View Full Version : Ridge beam and rafter sizing?



Jerry Olexa
06-25-2009, 5:09 PM
Considering adding an addition with open "cathedral" ceiling (to avoid trusses). Span will be 20' with 2' roof overhang on each end. I'm considering 2 or 3 2X10's laced together as ridge beam (since it will be supporting the load) supported by several vertical 2X4's burried in wall to support the beam. Rafters probably 2X8's or 2X10's on a 18' span resting on beam. Is this enough or do I need a engineered wood lam for the ridge beam? I would probably do mockup beams accross acting as cross beams or ties on 4' centers. I usually overkill. Am I on track?

John Callahan
06-25-2009, 5:49 PM
Any particular reason to avoid trusses? A scissors style truss will give you the cathedral ceiling and more than likely allow more room for insulation plus eliminate the ridge beam. Should go up much faster, too. Downside is that a it's not really a true cathedral ceiling; the inside pitch won't mimic the exterior pitch because of the need for the interior truss components- the inside pitch is shallower.

Frederick Wilt
06-25-2009, 5:58 PM
How about going with a true timber frame? It's a fine look.

Brian Effinger
06-25-2009, 10:15 PM
Jerry, is this what you mean (with 2' overhangs instead of the 1' I drew)? In this case, 2x8's will work, but you might want to use 2x10's for added insulation. I'd need to know how far the ridge will be spanning to say whether 2x10's would work, or you'd need an L.V.L. As for the wall ties at 4' o.c., they would probably be overkill, since the ridge is resisting the outward pressure of the roof on the walls.

Jack Ellis
06-26-2009, 12:22 AM
How much snow do you get? How much wind? Does the ground move in Illinois (New Madrid fault)?

We've just had a house built at Lake Tahoe. Design snow load is 200 psf. In an earthquake. Each new home built up there empties a lumberyard (figuratively speaking).

Consider hiring an engineer to do the calcs?

Walter Plummer
06-26-2009, 4:57 PM
Hello Jerry. I would call or go by your building inspectors office. They can advise you of local minimum requirements and may have a hand out with info.

Brett Nelson
06-26-2009, 6:52 PM
Jerry,

First a disclaimer: you should always check with the building department. That said, they will probably just refer you to the codes that won't tell you the particulars of what you are asking. So I will tell you what I would suggest as I have just a few extra moments here.

Consider just using scissor trusses manufactured locally. They will build them to code and they will be a much easier and faster install. But the interior pitch won't match the exterior pitch. Personally I hate it when I ask for advice on a certain method and all I get is alternate method advice, but just in case you were open to the easier alternatives.

My #2 suggestion would be to use engineered lumber. Since you are suggesting using regular dimensional lumber I am going to assume that the length of the room is less than 16' and that the span width is your stated 20'. I'll assume a modest 6:12 pitch and being in northern Illinois I'm assuming a live load of 40#. In this case you'll be ok with two 11.875" LVL beams ganged together for the ridge beam. If the roof length increases to greater than 16' but still less than 20', then you'll need two 14" LVL beams instead.

Create a beam pocket in a gable end, with a continuous run to a footer. If you don't know what that is, picture four 2x6 studs nailed together with the center two being 12" shorter than the outer two. You'll also need a layer of 1/2" ply between the center two in order to fit the 3.5" thick beam you've just created.

Oops.. out of time. Gotta go., I'll try to finish up later.

John P Clark
06-26-2009, 7:14 PM
Jerry:

Hire a licensed professional engineer in your state to determine your roof loads and size the structures. As an engineer, some of the information in the postings is correct, but not all. I do not think you will get a building permit for this roof without stamped structural plans - my two cents as a professional engineer

Pete Hay
06-26-2009, 7:39 PM
++ for John Clark's response

Julian Nicks
06-27-2009, 10:39 AM
Jerry, I have been a carpenter for over 20 years now, and will tell you from experience NOT to use microlams glued and nailed together. I have seen them pull apart and fail. Use a glue lam that's rated for your application. A quick call to a quality local lumberyard should be all you need to figure out what you need. Personally though, I'd go with at least a 5 1/4x16" glue lam.

Brett Nelson
06-28-2009, 2:58 AM
Well I don't mean any disrespect for the rest of the pros around here at all. What I am suggesting is that the OP is asking for advice on something that is very simple and typical of residential roof construction.

Indeed, most places will require a stamped set of engineered documents for the roof anyway. My suggestion to use the LVLs was based on the manufacturers specs, which is exactly what the engineer is going to use. This is not a complicated engineering feat, but rather framing 101.

5.25x16" beam is very much overkill for the application. A little 20' x 16' addition doesn't really need a beam that large. But if it makes you sleep better at night. Also, I usually lag screw the beams together. In any case, if I were building this addition, I would do the following, and it wouldn't require engineered docs here because it is in accordance with the lumber manufacturers specs.

Two 12" LVLs glued and lagged together. 9 1/2" TJI for rafters spaced 24"o.c. Attach to beam with simpson variable slope joist hangers and simson strap tied over the peak. Strap the TJIs together according to manufacturers specs and apply 5/8" sheathing.

