So.... I'll try to keep it short. :rolleyes:
Here's the problem..... during peak times, the AC unit seems to only be pumping room temp air through the house. When it's 88 outside at 1pm, it's 88 degrees in the house. "Non peak" hours, as in evening, night and early morning it's putting out good cold air.
1) 20+ year old house, original AC unit. About 1100 square feet of living space and a 2T Trane unit.
2) I've replaced the fan motor once, 2 years ago now.
3) The coils on the condenser unit are clean.
4) There's plenty of air flow out of the ducts so the "A coil" isn't clogged.
5) There's plenty of refrigerant in the lines and no leaks (tested with gauges).
It's been working fine until about 36 hours ago.....
I had a friend who's mostly an appliance guy (but does some HVAC and is certified) look at it tonight after work & he said "looks like an inefficient compressor". Is this a "normal" symptom of a compressor starting to fail? Inefficient would mean it was undersized 20 years ago, but it's always kept up and never had an issue for the 10 years I've owned the home.:confused:
The replacement compressor is about a $1k, a new unit isn't "that" much more... the refrigerant change from R22 to R401A (I think that's right) means the lines need to be flushed and maybe the A coil needs to be changed as well.
Anyone here have any $0.02 they can toss at me?
Thanks in advance.

Greg

Mitchell Andrus
06-21-2010, 8:30 PM
I had about the same thing happen last week... the blower in the house runs but it's not cool, the compressor outside won't run.

It was the starter cap on the compressor's fan that went bad. Sometimes its the little stuff that gets ya, not the big things. My kudos to the tech, he didn't even attempt to sell me on a new unit to replace my 15yo system. He just poked around with the meter and bingo! Had it running in 5 minutes and spent another 30 making sure all else was up to specs.
.

Prashun Patel
06-21-2010, 8:34 PM
I love this forum. The same thing has happened to me yesterday, and I'm online as we speak trying to troubleshoot it.

I can hear the motor on the outside unit hum for a minute or two after the call for power from the thermostat, but the compressor doesn't kick on. I'm placing a call to a tech tomorrow AM.

Chris Walls
06-21-2010, 8:36 PM
Greg

Does the A/C have it's own meter ? As in one that could shut off the compressor during the high cost hours ? Could it be faulty? If it works ok during hours that are off peak then it is likely that the compressor is not the culprit. It's in the controls.

I've been working AC/R for about 30 years. Compressors do not have a time schedule of their own, something is telling it not to run.

Chris

Greg Cole
06-21-2010, 10:07 PM
The compressor starts and stays on when the unit cycles.
I work with alot of industrial machinery and can read prints, check the cap's etc. Kinda scratching my noodle here about it....:confused:
I know compressors don't have a schedule, they kinda go or no go....
The only thing "controlling" the AC unit is the t-stat and right now it can turn on cold, heat and fan only options so it's ok.
My wife was off work today and said until 3pm it was "fine" & then all the sudden it got wasn't "fine". I had my friend come look it as described above... I shut it off, turned it back on and it's been ok since. But I do seem to notice the temp differential from inside to outside isn't as "good" as usual......
It's a bit of $ to just say screw it and replace the whole thing, but given the age of the AC and all.... it kinda is time and all.

Jim Finn
06-21-2010, 10:24 PM
"The only thing "controlling" the AC unit is the t-stat .............."
Some units have a high pressure switch which will trip when it gets to hot.

Mitchell Andrus
06-21-2010, 11:02 PM
You might want to check to see that the consensate drip pan is draining and that if it has a sensor that it works properly. Some will stop if the pan's drain clogs to keep from leaking in the house.

Greg Cole
06-22-2010, 9:26 AM
The unit doesn't stop, it just seems to stop putting out cold air after a few hours of running. :confused: The condenser and fan still run and will stay running for hours. If I shut the AC off for an hour or 2, it fires back up and puts out cold air again...:mad:

David Weaver
06-22-2010, 9:38 AM
Given that it was looked over by an A/C guy, i'm assuming it isn't an issue of restricted airflow causing it to frost over? I haven't had that happen to me, but I've heard other people talk about finding out that their A/C frosted over because their filter needed changed.

