Page 1 of 2 12 LastLast
Results 1 to 15 of 17

Thread: Wiring in unfinished basement shop

  1. #1
    Join Date
    Dec 2007
    Location
    Arlington VA
    Posts
    8

    Wiring in unfinished basement shop

    I'm rewiring my basement shop to provide additional circuits for some new tools.

    If I put furring strips on the cinderblock walls leading to the receptacles, can I avoid having to run conduit for the wiring. This is what is currently done in the basement, but I know that there are some code violations (which I'm in the process of fixing prior to the inspection) and I'm not exactly sure what the National Electric Code calls for here.

  2. #2
    Join Date
    Feb 2003
    Location
    South Windsor, CT
    Posts
    3,304
    The requirement is that NM be protected from damaged. If you're running the NM down the face of the furring strips, that could be considered "subject to damage" from something leaning or falling against the wiring.

    I'd ask your inspector what they require. If they say that running the NM down the side of the strip is all you need to do with exposed NM wiring, then you're OK.

    You can use conduit to "sleeve" NM for the part where it's running down the wall to protect it from damage.

  3. #3
    Join Date
    Sep 2006
    Location
    Deep South
    Posts
    3,970
    I would be shocked if an inspector let you get away with that.

  4. #4
    Join Date
    Dec 2006
    Location
    Toronto Ontario
    Posts
    11,294
    If you don't want to use NM (or aren't allowed to), you could use BX........Rod.

  5. #5

    Arrow

    It all depends on your local code. Call and talk to your electrical inspector and they will most likely be glad to volunteer information; or your code authority might have information on a web site.

    In Florida (we currently live in central Texas), the electrical code changed four or five years ago (maybe longer) for garages. Wiring had to be in conduit up to so many feet in the air (don't know the number.)

    Makes sense - exposed NM is subject to damage if exposed in an area where people are present. Kind of a long-shot of any harm actually happening, but our country seems bent on protecting us from ourselves.

  6. #6
    Join Date
    Mar 2003
    Location
    SE PA - Central Bucks County
    Posts
    66,009
    Marc, welcome to SMC!

    Around here, one must "sleeve" the NM drop in conduit down the exposed wall as Rob mentioned. Even if that isn't the rule, it's not expensive to do and makes good sense from a practical standpoint, IMHO.
    --

    The most expensive tool is the one you buy "cheaply" and often...

  7. #7
    Join Date
    Feb 2003
    Location
    South Windsor, CT
    Posts
    3,304
    Quote Originally Posted by Art Mann View Post
    I would be shocked if an inspector let you get away with that.
    "Shocked" ... got the pun ... if an inspector let you get away with what? Running down the side of the furring strips? Sleeving the NM-Cable?

  8. #8
    Join Date
    Aug 2005
    Location
    Northern New Jersey
    Posts
    1,958

    All wired up.

    It sounds like a job for either conduit or BX cabling. BX cabling is much easier to work over conduit...especially if you have the hand tool that cuts BX (usually about $30). There is also aluminum cased cable that looks like BX but is aluminum. However, I don't know if it would be sufficient.

    Also, you may wish to check if the electrical outlet boxes must stand off the block wall with a wood shim or board due to moisture issues being tight up against the block. Also, there is likely a minimum height requirement above the floor for basements outlets which is much greater than the usual 12" to 14".

    Lastly, I recommend that you don't skimp on duplex outlet quality. Home Depot and Lowes sells cheap stuff and good stuff (contractor grade). The cheap stuff will crack. It's almost a given. And if you're using all metal stuff (boxes, conduit, BX, etc), it all must be grounded.

    -Jeff

  9. #9
    Quote Originally Posted by Jim Becker View Post
    Marc, welcome to SMC!

    Around here, one must "sleeve" the NM drop in conduit down the exposed wall.
    Same here in Cranbury, NJ.

    I was counselled that for short runs, heat dissipation is not an issue, so it's ok to have Romex in a conduit. If you need longer protection of the cable than 6ish feet, I think u need wires without the outer sleeve.

  10. #10
    Join Date
    Dec 2007
    Location
    Arlington VA
    Posts
    8
    Thanks. I'll call the inspector and ask, but I'll probably run conduit down the wall, even if it isn't required as that sounds like the safer thing to do.

    I'm also assuming I need to run conduit between the main panel and the subpanel I'm installing, right?

  11. #11
    Join Date
    Feb 2003
    Location
    South Windsor, CT
    Posts
    3,304
    Quote Originally Posted by Marc Schneider View Post
    I'm also assuming I need to run conduit between the main panel and the subpanel I'm installing, right?
    Not necessarily. You should be able to run NM or SER depending on the size subpanel you're installing. You want to put the subpanel on plywood that's mounted on something like 2x4's that are attached to the concrete. The subpanel feed can come out the top and go right up the the ceiling joists for the run over to the main panel.

  12. #12
    Quote Originally Posted by Marc Schneider View Post
    I'm also assuming I need to run conduit between the main panel and the subpanel I'm installing, right?
    How far is the sub from the main?

  13. #13
    Join Date
    Dec 2007
    Location
    Arlington VA
    Posts
    8
    About three feet. I'm putting the sub right next to main. So would it be okay to run 6/3 NM directly between the two panels (attached to plywood). It seems wasteful to run the cable up to the joist and back down again.

  14. #14
    Join Date
    Feb 2003
    Location
    South Windsor, CT
    Posts
    3,304
    Quote Originally Posted by Marc Schneider View Post
    About three feet. I'm putting the sub right next to main. So would it be okay to run 6/3 NM directly between the two panels (attached to plywood). It seems wasteful to run the cable up to the joist and back down again.
    If the 2 panels are next to each other, there is no need to run up and down.

    FYI, #6 NM will be limited to a 55 amp subpanel - you can't run a 60 amp subpanel with 6-4 NM. If you want a 60 amp subpanel, run a short piece of conduit (straight across is easy to do) and pull #6 THHN/THWN.

    Rob

  15. #15
    Join Date
    Mar 2006
    Location
    SoCal
    Posts
    22,520
    Blog Entries
    1
    Where I am the wire must run at least 1 1/2" behind the rear of the wallboard or other covering. In my case the firring strips would have to be at least 2 - 2 1/2" deep. Not really firring strips anymore.

    If you have similar requirements I would say conduit would cost you the least floorspace due to increased wall depth. Just my .02.
    "A hen is only an egg's way of making another egg".


    – Samuel Butler

Similar Threads

  1. Basement Shop, Pros and Cons Question...
    By John Dingman in forum WorkShops
    Replies: 27
    Last Post: 10-20-2008, 8:09 AM
  2. Shop renovation -- What do I do?
    By Nathan Conner in forum General Woodworking and Power Tools
    Replies: 40
    Last Post: 09-24-2007, 10:27 PM
  3. Shop Location - What Would You Do?
    By Douglas Robinson in forum General Woodworking and Power Tools
    Replies: 35
    Last Post: 08-20-2007, 3:49 PM
  4. Another electrical question for shop wiring
    By Alan Tolchinsky in forum General Woodworking and Power Tools
    Replies: 40
    Last Post: 07-22-2007, 5:00 PM
  5. Basement Shop Floor Coatings?
    By John Dingman in forum Neanderthal Haven
    Replies: 2
    Last Post: 04-29-2005, 3:02 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •