PDA

View Full Version : Sub-Panel questions



Jay Maiers
05-23-2010, 6:28 PM
Hey folks,
I want to install a sub-panel next to the existing house panel. I'd like to run 100A service to this panel to cover general lighting, a smallish wood working setup, and a pottery kiln.

1) Am I allowed to run power out through the bottom of the existing panel, throught the stud, in through the bottom of the new panel, and up to the main breaker lugs at the top? (I'm planning on using 2-2-2-4 Aluminum for this connection)

2) I picked up a Siemens panel that looked like it would fit my needs. During test-fitting, I found that the door for the new panel overlaps the breakers on the first panel. Will this pass inspection, or do I need to find a different panel (with a narrow door)?

Thanks!
Jay M

Rob Steffeck
05-23-2010, 6:56 PM
I just finished wiring my shop a few months ago and did something very similar, except I skipped a stud bay. So my 100A sub is 16" away from my main panel. I used #2 NM-B copper feeder from the main using a 90A breaker (#2 copper is rated at 95A, aluminum is less...75A I believe). I routed the feeder out of the bottom of the main panel, through the stud, up through the empty bay, through the stud, then down through the top of the sub-panel. Can you skip a bay and go this route?

If not, you could always mount the subpanel upside down to avoid taking up the space inside the sub by routing the feeder through it. If your sub is a main lug, then it shouldn't matter at all to mount it upside down.

The door / trim overlap sounds like it may be your big problem. I know the panel covers for my main and sub would not allow them to be in adjacent stud bays even if I wanted them to.

Dan Friedrichs
05-23-2010, 7:09 PM
I'm not a code expert, but there is nothing technically wrong with what you suggest.

However, is this work going to be subject to inspection? If so, you should simply ask the inspector these questions, because his opinion is what matters, and his opinion may not even agree with code.

As Rob said, since you won't have a main breaker in the subpanel, you could mount it upside down if that's more convenient.

Since the run between panels is so short, consider using copper wire, instead. The smaller size (for the same ampacity) will be a huge help when trying to route it.

Jay Maiers
05-23-2010, 7:20 PM
I routed the feeder out of the bottom of the main panel, through the stud, up through the empty bay, through the stud, then down through the top of the sub-panel. Can you skip a bay and go this route?

If not, you could always mount the subpanel upside down to avoid taking up the space inside the sub by routing the feeder through it. If your sub is a main lug, then it shouldn't matter at all to mount it upside down.

Thanks Rob.
I can't skip a bay. The existing panel is near the outside wall of the basement; the next opening is the only one on that wall that will fit the panel. I could run the feeder past the panel, up the wall, and back through the stud, but that seems a bit absurd. Your suggestion about turning the panel upside down is a perfect answer to both issues if it's permissible. I don't see why it wouldn't be, but who knows?

Dan, this will be inspected bofore it's all over. I'm really in my planning stage (new house, big basement playroom :) ); I bought the panel to help visualize the issues, and so that I can get going ASAP. I have exactly one outlet and five lightbulbs in a 1000+sf basement :rolleyes:

I'll look at the copper wire. Can I pull individual wires, or does this have to be a bundled cable? From what I've read, individual cables seem to be a legal and reasonable way to go, but I'm very new to this level of wiring.

Don Jarvie
05-23-2010, 7:28 PM
Do you know an electrician that could answer a few questions? I don't see why you can't go in from the bottom (I'm not an electrician) since they have knockouts in the bottom. If it was against code then they wouldn't make holes in the bottom.

Dan Friedrichs
05-23-2010, 7:33 PM
Your local building inspector's office should be able to answer these questions for you easily. If it didn't require inspection, I'd do it exactly as you want, but since it does...





I'll look at the copper wire. Can I pull individual wires, or does this have to be a bundled cable? From what I've read, individual cables seem to be a legal and reasonable way to go, but I'm very new to this level of wiring.

Will there be conduit between the boxes? If so, use individual wires.

Rollie Meyers
05-23-2010, 8:17 PM
Hey folks,
I want to install a sub-panel next to the existing house panel. I'd like to run 100A service to this panel to cover general lighting, a smallish wood working setup, and a pottery kiln.