Pat Germain
06-22-2010, 10:12 AM
Those symptoms do indeed sound like classic freeze-up. As the unit runs, ice builds up until air doesn't flow well across the condenser. You'll still feel air coming out. But since it's not flowing across the condenser properly, it won't cool down. Then, when you shut it off for awhile, the ice melts. You turn it back on and it runs fine; until it freezes up again.

I'm no expert, but as I recall from previous incidents, there are multiple problems which can cause icing. Airflow is one of them. I'm sure any good HVAC guy can resolve an icing problem once it's diagnosed.

Lee Schierer
06-22-2010, 10:51 AM
Those symptoms do indeed sound like classic freeze-up. As the unit runs, ice builds up until air doesn't flow well across the condenser. You'll still feel air coming out. But since it's not flowing across the condenser properly, it won't cool down. Then, when you shut it off for awhile, the ice melts. You turn it back on and it runs fine; until it freezes up again.

I'm no expert, but as I recall from previous incidents, there are multiple problems which can cause icing. Airflow is one of them. I'm sure any good HVAC guy can resolve an icing problem once it's diagnosed.

I agree with Pat. When the cool air isn't flowing look inside at the evaporator and most likely it will be frozen. The usual culprit is poor air flow. This can be caused by a clogged filter or slipping fan belts. I think there is also a temperature cutout on the evaporator coil to prevent freezing. It should cycle the compressor off when the evaporator coil is cold enough to cool but not so cold that it freezes the condensate. If this switch has failed then the compressor would run too long causing the freeze up.

Another option is that the compressor is overheating and the internal thermal protection is preventing it from running. So you need to check to see that the compressor starts running when the outside fan in the condenser is running.

Greg Cole
06-22-2010, 12:56 PM
There's no frost anywhere. Plenty of CFM's in the registers... so the a coil isn't plugged. The filter is brandy new as well. Anyway... my thought on the intermittent cooling was MAYBE the contactor was starting to flake out under heavy loads but the unit conked out at 2am last night under less than peak load so, I checked it this morning and it was a-ok.
I just ran home to check on it again & finally the condenser wasn't running when the fan was still on and the t-stat was calling for cool air. Not a revelation, but something to work with! I checked both run cap's for the condenser and one was 9 mF of 16 & the other was about 12 mf of 30. They didn't show obvious signs of failure (usually you can see them kinda dome out the end with the terminals in them but a cap meter is a wonderful toy) I guess the condenser finally found the point where it tripped the internal overload from running w.out the cap's help.
I replaced both cap's and have to wait for the internal overload to reset. If it doesn't reset, it's toast. The replacement condensor is about $1k, which is about the point where I'd rather just replace it... but here's to hoping it comes alive when I get home and try to fire it up again. I have visitors coming from Vermont for 4 days... hopefully they have a cool house to welcome them!
Thanks for the hints.

Ken Garlock
06-22-2010, 2:29 PM
Being a late arrival on the is thread, I sense that we may have a problem with terminology.

First, the condenser is the set of coils that are normally wrapped around the compressor which sets outside the house. During normal operation the compressor fan will blow hot air out through the grill work at the top of the outside unit. The condenser's job it to cool the hot gas coming out of the compressor thus turning it back into a liquid.

Second the evaporator is the unit in your furnace plenum and is a coil of copper tubing and is configured often as an A. This is the only part of the AC that gets cold. It gets cold because the freon/coolant is under pressure and when the coolant flows through a very small nozzle called an expansion valve, it rapidly expands and absorbs the heat in the air that is blowing across the coils, thus turning it back into a gas.
This is real world example of the universal gas law: PV=NRT Simply said, if you change the pressure(P), or the volume (V) of a gas, the temperature(T) must also change. If we are dealing with only one gas we can toss out the NR constants that describe the nature of the gas. We can then say when we have two different conditions of the same gas: (PV/T)1 = (PV/T)2 which is Boyle's law.

So basically, the only place in an AC system that can ice over is at the evaporator. This is caused by several possible problems, bad expansion valve, or the incorrect amount of coolant in the system, or the furnace fan is doing its job.

Scott Shepherd
06-23-2010, 8:20 AM
Ken, I think you may have that backwards. All instances of icing up I've ever seen are on the outside unit only. I've seen mine, and several others, frozen up solid before. However, I've never seen the inside unit iced up.