That really would more than get the job done. In fact even the lowest rated TJIs could be used for this job as there is only a 10' horizontal span.

Brett Nelson
06-28-2009, 3:32 AM
The other benefit to using the LVLs instead of the glulams is that they are a not nearly as awkward to install. A 5.25x16" glulam is really quite heavy, at something like 320#. He'd either need a crane or about four other guys on ladders to get it up there. OTOH, each of the LVLs I suggested would come in at about 100# and can be managed by just 2 people really easily.

Jim Andrew
06-28-2009, 11:43 PM
You gave the span as 20' but didn't give the length of the addition. 20' is not much, 2x6's would be strong enough, but no room for insulation. Personally I prefer an attic, and therefore like to build a beam at the ceiling height preferred, and then brace the roof up off the ceiling beam. Also, not a fan of plywood beams, usually they sag of their own weight, and you need to brace them up.

Glen Butler
06-29-2009, 5:27 AM
There is not enough information to answer your question. If you are running your rafters to walls as Brian suggested in his sketch then you are relying on that ridge beam far more than if you are adding a bonus room for example and the rafters meet the floor.

You should have it engineered: snow and wind loads, the pitch of the roof, the length of the rafters resting on the ridge beam, and the free span of the ridge beam all need to be considered. If it is a 20' span in the ridge beam you could easily need 3-18" LVL's if not more and 18' rafters will probably need to be 11 7/8's I joists. Trusses are usually cheaper than stick framed roofs.

Do it right and safe. Get a building permit and have your plans engineered.

Larry Edgerton
06-29-2009, 7:14 AM
Also, not a fan of plywood beams, usually they sag of their own weight, and you need to brace them up.

Not necessarily true. I restored a Carl Strauss designed house built for the Dracket family that had great high ceilings[27'], carried on plywood box beams spanning 26' themselves. It was standing proud from 1962 until about 5 years ago when the current owner let the roof leak into the box beams. I built new box beams in the affected sections and all is well.

Interesting house. It had 87 windows and twenty one exterior doors. Each bedroom had two exterior doors, and some rooms were not accessable from inside the house, you had to go out on the deck to get to the bedrooms. We replaced all of the windows and doors with units built in our shop.

Jerry: I could tell you what you need to do here, but that would not mean anything to you. I would go to your local building department and ask politely. Some departments have a god complex, so keep that in mind and be humble. They will tell you what is the minimum, go one size over. I would not even consider trusses if you have the ability to do it with rafters. Scissor trusses are usually so inaccurate that I find them very frusterating at the finish stage, I prefer rafters in any case. Old school and not afraid of a framing square I guess. :)

Jim Andrew
06-29-2009, 11:38 PM
Larry, I was talking about the LVL's that are manufactured plywood beams. You are talking about box beams built on site. I can build a better beam using lumber and plywood than these LVL's. I call them plywood beams because they are layered like plywood and available practically any length, because they made in plys. As for engineering, the beam companys will size their beams for you if you take a plan to the lumber yard where you plan to purchase them.

Brett Nelson
06-30-2009, 12:59 PM
Larry, I was talking about the LVL's that are manufactured plywood beams. You are talking about box beams built on site. I can build a better beam using lumber and plywood than these LVL's. I call them plywood beams because they are layered like plywood and available practically any length, because they made in plys. As for engineering, the beam companys will size their beams for you if you take a plan to the lumber yard where you plan to purchase them.


Really, you've seen an LVL beam bend under its own weight? Maybe you should get a different manufacturer, because LVLs are by far the stiffest and most structurally sound beams I've ever used, excluding steel.

Jerry Olexa
06-30-2009, 9:33 PM
Wow...thanks guys. Good and thorough responses... I've been out of town for several days (w/o my laptop) @ this country property we are discussing. Sorry to get back to you all so slowly.
More detail now :The addition would be 19X 20 (possibly 22'). The ridge beam would be approx: 24' or 26' allowing for a 2' overhang on both ends. The roof pitch would be 1/1 or a 45 degree slant. (this permits a small loft on the 2nd floor). We would use a few cross ties in area not included in the loft.
I met with 3 contractors while there to get their plans, estimates to do the foundation, framing, roof , windows, siding, etc..I plan to do all the interior work myself including wiring ,some plumbing, etc. Each of the bidders is checking further the local building engineer, inspector and plan to get back to me in a few days (in the country that means a few weeks:)). 2 of them are talking prelaminates and the 3rd, lacing together 2 2X10's.
The site itself is on a hillside with some slope so foundation will be piers driven 4 to 5 ' topped with 6X6 posts and a strong system of beams and joist.
Your advice is very helpful to me. Thanks... I'll continue to follow this thread..

Jerry Olexa
06-30-2009, 9:37 PM
Jerry, is this what you mean (with 2' overhangs instead of the 1' I drew)? In this case, 2x8's will work, but you might want to use 2x10's for added insulation. I'd need to know how far the ridge will be spanning to say whether 2x10's would work, or you'd need an L.V.L. As for the wall ties at 4' o.c., they would probably be overkill, since the ridge is resisting the outward pressure of the roof on the walls.

