2005, 6:31 PM
I have an agreement with the wife, anything electrical must be done by a pro. Something to do with the quality of her sleep at night and her not needing anything "else" to worry about( her words :D ) So I will pick up a 60 amp sub panel and it will be mounted about 15' feet or less from the main panel, and all wires will be run to that. I am not sure if I need any permits here in rural vermont. My niece's boyfriend owns his own elctrical company, so i will check with him.

Rob Russell
01-20-2005, 8:03 PM
Ask your wife if she'll let you do all the rough-in work. That means hanging the panel, mounting boxes, running wire from the subpanel to the boxes, stapling wire to the wood, etc. You can leave the installation with no wires hooked up and go from there. It's worth a shot.

Tim Morton
01-20-2005, 8:09 PM
Oh, I will do all that....its just the last connection that she wants done by a pro. Its a peace of mind thing for her, and who am I to argue. it would be one heck of an "I told you so" if we were out on the street watching the fireman putting out the fire. :eek:

Wm Bauserman
01-21-2005, 9:44 AM
Tim,

FYI, the NEC code section on conduit and NM says that NM must be run in condut when needed for protection. There is no statement that says "short lengths". That's one of the reasons that there are debates about running NM in conduit for longer runs.

Rob
Technically you are correct, Section 336-6(b) says it must be protected and it doesn't limit the length. One of the problems that sometimes comes into play, is how inspectors like to apply Section 310-15(a)(2) which applies to derating the ampacities of the circuit. The exception to this section says it doesn't apply to conduit that is 10ft long or 10% of the total circuit length, whichever is less. I've seen some inspectors that won't allow NM in conduits over 10 feet long because of this.

Inspectors can seem to be quite irrational at times and I have even had them completely ignore sections of the NEC just because they felt like it. The question then becomes, how long and hard do you want to fight with the inspector? The usual answer is it is best to do it his way and move on.

Steven Wilson
01-21-2005, 11:16 AM
...then I can do all the wiring to the sub panel, and then the electrician just comes into check everything and run one wire to connect the two?

I don't know what the regulations are where you live so I can't answer the question. In my area home owners may legally perform electrical work on residences that they currently or plan to occupy - not rental property, not commercial property, etc. Given that, I had an electrician wire in a subpanel for me because I was busy with some other things and wanted it done quickly. I then obtained the necessary permits and wired the branch circuits to my 220V tools. Once completed, and before final hookup I had the local electrical inspector come out and sign off on my work. Then I hooked up the machines. All of this is necessary for the work to be legal. Before undertaking this work I obtained a relevant copy of the NEC (box fill calculations, sizing, etc.), some books on residental wiring, and ran by the electrical inspector what my plan was (our electrical inspector has time set aside for answering question early in the morning). I'm fairly comfortable in performing most electrical work but maintain a healthy respect for what can happen if things go wrong. I will also follow code and follow the legal requirements for my area.

Now, my question is how comfortable do you feel in performing electrical work? Do you know what you are legally able to do in your area? Do you know what the governing code is in your area? Are there any local variations to the relevant national code? If you know the answers to those questions then enjoy the work, it's fairly easy. If not, then you have some homework to do.

Be safe and do it right.

Tim Morton
01-21-2005, 11:21 AM
Now, my question is how comfortable do you feel in performing electrical work? Do you know what you are legally able to do in your area? Do you know what the governing code is in your area? Are there any local variations to the relevant national code? If you know the answers to those questions then enjoy the work, it's fairly easy. If not, then you have some homework to do.


I feel pretty Ok with doing all the wiring to the machines and setting up the sub panel, I will have help from a book, and friends. Where I DON"T feel comfortable is taking the main panel face off and playing around with the live wires. Hopefully i will be around when that part of the job is done so i can learn what to do and more importantly what NOT to touch :confused:

Steven Wilson
01-21-2005, 11:41 AM
Where I DON"T feel comfortable is taking the main panel face off and playing around with the live wires.

Well you shouldn't ever have to play with "live" wires. And yes having the panel cover off has a significant pucker factor. When I dig into the main panel (for wiring) I have the main breaker off and my wife around with a 4x4 to knock me off of a wire if I get shocked. When I work on my sub panel I turn off the sub's breaker on the main. Then I check for stray voltages on the sub panel, that's before my fingers get in there to work with anything. When I was initially working on my sub panel I just pulled it's breaker from the main panel and felt pretty safe working on the sub. Just have a healthy respect for what you're doing. BTW, your friends may not be of any help because you're wiring branch circuits for use with motors. Depending on your local electrical authority and how you wire the circuits you may need to following the part of the NEC that apply's to motor circuits and not branch circuits. I suggest you start reading the NEC if you aren't familliar with it.

Lewis Mills
01-21-2005, 12:11 PM
Ha! If I ever asked my wife to hang around with a 4X4 just in case, she'd knock me out with it before I even start and then call in an electrician!
Lewis

Rob Russell
01-21-2005, 12:35 PM
Technically you are correct, Section 336-6(b) says it must be protected and it doesn't limit the length. One of the problems that sometimes comes into play, is how inspectors like to apply Section 310-15(a)(2) which applies to derating the ampacities of the circuit. The exception to this section says it doesn't apply to conduit that is 10ft long or 10% of the total circuit length, whichever is less. I've seen some inspectors that won't allow NM in conduits over 10 feet long because of this.

Inspectors can seem to be quite irrational at times and I have even had them completely ignore sections of the NEC just because they felt like it. The question then becomes, how long and hard do you want to fight with the inspector? The usual answer is it is best to do it his way and move on.