1) Am I allowed to run power out through the bottom of the existing panel, throught the stud, in through the bottom of the new panel, and up to the main breaker lugs at the top? (I'm planning on using 2-2-2-4 Aluminum for this connection)

2) I picked up a Siemens panel that looked like it would fit my needs. During test-fitting, I found that the door for the new panel overlaps the breakers on the first panel. Will this pass inspection, or do I need to find a different panel (with a narrow door)?

Thanks!
Jay M

#2 AL is only good for 90 amperes, since it is not a residential main service you are not allowed to undersize your conductors, subpanels, feeders to outbuildings must use full sized conductors. You must use table 310.16 for sizing conductors,table 310.15(B)(6) does not apply.

Here is a copy & paste from the 2008 NEC which is unchanged from the 2002,2005 editions. 310.15(B)(6)

(6) 120/240-Volt, 3-Wire, Single-Phase Dwelling Services
and Feeders. For individual dwelling units of onefamily,
two-family, and multifamily dwellings, conductors,
as listed in Table 310.15(B)(6), shall be permitted as
120/240-volt, 3-wire, single-phase service-entrance conductors,
service-lateral conductors, and feeder conductors
that serve as the main power feeder to each dwelling unit
and are installed in raceway or cable with or without an
equipment grounding conductor. For application of this section,
the main power feeder shall be the feeder between the main disconnect and the panelboard that supplies, either by
branch circuits or by feeders, or both, all loads that are part
or associated with the dwelling unit. The feeder conductors
to a dwelling unit shall not be required to have an allowable
ampacity rating greater than their service-entrance conductors.
The grounded conductor shall be permitted to be
smaller than the ungrounded conductors, provided the requirements
of 215.2, 220.61, and 230.42 are met.

Tom Godley
05-23-2010, 8:30 PM
Is the main panel short on open spaces?

If you have two extra open spaces I would run the kiln directly off the main panel-- this would allow for a smaller sub-panel.

100 amp is a lot of power.

Jay Maiers
05-23-2010, 8:48 PM
Is the main panel short on open spaces?

If you have two extra open spaces I would run the kiln directly off the main panel-- this would allow for a smaller sub-panel.

100 amp is a lot of power.

Tons of physical space available, but they used the slimline breakers and have taken all but two or three of the ground and neutral openings on the bars. I could probably get by with 75 or 80A, enough for the kiln, the lights, and a couple of utility outlets.

Dan Friedrichs
05-23-2010, 8:59 PM
You have room in the main box, but are just short on lugs for the neutrals and grounds? You can move those neutrals and ground around and place more than one in each screw hole (if there's room). You could also add additional bus bars for more neutral and ground connections, and bond them to the existing neutral and ground bus bars.

Jay Maiers
05-23-2010, 9:00 PM
#2 AL is only good for 90 amperes, since it is not a residential main service you are not allowed to undersize your conductors, subpanels, feeders to outbuildings must use full sized conductors. You must use table 310.16 for sizing conductors,table 310.15(B)(6) does not apply.

Huh. Thanks Rollie. Looks like I was working off of the wrong table. I'll have to decide if I want a true 100A at that panel or not.

This is the first time I've had to apply for a permit. Since I'm not familiar with the process, I'm trying to knock out all of the reasonable questions / "get my ducks in a row" before setting up any appointments.

Thanks everyone.
Jay M

Tom Godley
05-23-2010, 9:55 PM
The point of placing the kiln directly on the main is it would eliminate the need to plan for the load on the new panel. Since the panels are close to one another what is the need for the kiln on the sub

You can add bars to increase the spaces for the neutrals and grounds-- but you still must say within the listed maximum number of circuits on the panel

Tom Vanzant
05-24-2010, 12:32 PM
Jay,
Are the lugs compatible with aluminum wiring?
Tom

Darryl Hazen
05-24-2010, 4:35 PM
Before you use aluminum wiring do a Google search for "aluminum wiring dangers". You may want to reconsider. I owned a house in CA where aluminum was permitted. Three home in the area burned to the ground within a year. Fire inspectors findings: aluminum wiring. If I were you I'd bite the bullet and use copper.

Roger Jensen
05-24-2010, 5:36 PM
100A is a lot of power. Are you going to be running multiple heavy machines simulaneously? I ran a 60A sub-panel in my one-person shop and have never been short of power. If you're adding that much you may need to upgrade the lines to your house. Do you know how much capacity the lines to your house have?