Joe Leigh
06-23-2010, 8:42 AM
Ken has the terminology correct. The condenser coil is outdoors. The only time you'll notice ice on that coil is if the unit is a heat pump, operating in the heat mode, in which case that coil is referred to as the "outdoor" coil. In that case the outdoor coil becomes the "cold" coil, and given the right outdoor temp/humidity conditions, will accumulate ice.

If the system seems to cool ok during light load conditions such as night time or early morning, but struggles during the peak heat times (assuming everything else you told us was accurate) you are looking at one of two situations: First, the compressor is not running all of time that it is being told to run. This could be caused by compressor overheating due to dirty condenser coil, unit overcharged, condenser fan motor failure.
The second reason, and the one I'm leaning towards is inefficient compressor. This occurs when the internal valves fail internally in the compressor. When this happens the compressor will fail to pump, bypassing refrigerant gas internally. This can only be determined by a competent technician, an amprobe to measure compressor current draw, and a set of refrigerant gauges.

Pat Germain
06-23-2010, 9:03 AM
I was wondering if I had the condensor/evaporator thing backwards. Thanks for the correction, Ken.

Greg Cole
06-23-2010, 11:09 AM
The second reason, and the one I'm leaning towards is inefficient compressor. This occurs when the internal valves fail internally in the compressor. When this happens the compressor will fail to pump, bypassing refrigerant gas internally. This can only be determined by a competent technician, an amprobe to measure compressor current draw, and a set of refrigerant gauges.
Welp, me thinks Joe's got it right here. D'oh. :mad:
Seems as once a month since March I've had one large unplanned expense a month... I was hoping to get through June without.:rolleyes:

Jerome Stanek
06-23-2010, 11:20 AM
My unit will freeze up on the inside coil if my filter is plugged or there is to much humidity in my house.

Tom Godley
06-23-2010, 1:44 PM
The outside units will ice up in the winter -- if its a heat pump. You normally do not notice this when it is summer because the internal ductwork covers up the evidence.

If its straight cool - Then the outside will not ice up.

If everything is running -- and the unit is properly filled -- then you do have an internal problem. A system low on refrigerant may perform like this and will often freeze up.

Some units have more sensors than others -- some of the builder grade units will run until they die. The compressors do fail with the motors still running.

I would not fix the old unit -- especially if you have already changed the evaporator. The newer units are so much more efficient and also quieter. You want a matched set.

Joe Leigh
06-23-2010, 2:34 PM
If you're thinking of replacing the system you'll want to upsize a bit. 2 tons is undersized for 1100 square feet. Rule of thumb for residential application is 500 sq/ft per ton.

Lee Schierer
06-23-2010, 3:03 PM
I would not fix the old unit -- especially if you have already changed the evaporator. The newer units are so much more efficient and also quieter. You want a matched set.

If you need to replace the unit, some of the new units qualify for a 15-30% tax credit, which can ease the pain of purchase considerably. In the long run a new unit will use less energy for the same cooling.

JohnT Fitzgerald
06-25-2010, 9:57 AM
Ken, I think you may have that backwards. All instances of icing up I've ever seen are on the outside unit only. I've seen mine, and several others, frozen up solid before. However, I've never seen the inside unit iced up.

The inside unit can indeed ice up, and you can still get airflow with 'icing'. Another cause of icing is low refrigerant level - sorta counter-intuitive, but it's the way refrigeration works.

Pat Germain
06-25-2010, 10:45 AM
If you need to replace the unit, some of the new units qualify for a 15-30% tax credit, which can ease the pain of purchase considerably. In the long run a new unit will use less energy for the same cooling.

That's a really good point, Lee. It's painful to pony up for a new HVAC system. But after you do, it's really nice to be more comfortable for less dollars per month.

Chris Kennedy
06-25-2010, 8:56 PM
Ken, I think you may have that backwards. All instances of icing up I've ever seen are on the outside unit only. I've seen mine, and several others, frozen up solid before. However, I've never seen the inside unit iced up.

Not to cause trouble, but he may not have it backwards. I make no claims to having any sort of HVAC knowledge, but I have had my internal unit ice-up while my external unit is free and clear. There was some issue with the blower, and the external unit was working nicely, sending cold air in, but it wasn't being blown out and the unit iced up.

Cheers,

Chris

Jim Finn
06-25-2010, 10:20 PM
In my experiance as an air conditioner serviceman I have seen the inside (evaporator) coil freeze up but not the outside (condenser) coil except in the case of a heat pump. Is this a heat pump?