If the AHJ wants to get into derating of bundled NM, it's still not an issue until you have a lot of NM running through a single run of conduit.

From 334.80, "The 90°C (194°F) rating shall be permitted to be used for ampacity derating purposes, provided the final derated ampacity does not exceed that for a 60°C (140°F) rated conductor." Using the 90 degree column and looking at Table 310.310.15(B)(2)(a) Adjustment Factors for More ThanThree Current-Carrying Conductors in a Raceway or Cable, you have to get more than 9 current carrying conductors bundled before derating becomes an issue for either #14 or #12. That means you can have (4) 14/2 or 12/2 NM through a conduit and - even with the 70% derating - you're still OK using 15 and 20 amp breakers respectively.

The issue here isn't whether or not the derating happens, it's whether or not the derating has any impact on the net ampacity of the circuit.

Steve,

I'm familiar with 430 (Motors, Motor-Circuits, and Controllers) because of my phase converter work. If Tim follows normal branch circuit wiring (#14=15 amps, #12=20 amps), uses plugs/receptacles to connect everything and doesn't have breaker trips when he's firing machines up - the normal branch circuit wiring methods will provide a more conservative setup than what's allowed under Article 430. In other words, Article 430 allows you to put more than a 15 amp breaker on #14 based on motor sizes and other factors. I really wouldn't go that route because it means those circuits would need to be dedicated to motor loads and that becomes restrictive in a home shop.

I'll agree that working in the main panel is pause for an extra safety check before pulling the panel cover off.

Rob
(Addy protocol - experienced homeowner electrician)

Gary Sostrin
01-21-2005, 3:26 PM
When wiring up different circuits, you might want to put 2 separate 120v circuits in each box like I did in all around my garage and maybe some separate circuits for specific purposes (extra refrigerator, etc) and use different colors (black, white, silver, brown, etc) for the recepatcles. That way you have a visual indication of what circuit is being loaded. I have installed both main panel (200 amp) and garage subpanel (125 amp), and found that the advanced wiring book by black and decker (I think) shows how easy it is. I always work with power off, and when doing the main panel , I had the electric company disconnect power in the morning and reconnect in the afternoon.

Funny thing when I wired up the main panel (200 amp) using 00 (I think) cable to the pole , and labeled it (2 highs and a ground), a few of us watched the main power being wired from the pole to the house. The first electric company guy cut off all the cables and left. The second guy not seeing what the first guy did started wiring to the pole. Unfortuneately he tied the ground to one of the poles high side. No one was hurt, and excellent fireworks show. The second guy was cussing at me until I told him the other guy cut of the labels. Electrical accidents are nasty. I always work when power is dead. Electrical accidents could be fatal and burns do not heal.

Wm Bauserman
01-21-2005, 3:45 PM
If the AHJ wants to get into derating of bundled NM, it's still not an issue until you have a lot of NM running through a single run of conduit.

From 334.80, "The 90°C (194°F) rating shall be permitted to be used for ampacity derating purposes, provided the final derated ampacity does not exceed that for a 60°C (140°F) rated conductor." Using the 90 degree column and looking at Table 310.310.15(B)(2)(a) Adjustment Factors for More ThanThree Current-Carrying Conductors in a Raceway or Cable, you have to get more than 9 current carrying conductors bundled before derating becomes an issue for either #14 or #12. That means you can have (4) 14/2 or 12/2 NM through a conduit and - even with the 70% derating - you're still OK using 15 and 20 amp breakers respectively.

The issue here isn't whether or not the derating happens, it's whether or not the derating has any impact on the net ampacity of the circuit.
I'm not disagreeing with you at all. What I am saying is that it really isn't clear cut in the NEC and that if the inspector decides to pull a section out of nowhere and apply it, what do you do? It is much easier to just go with the flow in most cases than to fight it. If the inspector doesn't like NM in conduit behind drywall, what are you going to do?

I have inspectors that want to disallow things we do everyday in new remote switching stations even though the code specifically states it does apply to these facilities. But if we fight them and prove we are right, what do we gain other than a mad inspector?

Michael Gabbay
01-21-2005, 3:47 PM
Tim -

Basically everyone has covered what I was going to say. I would strongly recommend the subpanel. When I finished by basement and built my shop I did that. It makes installing new circuits a snap. Also, I pulled all my cable and mounted all my boxes and had a friend (licensed electrician) do the hook up of the subpanel to main box. Working with live wires is somethiing definately left for the pros.

You may also want to cosider getting an electric permit from your county/city for the work. This will help protect you in case of an electrical fire with the insurance companies. I've seen insurance companies deny claims due to work that was never officially inspected. They'll do there best to not pay a claim.

my 2 cents...

Mike

Steven Wilson
01-21-2005, 5:15 PM
I'm familiar with 430 (Motors, Motor-Circuits, and Controllers) because of my phase converter work. If Tim follows normal branch circuit wiring (#14=15 amps, #12=20 amps), uses plugs/receptacles to connect everything and doesn't have breaker trips when he's firing machines up - the normal branch circuit wiring methods will provide a more conservative setup than what's allowed under Article 430.
I agree Rob, He shouldn't have a problem but it's up to the inspector. My inspector basically said that as long as I wire my machines with pigtails and plug them in then my circuits just need to be branch circuits. However if I hardwire something like a DC or air compressor then he would treat them as motor-circuits. In any case you still need to be aware of this stuff before you start. The most usefull part of the NEC I found were the table associated with do box fill calculations. It doesn't take many wires running through a conduit before you have to increase the conduit size, increase a box size, find a cover plate with more volume, or derate the wiring.