Roger

Bruce King
05-24-2010, 6:27 PM
Lots of errors are made with sub panels. I inspect houses for a living and see it all so here is some advice.....

Sub Panels must be fed with a 4 conductor cable. The neutrals and grounds must be on seperate busses. This is known as "floating neutral". Only the ground bus can be bonded to the metal box with the (usually)green screw. Also the neutral wires must be connected seperate under each screw, no double tapping allowed on hots or neutrals. The exception for hot wires is on the breakers designed for two wires. The way to tell if it is designed for two wires is that the wires do not touch each other when installed on the breaker. FYI, the correct term is "panel" but I like sub panel since everyone knows what they are. Technically you only have "main panels" or otherwise known as "service equipment" and then all else is just a "panel". The only place where the neutrals and grounds are connected together is at the service equipment or main panel.

Jay Maiers
05-25-2010, 7:48 AM
Jay,
Are the lugs compatible with aluminum wiring?
Tom
I certainly hope so. It appears that the inbound power is on aluminum. I can't really see any wire around the two main lugs, but the third cable that I can see is aluminum.


Before you use aluminum wiring do a Google search for "aluminum wiring dangers"...

Yeah, I've done a bit of reading on that subject; my understanding is that you have to use some sort of conducting compound where the wire joins the lugs, and check the torque values once in a while to make sure that the wire expansion has not loosened the connection.

However, as short of a run as this is, copper won't break the bank.

Dan / Tom, I'm one grounding slot shy of putting two big breakers in the existing box. I don't like the idea of doubling up the ground or neutral connectors, and it seems silly to add ground and neutral bars to the existing panel, plus add the extra panel. However, it's a valid point, and I'm re-thinking things right now. After taking a careful look, I've got a LOT more planning to do. One thing that I am sure of is that I do want an additional panel. I like the idea of segregating the shop / downstairs power for safety (lockout) reasons as well as the ability to run power and work on things without shutting down the main power panel. It just makes good sense to me. I know it'll cost a couple of hundered bucks to get the panel in and working, but I think it will be worth the money and hassle in the end.

Jay Maiers
05-25-2010, 8:14 AM
After thinking about it, I don't think the house will allow more than another 50-60A during the summer. The house has (2) AC Units with a 70A breaker, plus the normal house stuff.

During the winter (gas fired heat)If I fire up the kiln (60A breaker) plus the lights in the basement (10-15A, depending on how many lights I turn on), plus a small tool and dust collection, I'll probably be over 60A. Do I need 100A? No. 75-80 would probably suffice. I picked 100 to keep from flipping breakers or starving any point of the system. I was stuck for way too long in a garage shop with inadequate power. I can't tell you how many times the compressor kicked on right in the middle of a cut, tripping the breaker :rolleyes:


Bruce, the panel that I picked has a thick bonding wire stretched across the breaker mounts, and screwed into the bars. I'm assuming that I just have to cut that wire in order to seperate the two.

As soon as I can figure out who has inspection jurisdiction (county or city) and which office to call, I'll be able to get some more concrete info. Until I know if I can mount that panel upside down or if I am really allowed to bring the power in through the bottom, I'm sort of stuck in limbo. Not really a bad thing since I still have boxes of stuff all over the house, waiting patiently (along with my wife) for me to put them away :D

Thanks everyone!

Rollie Meyers
05-25-2010, 8:39 AM
Bruce, the panel that I picked has a thick bonding wire stretched across the breaker mounts, and screwed into the bars. I'm assuming that I just have to cut that wire in order to seperate the two.

As soon as I can figure out who has inspection jurisdiction (county or city) and which office to call, I'll be able to get some more concrete info. Until I know if I can mount that panel upside down or if I am really allowed to bring the power in through the bottom, I'm sort of stuck in limbo. Not really a bad thing since I still have boxes of stuff all over the house, waiting patiently (along with my wife) for me to put them away :D

Thanks everyone!

The only thing preventing mouting a panel "upside down" is if there was a vertically mounted main breaker because the "ON" position has to be up, which is why most resi panels have been redesigned w/ sideway's operating main breakers.

Do not cut the bonding between neutral bars, buy a ground bar kit instead,a split neutral is for ease of wiring.