Brian, yes as you drew it but 19 ft across and 20 feet deep where the ridge beam spans. Thanks and roof pitch/rise would be 1/1.

Jerry Olexa
06-30-2009, 9:47 PM
Forgot to mention: I'm avoiding trusses as I want to incorporate a 2nd floor loft and want it to blend and match the interior of the existing structure,
Yes, we spoke today and will get necessary permits, inspection, etc. All 3 builders with be meeting with the local engineer, inspector for verifying code.. Just wanted your general input guidelines prior to start. I usually overkill on my rafter, joist, beam, etc sizes:) Thanks guys

Brett Nelson
07-02-2009, 10:13 AM
Wow...thanks guys. Good and thorough responses... I've been out of town for several days (w/o my laptop) @ this country property we are discussing. Sorry to get back to you all so slowly.
More detail now :The addition would be 19X 20 (possibly 22'). The ridge beam would be approx: 24' or 26' allowing for a 2' overhang on both ends. The roof pitch would be 1/1 or a 45 degree slant. (this permits a small loft on the 2nd floor). We would use a few cross ties in area not included in the loft.
I met with 3 contractors while there to get their plans, estimates to do the foundation, framing, roof , windows, siding, etc..I plan to do all the interior work myself including wiring ,some plumbing, etc. Each of the bidders is checking further the local building engineer, inspector and plan to get back to me in a few days (in the country that means a few weeks:)). 2 of them are talking prelaminates and the 3rd, lacing together 2 2X10's.
The site itself is on a hillside with some slope so foundation will be piers driven 4 to 5 ' topped with 6X6 posts and a strong system of beams and joist.
Your advice is very helpful to me. Thanks... I'll continue to follow this thread..

The 2' extra on each end of the beam doesn't really come into play. What really matters is the span between bearing walls and the length of nailing surface where the beam sits on the wall. Sounds like you'll have drywall directly on the rafters which means you don't want any more deflection than l/240 or your drywall flexes too much. I would stick with l/360 personally.

The 2x10s will certainly be cheaper, but not strong enough in my estimation. I'll check my span tables later, but I really think that 2 ganged 2X10s isn't enough for this application. By size, LVL beams can span the greatest distances and they still call for a 3.5x14" beam. Again, I'll have to check my span tables, but If using dimensional lumber, I think you'll actually need to go with 2x10s for the rafters with a pitch that steep. If your lumber yards are like mine, you'll be looking at No.2&btr for your lumber. I really have to be picky if I want select lumber. But if you can get select lumber, then 2x8s shouldn't be problem for the rafters. You have to remember that your 12:12 pitch results in a surface area 41.4% larger than the floor space underneath it. Conversely, if the roof were only 6:12 pitch (half as steep as your roof) then the surface areas would only be 11% greater than the floor space beneath it. IOW, by doing a really steep roof, you're gonna have 30% more snow on it. Given that you have a steep roof, and you're suggesting that the room width might actually be closer to 22', I would count on needing to use 2x10 lumber, or 9 1/2" TJIs for the rafters. In that case you would need to use at least 2x12" for the ridge beam anyway, to have a large enough nailing surface for the angled rafters to nail to.

All this changes if you are planning to install collar ties. Without the collar ties, the load of the roof rest mainly on the ridge beam without much lateral stress on the walls. Conversely, when using collar ties, you can shift some of the load to the walls to get it off the ridge beam. This is similar in concept to trusses. That is why they don't need ridge beams.

Jerry Olexa
07-02-2009, 11:26 AM
All this changes if you are planning to install collar ties. Without the collar ties, the load of the roof rest mainly on the ridge beam without much lateral stress on the walls. Conversely, when using collar ties, you can shift some of the load to the walls to get it off the ridge beam. This is similar in concept to trusses. That is why they don't need ridge beams.[/QUOTE]

I plan to do collar ties on 4' centers on the open ceiling. It'll be covered with 1X6" car siding. The loft area will have joist to serve same purpose as collar ties. Thanks

Brett Nelson
07-02-2009, 4:19 PM
Alright, that will help to transfer some of the stress to the exterior walls and take some off the ridge beam. This is where things actually start to get tricky to calculate though. You will be able to get away with 2x8 rafters if there is a collar tie, but you'll need an engineer to size the ridge beam for you. Personally I would still use the 12"TJI for the rafters so that you can blow it full of insulation. That will give you an R35 ceiling vs just an R25.

I was checking my span tables and if you wanted to go with dimensional lumber for the ridge beam, you'd really be looking at 2x12s ganged about 5 thick. I don't know if you've ever made a beam out of 2x12s, but it isn't fun. They aren't dimensionally stable, and there will always be warping and cupping. I would still recommend going with an LVL ridge beam. You'd only need two 14" for your span and you can lift them into place easily and lag them together. They are perfectly straight every time with no cupping. But for the application you will be spending an extra $100 or so to use the LVL.

BTW, I wouldn't hire the guy who said he would use 2 2x10s for the beam.