Scott Adamson
02-15-2011, 3:22 PM
Was curious to see what current users of this machine (1 phase motor) were using in terms of breaker size and wire gauge. I have about a 30 foot run from the panel. Machine does not arrive until March, but want to get the electrical installed now. My thoughts are 10/3 or 12/3 cable, NEMA 6-30, and 25 amp breaker. Appreciate your feedback.

Rod Sheridan
02-15-2011, 5:33 PM
Scott,
i'm Canadian so mine came with CSA electrical approval.

Mine is marked 16 amperes, protection not to exceed 20 amperes.

Felder can advise you on whether yours will have a maximum protection requirement also.

Mine's using a 6-20R with a 20A breaker.........Regards, Rod.

Brian Cosgrove
02-15-2011, 8:30 PM
I have Hammer A3-31. You only need 12/2 wire, 20 amp circuit with nema 6-20p outlet. 20 amp breaker is fine, per Felder USA.

Brian

Scott Adamson
02-16-2011, 3:42 PM
Rod, Brian, thanks for the clarification!