Dan Friedrichs
05-25-2010, 9:32 AM
Also the neutral wires must be connected seperate under each screw, no double tapping allowed on hots or neutrals.

I thought multiple ground wires under screws was allowed. Clearly you can't put both the neutral and ground under the same screw on a sub panel, but you can put multiple grounds under the same screw.


Jay - if you're only one ground lug shy in the main panel, you should consider just moving some of the existing ground wires out of their own spots and making them share a spot with other existing grounds.

Don Jarvie
05-25-2010, 1:17 PM
Jay,

A few thoughts, if your worried about not having enough amps then have you service into your house upgraded to 200 amp. This will provide plently of power.

Instead of a subpanel, put in a full panel with a 100A breaker to power the shop/kiln. All you need is 2 slots in your main panel for a 100 A breaker. The beauty of a full panel is you can have plently of slots to run lines throughout your shop. Sub-panels limit you to 6 or so slots.

It's probably worth the money to bring in an electrician and upgrade your system especially since the kiln pulls all that power.

John Coloccia
05-25-2010, 2:08 PM
re: multiple neutrals under the same screw
Under certain conditions, that MAY be allowable if I'm remembering correctly. I forget exactly what criteria exists for that. As a general rule, though, it's not allowable.

You can put up to 3 ground wires under together provided that they are the same gauge and that the panel is rated for it.

That's my understanding.

I believe part of the reasoning for these rules is to prevent a situation where a current is forced through the screw, instead of the bar, or where a 30A ground fault coming in through a 10AWG wire travels through the 14AWG wire it's bundled with. That would be VERY bad. It's always a VERY good idea to refer to the NEC when doing any wiring as these guidelines are usually in place for a good reason.

Dan Friedrichs
05-25-2010, 3:59 PM
re: multiple neutrals under the same screw
Under certain conditions, that MAY be allowable if I'm remembering correctly. I forget exactly what criteria exists for that. As a general rule, though, it's not allowable.

You can put up to 3 ground wires under together provided that they are the same gauge and that the panel is rated for it.


Yeah, John - you're right. If the box is rated for it, multiple grounds can be put under a single screw, but not multiple neutrals. I appologize for misstating that in my earlier post, and corrected it.

Joe Wiliams
05-25-2010, 8:02 PM
Regarding side by side panels & the covers (having the panels in adjacent bays).

Is there a way to make this work?

John Coloccia
05-25-2010, 9:44 PM
Yeah, John - you're right. If the box is rated for it, multiple grounds can be put under a single screw, but not multiple neutrals. I appologize for misstating that in my earlier post, and corrected it.

No biggie. Multiple eyes on a problem has picked up many boo boos in my line of work...usually mine. LOL.

Jay Maiers
05-27-2010, 7:09 AM
Regarding side by side panels & the covers (having the panels in adjacent bays).

Is there a way to make this work?

The original panel has a narrow door in the center of the box. If the new panel had the same size door, it wouldn't be a problem. Unfortunately, it's a wide door, so I'm going to mount the new panel on the right side of the old one, and upside down so that it opens away from the existing panel.

Brian Cover
05-31-2010, 7:07 PM
1) Am I allowed to run power out through the bottom of the existing panel, throught the stud, in through the bottom of the new panel, and up to the main breaker lugs at the top? (I'm planning on using 2-2-2-4 Aluminum for this connection)


Why not just drill a hole in the side of each panel and bridge them with 1.5" conduit? That is much easier than trying to route wires through a hole in the wall, through a stud, and back into a panel.

That's how I install panels.

Greg Woloshyn
05-31-2010, 9:00 PM
Quick question: I have a sub panel I'm installing with a 60 amp breaker that is going to be connected to an existing sub panel in the house that is only fed with 50 amps. Will I still be able to install a 60 amp breaker for my new panel?

Jay Maiers
06-01-2010, 10:38 AM
Why not just drill a hole in the side of each panel and bridge them with 1.5" conduit? That is much easier than trying to route wires through a hole in the wall, through a stud, and back into a panel.

That's how I install panels.

Not a bad idea, but the existing wiring (inside the main panel) would have to be removed and reconnected. there's next to no open space on that side of the panel. The other side is nice and open, unfortunately there's no room for the new panel without removing / changing the wall stud layout.